APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-25 09:27 PM . Last Modified: 2024-03-19 04:28 AM
Dear friends,
I HAVE 2 BY SUVTP 40KH WHICH ARE EXPERIENCING NO MAINS ERROR. MAINS NOT AVAILABLE IS THE MAIN ERROR EVEN WHEN I CAN CONFIRM THE MAINS AVAILABILITY. THE OTHER ALARM IS BATTERY DISCHARGED. HOW CAN I BE HELPED.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-25 09:27 PM . Last Modified: 2024-03-19 04:28 AM
Hello
Referencing the SUVT Operations Manual, please refer to page 42.
http://www.apcmedia.com/salestools/AHIE-83NAUF/AHIE-83NAUF_R0_EN.pdf?sdirect=true
Mains Not Available. Input Freq/Volt Out of Range.
Meaning: The frequency or voltage is out of acceptable range for normal operation.
Corrective Action: Correct the input voltage to provide acceptable voltage or frequency.
Battery Discharged.
Meaning: The UPS is in battery operation and the battery charge is low. Note: Runtime is limited in duration.
Corrective Action: No corrective action is necessary. Shut down the system and the load equipment or restore incoming voltage.
Kind Regards
Haseeb
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-25 09:27 PM . Last Modified: 2024-03-19 04:28 AM
Hello
Referencing the SUVT Operations Manual, please refer to page 42.
http://www.apcmedia.com/salestools/AHIE-83NAUF/AHIE-83NAUF_R0_EN.pdf?sdirect=true
Mains Not Available. Input Freq/Volt Out of Range.
Meaning: The frequency or voltage is out of acceptable range for normal operation.
Corrective Action: Correct the input voltage to provide acceptable voltage or frequency.
Battery Discharged.
Meaning: The UPS is in battery operation and the battery charge is low. Note: Runtime is limited in duration.
Corrective Action: No corrective action is necessary. Shut down the system and the load equipment or restore incoming voltage.
Kind Regards