I have a 20 kva SURT20KRMXLT with a SBP16KP Bypass panel running at 208 volts. I want to hardwire feed a distribution breaker panel with 120 volt 15 amps breakers. What is the wiring pattern that you use? ON input and output hardwiring diagram of the ups, the wires are ground , L1, N/L2. What does the slash means? L2 + N ? N only, L2 ONLY?
[UPS documentation|http://www.apc.com/products/resource/include/techspec_index.cfm?base_sku=SURT20KRMXLT&total_watts=20...]
The input and output of the bypass switch offers me ground, L1, L2, N
On my distribution panel I need L1 L2 N and ground.
Does someone of you did that setup. Do you have a wiring diagram of all device for my setup? Can I do it that way?
Thanks.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 01:35 AM . Last Modified: 2024-03-11 12:57 AM
Your load would be plugged into the SBP16KP(labeled pdu output terminal). Check the link below for details on the wiring. As you can see in the manual, the lines from utility connect directly to the SBP labeled AC Input. The input from the UPS wires to UPS input on the SBP and the output from the UPS wires to UPS output on the SBP. Please reply if you have any questions.
http://www.apcmedia.com/salestools/SCON-7Q3JQ2_R0_EN.pdf
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 01:35 AM . Last Modified: 2024-03-11 12:57 AM
Your load would be plugged into the SBP16KP(labeled pdu output terminal). Check the link below for details on the wiring. As you can see in the manual, the lines from utility connect directly to the SBP labeled AC Input. The input from the UPS wires to UPS input on the SBP and the output from the UPS wires to UPS output on the SBP. Please reply if you have any questions.