Hi all,
I have a CO2, Humidity and temperature sensor in my house and I would like to send object 1 (Relative humidity value) to the Multitouch pro system (object 49) in the same room.
The problem is that the dtp length is 1 byte (5.*) and the Multitouch pro system wants to receive 2 byte (9.007).
For now I convert the object from the humidity sensor in a LUA script so that the correct value can be displayed on the Multitouch but I'm sure this is not the correct way to do things.
Is there an update for the MTN6005-0001 so that object 1 can hold 2 bytes instead of 1?
Thanks.
Link copied. Please paste this link to share this article on your social media post.
Hi Henk,
to "Is converting the values in LUA script the only solution to overcome this?
Or are there other solutions in which no LUA script is needed."
Unfortunately it is currently the only way to realize it.
to "Another question, I'm missing a lot of data types in Wiser, only the most common data types are present.
Is there an option to add data types in Wiser?"
Currently not but I guess it will be improved with upcoming versions more and more.
Link copied. Please paste this link to share this article on your social media post.
Hello Henk,
unfortunately there is no update available 😞
Link copied. Please paste this link to share this article on your social media post.
Hi Thomas,
Is converting the values in LUA script the only solution to overcome this?
Or are there other solutions in which no LUA script is needed.
Another question, I'm missing a lot of data types in Wiser, only the most common data types are present.
Is there an option to add data types in Wiser?
Thanks.
Link copied. Please paste this link to share this article on your social media post.
Hi Henk,
to "Is converting the values in LUA script the only solution to overcome this?
Or are there other solutions in which no LUA script is needed."
Unfortunately it is currently the only way to realize it.
to "Another question, I'm missing a lot of data types in Wiser, only the most common data types are present.
Is there an option to add data types in Wiser?"
Currently not but I guess it will be improved with upcoming versions more and more.