DPretty215
Cadet
Cadet

DNP3 Setup in ION Meter with SEL RTAC RTU

When using DNP3.0 communications from ION8650 to SEL RTAC RTU, note you must configure the Master IP Address (DNPIP Master IP Address in RTAC), even if the RTAC is the master. This setting directs traffic to the RTU master and the communications will not work without this setup.ION Setup ConfigurationION Setup ConfigurationRTAC ConfigurationRTAC Configuration 