Public Numerics (Informational)
Copied from the Build 37 post so that others don't have to hunt around the
post listing to find something related to it. Just a synopsis for those
comfortable with Public Numerics or for those not comfortable with them
who want to experiment around.
SETTING PUBLIC NUMERICS:
To set Public Numeric, you can either use the initial values tab in the script
editor or link an object to the exposed Public Numeric on the wiresheet. If using an
initial value, make sure to set "Apply Initial Value" on the property sheet to Yes
and then download the script at some point for it to take effect. If you had set
the initial value and downloaded the script before setting "Apply Initial Value",
you must download the script again. It is possible to use an initial value and a
wiresheet binding at the same time, but the wiresheet object will win out.