Version 12 / Build 38 not starting out so good
SpaceLogic for Niagara Forum
This forum is a place for technical users to share information and collaborate on the integration of SpaceLogic BMS controllers into Niagara BMS.
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-02-2304:17 PM. Last Modified: 2021-02-2305:25 PM
Version 12 / Build 38 not starting out so good
The good news...
With this version I was able to download objects for the first time to an MPC-36 controller
with a Jace8000 hosting it.
The bad news...
My N4 Supervisor now has the same problem that Jace8000 had all along and i can't
download anything to any MPX controller.
I can flip back and forth between the N4 and Jace8000, re-host....and the Jace8000 can
download objects while the N4 Supervisor Fails. Error message at end of post.
Issue #2:
I continued on with just the Jace8000 and discovered that Visual Script objects aren't
downloading to the hosted controllers. They're creating fine, just not downloading.
Custom Script programs are downloading fine and working.
Issue #3
Another issue is that facets are no longer changeable for units such as Fahrenheit for
Temperature Input objects or percent for voltage outputs. No facets are changeable anymore
for any block i've come across.
Might have to punt on this version, because doing a full test without a working
N4 Supervisor as the "control group" , i might be spinning my wheels. The visual
script programs aren't downloading, so can't test the Latch block for example.
N4 Application Director output for download issue:
INFO [19:01:36 23-Feb-21 EST][schneiderMPX] Download All -- > Started. INFO [19:01:36 23-Feb-21 EST][schneiderMPX] Disabling the polling for MPX Controller[MP_881100]. INFO [19:01:36 23-Feb-21 EST][schneiderMPX] Deleting the object(s) from MPX Controller[MP_881100]. INFO [19:01:36 23-Feb-21 EST][schneiderMPX] Creating the object(s) into MPX Controller[MP_881100]. Inside isCommEnabled SEVERE [19:01:37 23-Feb-21 EST][schneiderMPX] Object [SpaceTemp] creation status [Failed] in controller[MP_881100]. java.lang.Exception: Object [SpaceTemp] is not created in controller[MP_881100] as controller is not reachable. at com.tridiumx.ps.schneider.device.BSchneiderCreateObjectJob.createSchneiderObject(BSchneiderCreateObjectJob.java:500) at com.tridiumx.ps.schneider.device.BSchneiderCreateObjectJob.createSchneiderObject(BSchneiderCreateObjectJob.java:354) at com.tridiumx.ps.schneider.config.util.Helper.createObjects(Helper.java:214) at com.tridiumx.ps.schneider.device.BDownloadAllObjectsJob.lambda$run$3(BDownloadAllObjectsJob.java:211) at java.util.stream.ForEachOps$ForEachOp$OfRef.accept(ForEachOps.java:184) at java.util.ArrayList.forEach(ArrayList.java:1257) at java.util.stream.SortedOps$RefSortingSink.end(SortedOps.java:390) at java.util.stream.Sink$ChainedReference.end(Sink.java:258) at java.util.stream.AbstractPipeline.copyInto(AbstractPipeline.java:482) at java.util.stream.AbstractPipeline.wrapAndCopyInto(AbstractPipeline.java:471) at java.util.stream.ForEachOps$ForEachOp.evaluateSequential(ForEachOps.java:151) at java.util.stream.ForEachOps$ForEachOp$OfRef.evaluateSequential(ForEachOps.java:174) at java.util.stream.AbstractPipeline.evaluate(AbstractPipeline.java:234) at java.util.stream.ReferencePipeline.forEachOrdered(ReferencePipeline.java:423) at com.tridiumx.ps.schneider.device.BDownloadAllObjectsJob.run(BDownloadAllObjectsJob.java:203) at javax.baja.job.BSimpleJob$JobThread.run(BSimpleJob.java:85)
INFO [19:01:37 23-Feb-21 EST][schneiderMPX] Downloading the object(s) into MPX Controller[MP_881100]. INFO [19:01:37 23-Feb-21 EST][schneiderMPX] Downloaded object[deviceObject] in controller[MP_881100]. SEVERE [19:01:37 23-Feb-21 EST][schneiderMPX] ** As Object[SpaceTemp] is not present on controller[MP_881100] so skipped downloading its property. INFO [19:01:37 23-Feb-21 EST][schneiderMPX] Downloaded object[deviceObject] in controller[MP_881100]. INFO [19:01:37 23-Feb-21 EST][schneiderMPX] Downloading the object's bindings(s) into MPX Controller[MP_881100]. INFO [19:01:37 23-Feb-21 EST][schneiderMPX] Bindings are downloaded for [deviceObject] in controller[MP_881100]. INFO [19:01:37 23-Feb-21 EST][schneiderMPX] Download All -> Completed.