  • Re: Niagara MPX Bacnet Network Used with BACNet Network - MSTP in same Jace
Community Menu
  • Forums
    • By Topic
        • EcoStruxure IT
          • EcoStruxure IT forum
        • Industrial Automation
          • Industry Automation and Control Forum
          • Alliance System Integrators Forum
          • Machine Solutions in the Digital Transformation
          • EcoStruxure Automation Expert / IEC 61499 Forum
          • Industrial Edge Computing Forum
          • Level and Pressure Instrumentation Forum
          • Modicon User Group
          • PLC Club Indonesia
          • SEE Automation Club Forum
          • Fabrika ve Makina Otomasyonu Çözümleri
          • Форум по промышленной автоматизации СНГ
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Forum
          • SCADA and Telemetry Devices Forum
        • Power Distribution IEC
          • Power Distribution and Digital
          • Power Standards & Regulations
          • Paneelbouw & Energie Distributie
        • Power Distribution Softwares
          • EcoStruxure Power Design Forum
          • SEE Electrical Building+ Forum
          • LayoutFAST User Group Forum
        • Solutions for your Business
          • Solutions for Food & Beverage Forum
          • Solutions for Healthcare Forum
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Forum
        • Healthcare
          • Solutions for Healthcare Forum
      • EcoStruxure IT
        • EcoStruxure IT forum
      • Industrial Automation
        • Industry Automation and Control Forum
        • Alliance System Integrators Forum
        • Machine Solutions in the Digital Transformation
        • EcoStruxure Automation Expert / IEC 61499 Forum
        • Industrial Edge Computing Forum
        • Level and Pressure Instrumentation Forum
        • Modicon User Group
        • PLC Club Indonesia
        • SEE Automation Club Forum
        • Fabrika ve Makina Otomasyonu Çözümleri
        • Форум по промышленной автоматизации СНГ
      • SCADA & Telemetry Solutions
        • Geo SCADA Expert Forum
        • SCADA and Telemetry Devices Forum
      • Power Distribution IEC
        • Power Distribution and Digital
        • Power Standards & Regulations
        • Paneelbouw & Energie Distributie
      • Power Distribution Softwares
        • EcoStruxure Power Design Forum
        • SEE Electrical Building+ Forum
        • LayoutFAST User Group Forum
      • Solutions for your Business
        • Solutions for Food & Beverage Forum
        • Solutions for Healthcare Forum
      • Food & Beverage
        • Solutions for Food & Beverage Forum
      • Healthcare
        • Solutions for Healthcare Forum
  • Blogs
    • By Topic
        • Industrial Automation
          • Industrial Edge Computing Blog
          • Industry 4.0 Blog
          • Industrie du Futur France
        • SCADA & Telemetry Solutions
          • SCADA and Telemetry Blog
        • Power Distribution IEC
          • Power Events & Webinars
          • Power Foundations Blog
        • Power Distribution NEMA
          • NEMA Power Foundations Blog
        • Power Distribution Softwares
          • EcoStruxure Power Design Blog
          • SEE Electrical Building+ Blog
        • Solutions for your Business
          • Solutions for Food & Beverage Blog
          • Solutions for Healthcare Blog
          • Solutions for Retail Blog
        • Community experts & publishers
          • Publishers Community
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Blog
        • Healthcare
          • Solutions for Healthcare Blog
        • Retail
          • Solutions for Retail Blog
      • Industrial Automation
        • Industrial Edge Computing Blog
        • Industry 4.0 Blog
        • Industrie du Futur France
      • SCADA & Telemetry Solutions
        • SCADA and Telemetry Blog
      • Power Distribution IEC
        • Power Events & Webinars
        • Power Foundations Blog
      • Power Distribution NEMA
        • NEMA Power Foundations Blog
      • Power Distribution Softwares
        • EcoStruxure Power Design Blog
        • SEE Electrical Building+ Blog
      • Solutions for your Business
        • Solutions for Food & Beverage Blog
        • Solutions for Healthcare Blog
        • Solutions for Retail Blog
      • Community experts & publishers
        • Publishers Community
      • Food & Beverage
        • Solutions for Food & Beverage Blog
      • Healthcare
        • Solutions for Healthcare Blog
      • Retail
        • Solutions for Retail Blog
  • Ideas
        • Industrial Automation
          • Modicon Ideas & new features
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Ideas
          • SCADA and Telemetry Devices Ideas
  • Knowledge Center
    • Building Automation Knowledge Base
    • Industrial Automation How-to videos
    • Ask Exchange
    • Digital E-books
    • Success Stories Corner
    • Power Talks
  • Events & Webinars
  • Support
    • User Guide
    • Leaderboard
    • Releases Notes
How can we help?
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
49555members
Join Now
242930posts
Join Now

Niagara MPX Bacnet Network Used with BACNet Network - MSTP in same Jace

Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Solved Go to Solution
Back to SmartX for Niagara
Solved
MatthewBurkhart
Ensign MatthewBurkhart
Ensign
‎2020-09-16 06:49 PM
0 Likes
12
665
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-09-16 06:49 PM

Niagara MPX Bacnet Network Used with BACNet Network - MSTP in same Jace

I was wondering if I add a MPX BACNet Network to a JACE, if we can also add a BACNet Network (Niagara) to the JACE also.  When i try to add both, I get a duplicate local device which I cannot rename.  Can a MSTP network be used in a Jace with a MPX Network?  Thanks, Matt

Solved! Go to Solution.

Attachments
Tags (1)
  • Tags:
  • english
Share
Reply

Accepted Solutions
Will_Workman
Janeway Will_Workman Janeway
Janeway
‎2020-09-23 08:25 AM
1 Like
3
617
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-09-23 08:25 AM

Re: Niagara MPX Bacnet Network Used with BACNet Network - MSTP in same Jace

@mikelotkowski_p ,

 

I have seen that as well.  The existing devices still communicate but don't show up in the device discovery view.

 

The devices that were under the original BACnet Network are basic BACnet controllers.  The MPX BACnet Network is an extension of the BACnet AWS Network so it only shows BACnet AWS devices and MPX Devices.

 

If you are building a new site with a mix of MPX devices and MNBs/3rd party devices, then you can add the MNBs/3rd party devices as generic AWS BACnet devices and they will show up under the Schneider Device Manager.

See Answer In Context

Tags (1)
  • Tags:
  • english
Share
Reply
  • All forum topics
  • Previous Topic
  • Next Topic
12 Replies 12
Jim_Okapal
Lt. Commander | EcoXpert Master Jim_Okapal Lt. Commander | EcoXpert Master
Lt. Commander | EcoXpert Master
‎2020-09-16 08:54 PM
2 Likes
11
661
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-09-16 08:54 PM

Re: Niagara MPX Bacnet Network Used with BACNet Network - MSTP in same Jace

My understanding is that you can only have one or the other for bacnet

interfaces, but not both in the same jace.  MSTP can be added to

the MPX Bacnet Interface

Tags (1)
  • Tags:
  • english
Share
Reply
MatthewBurkhart
Ensign MatthewBurkhart
Ensign
‎2020-09-16 09:18 PM
0 Likes
10
656
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-09-16 09:18 PM

Re: Niagara MPX Bacnet Network Used with BACNet Network - MSTP in same Jace

Thanks Jim, it's too bad they aren't both allowed, it would make adding MPX controllers to an existing Jace easier.  

Tags (1)
  • Tags:
  • english
Share
Reply
RandyDavis
Sisko RandyDavis Sisko
Sisko
‎2020-09-17 05:35 AM
1 Like
9
652
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-09-17 05:35 AM

Re: Niagara MPX Bacnet Network Used with BACNet Network - MSTP in same Jace

This has been discussed, especially in an instance where you are adding MP controllers to an existing site.  This should be placed as an enhancement.

 

Jim is correct that MSTP networks should be added in the MPX BACnet network


Randy P. Davis

Senior Application Engineer
Global Product Support Services
Digital Buildings LoB
Tags (1)
  • Tags:
  • english
Share
Reply
mikelotkowski_p
Ensign mikelotkowski_p
Ensign
‎2020-09-23 07:02 AM
0 Likes
8
638
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-09-23 07:02 AM

Re: Niagara MPX Bacnet Network Used with BACNet Network - MSTP in same Jace

Randy,

Hope this is added in the future. Could get a little scary when adding a MPX device to an existing system with BACnet IP/MSTP devices. Could see things going sideways real quick replacing the existing Niagara Bacnet Network with the new MPX Bacnet Network.

 

Am I remembering correctly that there is an issue discovering MNB devices using the MPX Bacnet Network? Thought that came up in the earlier webinar. If that is the case, has it been addressed?

Tags (1)
  • Tags:
  • english
Share
Reply
RandyDavis
Sisko RandyDavis Sisko
Sisko
‎2020-09-23 07:53 AM
0 Likes
7
630
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-09-23 07:53 AM

Re: Niagara MPX Bacnet Network Used with BACNet Network - MSTP in same Jace

@mikelotkowski_p  An MS/TP network can be added to the MPX Bacnet Network and devices discovered and added to it.  I have tested MNB and I am sure third party devices will work as well.


Randy P. Davis

Senior Application Engineer
Global Product Support Services
Digital Buildings LoB
Tags (1)
  • Tags:
  • english
Share
Reply
mikelotkowski_p
Ensign mikelotkowski_p
Ensign
‎2020-09-23 08:07 AM
0 Likes
6
626
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-09-23 08:07 AM

Re: Niagara MPX Bacnet Network Used with BACNet Network - MSTP in same Jace

@RandyDavis ,

Had an existing Niagara Bacnet Network on our testing JACE with a few BACnet devices on it. Added the new MPX Bacnet Network, moved the existing BACnet devices to the new MPX network, deleted the old Niagara Bacnet Network, and rebooted the station. After all that, the existing MNB devices do not display in either Schneider Device Manager or AX Bacnet Device Manger. These are MNB-1000's. The devices are listed when I preform a discover on the network. Just not in the "database" pane. 

Tags (1)
  • Tags:
  • english
Share
Reply
RandyDavis
Sisko RandyDavis Sisko
Sisko
‎2020-09-23 08:19 AM
0 Likes
1
621
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-09-23 08:19 AM

Re: Niagara MPX Bacnet Network Used with BACNet Network - MSTP in same Jace

Are the MNB 1000 MS/TP or IP?  This is a different workflow then I tried so I will do this and confirm your findings.  I simply added an MS/TP network, discovered devices, added them, and discovered points


Randy P. Davis

Senior Application Engineer
Global Product Support Services
Digital Buildings LoB
Tags (1)
  • Tags:
  • english
Share
Reply
mikelotkowski_p
Ensign mikelotkowski_p
Ensign
‎2020-09-23 08:20 AM
0 Likes
0
619
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-09-23 08:20 AM

Re: Niagara MPX Bacnet Network Used with BACNet Network - MSTP in same Jace

These are IP devices.

Tags (1)
  • Tags:
  • english
Share
Reply
Will_Workman
Janeway Will_Workman Janeway
Janeway
‎2020-09-23 08:25 AM
1 Like
3
618
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-09-23 08:25 AM

Re: Niagara MPX Bacnet Network Used with BACNet Network - MSTP in same Jace

@mikelotkowski_p ,

 

I have seen that as well.  The existing devices still communicate but don't show up in the device discovery view.

 

The devices that were under the original BACnet Network are basic BACnet controllers.  The MPX BACnet Network is an extension of the BACnet AWS Network so it only shows BACnet AWS devices and MPX Devices.

 

If you are building a new site with a mix of MPX devices and MNBs/3rd party devices, then you can add the MNBs/3rd party devices as generic AWS BACnet devices and they will show up under the Schneider Device Manager.

See Answer In Context

Tags (1)
  • Tags:
  • english
Share
Reply
mikelotkowski_p
Ensign mikelotkowski_p
Ensign
‎2020-11-04 07:49 AM
0 Likes
2
589
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-11-04 07:49 AM

Re: Niagara MPX Bacnet Network Used with BACNet Network - MSTP in same Jace

Is this something that will be corrected in a future build? Thinking of existing sites that we would want to expand on using MPX devices. Would be a lot of work, depending on project size, to switch from the regular Niagara BACnet devices to generic AWS devices. Not to mention if the copy/paste is not done correctly major issues could happen. Would be nice to have the MPXBacnetNetwork able to run along side of the NiagaraBacnetNetwork.

Tags (1)
  • Tags:
  • english
Share
Reply
Will_Workman
Janeway Will_Workman Janeway
Janeway
‎2020-11-05 05:36 AM
0 Likes
1
579
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-11-05 05:36 AM

Re: Niagara MPX Bacnet Network Used with BACNet Network - MSTP in same Jace

@mikelotkowski_p ,

 

The plan is to have the ability to upgrade a regular BACnet Network to a MPX BACnet Network with a software utility.  That will avoid having to copy/paste and potential issues with that.  We are working with Tridium to develop that utility.

Tags (1)
  • Tags:
  • english
Share
Reply
mikelotkowski_p
Ensign mikelotkowski_p
Ensign
‎2020-11-05 05:44 AM
0 Likes
0
576
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-11-05 05:44 AM

Re: Niagara MPX Bacnet Network Used with BACNet Network - MSTP in same Jace

@Will_Workman ,

 

Was going to suggest that as a possible migration tool. Once the traditional BACnet devices are switch to AWS BACnet devices they show up in the device manager. A software tool would make this change much easier and reduce possible issues.

Tags (1)
  • Tags:
  • english
Share
Reply
Top Experts
User Count
David_Purser
Sisko David_Purser Sisko
1
See More Top Experts
Find a Service Provider
Find a certified partner to help you address your integration, installation, maintenance and project needs.
View all Providers
Support

Have a question? Please contact us with details, and we will respond.

Contact Us
FAQ

Look through existing questions to find popular answers.

Learn More
About

Want to know more about Exchange and its possibilities?

Learn More

Full access is just steps away!

Join Exchange for FREE and get unlimited access to our global community of experts.

Connect with Peers & Experts

Discuss challenges in energy and automation with 30,000+ experts and peers.

Get Support in Our Knowledge Base

Find answers in 10,000+ support articles to help solve your product and business challenges.

Ask Questions. Give Solutions

Find peer based solutions to your questions. Provide answers for fellow community members!

Register today for FREE

Register Now

Already have an account?Log in

About Us FAQ Terms & Conditions Privacy Notice Change your cookie settings
©2020, Schneider Electric