I have connected two 10kohm poti on AI1 and AI2 and high speed contact on DI3.
I want control speed from poti 1 connected to AI1 in normal operation and from poti 2 connected to AI2 when DI3 is active.
Which setting need to be configured?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-03-30 07:19 AM
See the [Ref 1B switching] rCb paremeter in the Command and Reference Menu. Then you can set [Ref Freq 1 Config] Fr1 as AI1 and [Ref Freq 2 Config] Fr2 as AI2.
Also covered in our FAQs
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-03-30 07:19 AM
See the [Ref 1B switching] rCb paremeter in the Command and Reference Menu. Then you can set [Ref Freq 1 Config] Fr1 as AI1 and [Ref Freq 2 Config] Fr2 as AI2.
Also covered in our FAQs
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.