TTC error after connecting ATV320 V2.9 IE34
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-09-11 08:04 AM
hello Jerry
Both the ATV320 VFD and the VW3A1111 keypad firmwares have been upgraded to support compatibility. (6-2019)
Firmware versions required:
ATV320 V2.9IE37#3
VW3A1111 V2.0IE53
Earlier versions are not compatible.
Note: Early versions of the ATV320 catalog included the VW3A1111 keypad by mistake, but was removed from the Sept 2018 catalog.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-09-06 02:09 AM
@Zirwa , Could any Vw3A1111 or ATV320 expert adress this issue?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-09-11 08:04 AM
hello Jerry
Both the ATV320 VFD and the VW3A1111 keypad firmwares have been upgraded to support compatibility. (6-2019)
Firmware versions required:
ATV320 V2.9IE37#3
VW3A1111 V2.0IE53
Earlier versions are not compatible.
Note: Early versions of the ATV320 catalog included the VW3A1111 keypad by mistake, but was removed from the Sept 2018 catalog.