Posted: 2021-06-30 11:56 PM . Last Modified: 2024-03-06 03:07 AM
We have a rack-mounted UPS, model number :
APC | UPS Network Management Card 2
|
We receive the following alarms, as viewed from the browser:
Inverter Fault
In Bypass: Hardware Fault
and the battery bar graph display a particular pattern:
1
0
0
1
0
Bypass LED is amber
Fault LED is red
Do I need to replace the Battery?
Thank You.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 11:56 PM . Last Modified: 2024-03-06 03:07 AM
Thank you..
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 11:56 PM . Last Modified: 2024-03-06 03:07 AM
Mostafa,
The inverter is an internal component of the UPS that is non-user replaceable. I highly recommend calling in to local support for assistance or running the "braindead" procedure (this procedure can be found in other forum posts). If a braindead does not clear the fault, the UPS would need to be replaced as the inverter is critical to UPS function.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 11:56 PM . Last Modified: 2024-03-06 03:07 AM
Thank you..