I have just acquired an unused SmartUPS2200RM2U. It was in storage for a while and is unused, so I suspect the batteries are defunct. However, when I plug in the batteries, there's a bit of a spark at the blue plug and socket, so there's probably some charge there. When I power on the unit, it comes on and then there is a click and all six of the indicator lights (online, overload, AVR trim and boost etc.) flash. This is not documented in the manual and I haven't seen reference to it. Before I go and buy new batteries, I thought I'd check here and see if anyone else had encountered this.
This is a 240V UPS
Thanks
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 01:03 AM . Last Modified: 2024-03-11 03:16 AM
If the 6 center leds are blinking, that would indicate a AVR relay weld, the ups must be serviced to have the relay replaced. If the unit is out of warranty you can have Coastal Business Machines (http://www.cbmi.com), do the repair. if you know what you are doing you, you may find and replace the faulty relay yourself.
Note: This is my 200th post 😄
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 01:03 AM . Last Modified: 2024-03-11 03:16 AM
If the 6 center leds are blinking, that would indicate a AVR relay weld, the ups must be serviced to have the relay replaced. If the unit is out of warranty you can have Coastal Business Machines (http://www.cbmi.com), do the repair. if you know what you are doing you, you may find and replace the faulty relay yourself.