I have a UPS SURTD5000XLI which stopped with LEDs flashing like this:
Fault LED + 1st and 2nd Battery LED from top to bottom
Does anyboby know the meaning of these error codes?
I really appreciate your help
Thanks in advance!
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 07:16 AM . Last Modified: 2024-03-12 04:36 AM
Joe,
The fault code means Logic Power Supply Fault. Did the UPS dropped the load as well? Have you tried turning the UPS off/on?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 07:16 AM . Last Modified: 2024-03-12 04:36 AM
Yes, it dropped the load. I tried off/on several times but nothing changed. Even if i set it in bypass mode the result is the same.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 07:16 AM . Last Modified: 2024-03-12 04:36 AM
Joe,
The fault code means Logic Power Supply Fault. Did the UPS dropped the load as well? Have you tried turning the UPS off/on?