SpaceLogic for Niagara Forum
This forum is a place for technical users to share information and collaborate on the integration of SpaceLogic BMS controllers into Niagara BMS.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-01-15 09:41 AM
I am using the N4 (4.8.0.110) and downloading a plant program to a MP-C-32A (firmware 3.02.02.10022).
I have tried resetting the controller manually, resetting the controller through Niagara and erasing the database. I am still getting errors on the download. I have attached the .bog file, the wireshark capture of the download and the error messages from Niagara. Can someone take a look and see what the problem is or if is a potential bug?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-01-21 09:49 AM
INDICATION OF ISSUE: In the Download Failed, one can see that there were multiple objects unable to be created, then subsequent lines stated their attributes could not be written.
ISSUE: There are multiple objects with the same ID number.
CONSTRAINT: MPX objects require that the Object ID number be unique for every object, NOT the pair of Object ID Type and Object ID number to be unique.
RESOLUTION: Click on Config to see the list of objects, click on objects that did not download, and assign a new Object ID number, I chose 100-106 because sorting by Object ID column is Type first, then Number.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-01-21 09:49 AM
INDICATION OF ISSUE: In the Download Failed, one can see that there were multiple objects unable to be created, then subsequent lines stated their attributes could not be written.
ISSUE: There are multiple objects with the same ID number.
CONSTRAINT: MPX objects require that the Object ID number be unique for every object, NOT the pair of Object ID Type and Object ID number to be unique.
RESOLUTION: Click on Config to see the list of objects, click on objects that did not download, and assign a new Object ID number, I chose 100-106 because sorting by Object ID column is Type first, then Number.