You can use our Cbus Bacnet gateway. At the moment, only support 1 application and max 255 addresses.
Posted: 2014-04-16 08:56 PM
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
5500NAC Network automation controller.
or
LSS5500NAC ( Schneider Branded )
5 module wide DIN mount
BACnet IP server onboard
supports 500 BACnet points
Read/Write for BACnet points to /from a BACnet IP Client (BMS)
BACnet IP only, does not support BACnet ETHERNET protocol.
1 X RJ45 connection
Also provides an ethernet connection to a C-Bus network (same concept as a 5500CN2 CNI).