APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-10-12 12:21 AM
I noticed in the web interface of our symmetra px, battery voltage is listed as 214vDC.
Nominal Battery Voltage: | 192.2 VDC |
Actual Battery Bus Voltage: | 214.2 VDC |
But each battery back has 8x12v sla batteries.
8*12=96v right? So how do they come up with 192 or 214v?
96*2=192. So does this UPS use two battery modules in series to get 192v? It so, should I keep the A &B Columns even, and c&d columns even to keep it running smoothly? OR does the UPS monitor what bus needs a boost in voltage the most and use relays to change the DC bus its ok.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-10-13 12:06 PM
Hi,
A few additional comments based on your reply
If a C module "fails" then its paired D module should be listed 'unavailable' or something, not merely "ok".
It actually will do this but it depends on the scenario. There are four ways in which the PX 10-160 will declare a battery as being in a fault condition.
I would have at least labeled them A1, A2, B1, B2.
The batteries are labeled in this manner. Here is a screen capture from a Symmetra PX40 NMC. This is also available through the display in a slightly different format.
It sounds like shelves L1-L4 are one unit, and L5-L8 (in an 80kw system) are another,
Yes, but not from an electrical perspective. This is only how the monitoring works. The battery monitoring board present in the UPS can only monitor a maximum of 4 shelves. You'll find one of these boards in each Symmetra PX 40K and then 2 in each external battery cabinet.
Are the bus bars fully rated? in other words, if I had 1c, 1d, 2c, 2d, 3a, 3b, 4a, 4b all vacant, would the remaining cartridges on the right side of L1 and L2 balance out the left side of L3 and L4 without damaging the bus bar between L2 and L3?
The bus bars are rated to handle the full current capacity of the system. By reducing the number of batteries you would be reducing your runtime. The load (while on battery) or the number of power modules (while online - charging current) is what would dictate the current draw. It would not be standard to install the batteries in incomplete shelves.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-10-12 12:54 PM
Hi,
The 214v is the float voltage level. The nominal voltage is 192vdc. As you have surmised the batteries are connected in series to make 192vdc. The "AB" batteries make up the positive string and the CD batteries make up the negative. You can find a detailed description of the Symmetra PX batteries here: https://www.apc.com/us/en/download/document/SPD_AKAR-88TTJW_EN/
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-10-12 08:34 PM
Well. I wish I had known that! Sure does explain why cartridges that did not have a neighbor were always cold, even if they had been warm somewhere else previously.
It's a real shame that the web interface and front panel don't communicate that at all. If a C module "fails" then its paired D module should be listed 'unavailable' or something, not merely "ok".
Interesting design choice. I suppose necessary for their igbt approach. but I would have at least labeled them A1, A2, B1, B2. Or +a+b -a -b.
It sounds like shelves L1-L4 are one unit, and L5-L8 (in an 80kw system) are another, though it's probably of little consequence if they're paralleled together.
Are the bus bars fully rated? in other words, if I had 1c, 1d, 2c, 2d, 3a, 3b, 4a, 4b all vacant, would the remaining cartridges on the right side of L1 and L2 balance out the left side of L3 and L4 without damaging the bus bar between L2 and L3?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-10-13 12:06 PM
Hi,
A few additional comments based on your reply
If a C module "fails" then its paired D module should be listed 'unavailable' or something, not merely "ok".
It actually will do this but it depends on the scenario. There are four ways in which the PX 10-160 will declare a battery as being in a fault condition.
I would have at least labeled them A1, A2, B1, B2.
The batteries are labeled in this manner. Here is a screen capture from a Symmetra PX40 NMC. This is also available through the display in a slightly different format.
It sounds like shelves L1-L4 are one unit, and L5-L8 (in an 80kw system) are another,
Yes, but not from an electrical perspective. This is only how the monitoring works. The battery monitoring board present in the UPS can only monitor a maximum of 4 shelves. You'll find one of these boards in each Symmetra PX 40K and then 2 in each external battery cabinet.
Are the bus bars fully rated? in other words, if I had 1c, 1d, 2c, 2d, 3a, 3b, 4a, 4b all vacant, would the remaining cartridges on the right side of L1 and L2 balance out the left side of L3 and L4 without damaging the bus bar between L2 and L3?
The bus bars are rated to handle the full current capacity of the system. By reducing the number of batteries you would be reducing your runtime. The load (while on battery) or the number of power modules (while online - charging current) is what would dictate the current draw. It would not be standard to install the batteries in incomplete shelves.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-10-14 04:14 PM
Interesting. Every fault I've seen has been a single battery module. And they were all, obviously thermal (overheat) related.
Once I've gotten some of the older cells out and new ones in their place I'm going to to a runtime cal, and then schedule a weekly test to suss out any worn out pairs.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.