Niagara-MPX modules Version #16 (Build 42) (Fixes/Issues)
SpaceLogic for Niagara Forum
This forum is a place for technical users to share information and collaborate on the integration of SpaceLogic BMS controllers into Niagara BMS.
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-04-1410:47 AM
Niagara-MPX modules Version #16 (Build 42) (Fixes/Issues)
***************************************************************************************** Niagara-MPX modules Version #16 (Build 42) (Fixes/Issues)
***************************************************************************************** FORUM ITEMS FIXED:
1) VAV Block (DamperCommand): Priority 16 is now hidden. Problem was that it could fight the internal program of the VAV object if anything was attached.
NEW FORUM PROBLEM: 1) Box flow Present Value is hidden
***************************************************************************************** EVERYTHING FROM THIS POINT DOWN LOOKS LIKE IT HAS THE SAME PROBLEMS FROM PRIOR VERSIONS: ***************************************************************************************** FORUM ITEMS NOT FIXED:
1) Schedule: Minutes to Following Changes reflects a midnight time instead of what would be occurring the next morning. Example...showing midnight instead of 7am 2) Schedule: Previous Change Time, Next Change Time, and Following Change Time are showing incorrect times. 3) BO block shows a "Property:Unknown Property" error and goes into fault from time to time, but still functions when commanded ON/OFF 4) Temperature Input has an OutofService set to False upon import which is inconsistent with the other inputs set to True upon import 5) BV/BO: Priority arrays still show Active/Inactive even after changing text. This is the light blue dot section where you can override the value 6) Schedules priority level not changeable from 16 7) Event Enrollments don't have Alarm Text. (Perhaps Niagara function?) 😎 String fault. Occurs when a String Value object is freshly brought into a live controller. It'll start out with no errors, but if you wait for a bit it'll show the error message "Property:Unknown Property" and go into fault. If you put an actual string into the PresentValue, it will pass ok, but will go into fault eventually as well. While in fault, the block seems to act normally. 9) Lonworks Link appears on objects when deleting various other objects from wiresheet
***************************************************************************************** UTILITY BLOCK COMMON ISSUES NOT FIXED:
1) Some input type choices may not apply to the block type. All blocks have a choice of Boolean,DateTime,Float,Integer,String. 2) Input and Output names (in/out) can be changed, but the settings value reverts back to (in/out), while the block slot name will maintain the change.
BLOCK CONSISTENCY PROBLEM: 1) Equal: Default inputs are binary, while the other 5 comparison type of blocks have integer inputs as default
PERHAPS ADDITIONAL FUNCTIONALITY NEEDED: 1) IndexOf: "Find" syntax will find case insensitive items while "Search" syntax will find case sensitive items. May need both these options to handle various string scenarios.
***************************************************************************************** VAV OBJECT ITEMS NOT FIXED: 1) Velocity Pressure block: Block still shows "Out of Service" after initial Download All