Why does the ION 7400 meter show current phasor angles with cero magnitude when there are no current signals connected to the current input terminals?

Solved
ekourany_btupan
Lieutenant JG
Lieutenant JG
0 Likes
3
531

Why does the ION 7400 meter show current phasor angles with cero magnitude when there are no current signals connected to the current input terminals?

ION 7400 Naturgy.jpg

Tags (1)

Accepted Solutions
Charles_Murison
Picard Picard
Picard
0 Likes
2
526

Re: Why does the ION 7400 meter show current phasor angles with cero magnitude when there are no current signals connected to the current input termin

Hello @ekourany_btupan ,

 

Inside a meter there is some very low level thermal noise. The algorithms inside the meter to calculate phase angle is able to calculate a number based on this noise however the magnitude is 0.

 

Regards,

Charles 

L4 Prime for Advanced metering and Utilities

See Answer In Context

Tags (1)
3 Replies 3
Charles_Murison
Picard Picard
Picard
0 Likes
2
527

Re: Why does the ION 7400 meter show current phasor angles with cero magnitude when there are no current signals connected to the current input termin

Hello @ekourany_btupan ,

 

Inside a meter there is some very low level thermal noise. The algorithms inside the meter to calculate phase angle is able to calculate a number based on this noise however the magnitude is 0.

 

Regards,

Charles 

L4 Prime for Advanced metering and Utilities
Tags (1)
ekourany_btupan
Lieutenant JG
Lieutenant JG
0 Likes
1
507

Re: Why does the ION 7400 meter show current phasor angles with cero magnitude when there are no current signals connected to the current input termin

Thanks @Charles_Murison for the explanation. In that case, why isnt there an algorithm integrated in the framework to suppress the display of angles as long as the magnitudes are "0". The same would work for the frequency readings due to phantom power when the meter is energizes but has no voltage measurement signals connected to the voltage inputs ????

Tags (1)
Charles_Murison
Picard Picard
Picard
0 Likes
0
500

Re: Why does the ION 7400 meter show current phasor angles with cero magnitude when there are no current signals connected to the current input termin

Hello @ekourany_btupan ,

 

I do not know why the angles are displayed. 

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities