Pulse Width Modulated Output block:
It looks like the Pulse Width Modulated Output has an issue when bringing
it into the wiresheet of a live controller from the standard palette. If it's
brought into an offline wiresheet, it doesn't detect a problem at that time.
Curious if anyone else has this error message occur if they try it. It's the only
block in the entire palette that isn't getting into the wiresheet.
The error message is:
SEVERE [15:34:48 28-Sep-20 EDT][schneiderMPX] Create - object[analogOutput:-1][Pulse$20Width$20Modulated$20Output] failed.
Property:Value Out Of Range
at com.tridium.bacnet.stack.transport.BBacnetTransportLayer.sendConfirmedRequest(BBacnetTransportLayer.java:483)
at com.tridium.bacnet.stack.transport.BBacnetTransportLayer.sendConfirmedRequestComplex(BBacnetTransportLayer.java:363)
at com.tridium.bacnet.stack.client.BBacnetClientLayer.createObject(BBacnetClientLayer.java:749)
at com.tridium.bacnet.stack.BBacnetStack.createObject(BBacnetStack.java:709)
at com.tridiumx.ps.schneider.device.BSchneiderCreateObjectJob.createSchneiderObject(BSchneiderCreateObjectJob.java:330)
at com.tridiumx.ps.schneider.device.BSchneiderCreateObjectJob.run(BSchneiderCreateObjectJob.java:157)
at javax.baja.job.BSimpleJob$JobThread.run(BSimpleJob.java:85)
Solved! Go to Solution.
This defect has been fixed in the latest version.
This defect has been fixed in the latest version.