Mains voltage occurs due to the error, the device goes into bypass. But When the mains voltage returns to normal; SRT10KXLI is not change on-line with automatically, For on-line mode i need manually. And unit give this error code... Power Sys Error 00800.
Thx
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-07 11:06 PM . Last Modified: 1 month ago
Hi,
I try to say for solving; Example, main voltage is about 180V, Ups is changing online to by-pass. And after 30mins(All power system looks normal); ups is not changing by-pass to online. But if we set input Voltage 220V, no need for change the bypass to online with manually, I guess normall ups comes from factory input voltage 230V. I changed the input voltage 220V.Now if ups is bypass, change the online automatically. The problem is solved.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-07 11:06 PM . Last Modified: 1 month ago
Hello,
I am not sure what you're saying exactly. What I think you're saying is that your UPS is automatically going to bypass because of an input voltage problem but when the voltage returns to normal, the UPS does not come out of bypass automatically and you need to command it out of bypass. There is also an error code. To me, it doesn't make sense that if there is a voltage problem, your UPS is going to bypass.. if anything, it should go to battery power.
Could you provide any log files from the UPS to help clarify? The .tar file is preferred as explained in this link - http://www.apc.com/support/index?page=content&country=ITB〈=en&locale=en_US&id=FA156131. You can gather/download it from the on board management interface in your UPS.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-07 11:06 PM . Last Modified: 1 month ago
Hi,
I try to say for solving; Example, main voltage is about 180V, Ups is changing online to by-pass. And after 30mins(All power system looks normal); ups is not changing by-pass to online. But if we set input Voltage 220V, no need for change the bypass to online with manually, I guess normall ups comes from factory input voltage 230V. I changed the input voltage 220V.Now if ups is bypass, change the online automatically. The problem is solved.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.