APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 06:21 AM . Last Modified: 2024-03-12 11:40 PM
Greetings,
My environment:
- PCNS 4.2 for Virtualization running on dedicated WS2008R2 machine.
- 2 VMware ESXi hosts.
- 1 EqualLogic PS6100 storage array.
- vCenter Server running on a VM with HA enabled (no DRS).
Problem:
How to configure PCNS to shutdown the VMware hosts _before_ shutting down the EqualLogic SA.
The documentation states that the VMware hosts are shutdown after the command file duration elapses. Under "Shutdown Settings" -> "Run Command" is the option "Execute Command File After Host Shutdown". The documentation states: "Enable this option to execute the command file following Host Shutdown".
What is "Host" in this context, the VMware hosts or the PCNS host?
More specifically, will enabling this option cause the command file to be run after the VMware hosts are shut down?
Thanks,
Mike
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 06:22 AM . Last Modified: 2024-03-12 11:40 PM
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 06:22 AM . Last Modified: 2024-03-12 11:40 PM
Hi,
On 3/7/2017 5:44 PM, Mike said:What is "Host" in this context, the VMware hosts or the PCNS host?
The ESXi host.
This diagram is from page 85 of the PowerChute Network Shutdown VMware User's Guide
On 3/7/2017 5:44 PM, Mike said:More specifically, will enabling this option cause the command file to be run after the VMware hosts are shut down?
Yes.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 06:22 AM . Last Modified: 2024-03-12 11:40 PM
Thank you for the quick reply. That answers my question perfectly.
-Mike
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.