What is the difference between the motor control type SVC I and SVC V in ATV71?
When do I need to select SVC I ?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-10-25 12:39 AM
I always wondered the same thing. I think manual said something like SVC I is equal to the behaviour of the older ATV58 drives. But it does not say exactly what this "behaviour" is. As they decided to keep this "legacy" mode it has to have some positive effects too on some loads but I guess it's usage is probably very limited as SVC V was chosen as default.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2 weeks ago
svci is used when you have high demand load with fluctuation, if the motor doesn't have encoder feedback the vfd will manage the current to keep the motor in working as much possible in the optimum current and torque based on motor standard specs . while svcv is only used to keep frequency and voltage control of simple applications like fans , conveyors , ...
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 1 week ago
Sounds like you are referring SVC U like a scalar mode but it is not, both are vector modes. But you might be right that SVC I has advantages in demanding applications. The manual that not say anything about that, only that SVC I mimics the behaviour of older ATV58 drives.
Link copied. Please paste this link to share this article on your social media post.