Good news:
When performing a discover on my network, it found my office AS-P
and every MNB device for IA-Series, b3 on the AS-P, and all Andover
b3 devices under the bCX
Bad news:
It found my AS-P twice and put an orange highlight for both. Upon
investigation, i found that if i disable the 2nd ethernet port on the
AS-P, then everything clears up if i purge all entries in the Bacnet
Comm/network/router table and re-discover.
My 2nd AS-P port is set up as a dual Ip network with DHCP, just like
we'd want for bringing in MPX devices on a private network. The
2nd IP port also has its own unique bacnet network number. I even
changed it to make sure it is unique and purged the entries again
in the jace bacnet network and rediscovered. No difference.
It plainly doesn't like seeing the 2nd AS-P ethernet port being activated
as it's own bacnet network. Issue or no issue?
Jace Port #1 is attached to the office ethernet (BACnet network 100)
Jace Port #2 is used for MPX controllers (Bacnet network 71)
AS-P Port #1 is attached to the office ethernet (Bacnet network 100)
AS-P Port #2 is DHCP server 10.110.210.1 (BACnet network 200)
AS-P is being seen twice from Jace when Ethernet Port #2 is active
on the AS-P