Hi,
I have several racks in a data Center that have the AP 7894, 7862, and 7941 PDUs... I need the total power in watts OID for each of those APC models. Can anyone assist with that, or point me to the right docs that have the OIDs listed for those models?
Thanks in advance!
-Scott
Message was edited by: swpaisley
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 06:25 AM . Last Modified: 2024-03-18 01:33 AM
no problem 🙂
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 06:24 AM . Last Modified: 2024-03-18 01:33 AM
keep in mind that these models only measure amps and they assume voltage and power factor (which can be adjusted). thus the watts calculation is a result of those. you can try these OIDs:
.iso.org.dod.internet.private.enterprises.apc.products.hardware.rPDU.rPDUIdent.rPDUIdentDevicePowerWatts / .1.3.6.1.4.1.318.1.1.12.1.16
.iso.org.dod.internet.private.enterprises.apc.products.hardware.rPDU.rPDUIdent.rPDUIdentDevicePowerFactor / .1.3.6.1.4.1.318.1.1.12.1.17
.iso.org.dod.internet.private.enterprises.apc.products.hardware.rPDU.rPDUIdent.rPDUIdentDevicePowerVA / .1.3.6.1.4.1.318.1.1.12.1.18
our newer PDUs (AP8XXX) actually measure kW, kWh, amps, and volts so these are real time measurements versus the AP7XXX series above that measure amps and calculate the rest. hope that helps.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 06:24 AM . Last Modified: 2024-03-18 01:33 AM
Thanks for the OIDs, I'll test these and let you know how it pans out.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 06:25 AM . Last Modified: 2024-03-18 01:33 AM
no problem 🙂