Can anybody advise is it possible to get UPS status via SNMP and Modbus TCP comms simultaneously from Network Management Card 2, or does the card have to be set up for a single protocol?
Thanks in advance for your responses.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 02:21 AM . Last Modified: 2024-03-13 04:21 AM
Yes, the NMC2 handles all protocols simultaneously. For SmartUPS', Modbus TCP support started with SUMX and SY 640.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 02:21 AM . Last Modified: 2024-03-13 04:21 AM
Yes, the NMC2 handles all protocols simultaneously. For SmartUPS', Modbus TCP support started with SUMX and SY 640.