This is an update to a previous post's issue since we're now at build 23.
The picture below is a Jace 8000 hosting a VAV box with a temperature input brought into it.
The VAV controller MP_881200 pings no problem, shows the proper hosting name of "Wadsworth"
in the Config Device Object. I can discover all default config objects in the controller.
Upon bringing in the Temperature Input, it also shows it was successful. The problem is
during a "download all".
Below the picture will be the Application Director message. Keep in mind that if i bring this
same exact controller into the the N4 supervisor instead, and re-host it ("WadsworthENS2"),
it works flawlessly. If deleted from the Supervisor and brought into the Jace and rehosted,
same problem as before. I've even done a factory refresh and initialized it from the Jace's
own un-initialized screen.
SEVERE [12:00:35 11-Nov-20 EST][schneiderMPX] Object [Space Temp] creation status [Failed] in controller[MP_881200].
java.lang.Exception: Object [Space Temp] is not created in controller[MP_881200] as controller is not reachable.
at com.tridiumx.ps.schneider.device.BSchneiderCreateObjectJob.createSchneiderObject(BSchneiderCreateObjectJob.java:395)
at com.tridiumx.ps.schneider.device.BSchneiderCreateObjectJob.createSchneiderObject(BSchneiderCreateObjectJob.java:255)
at com.tridiumx.ps.schneider.config.util.Helper.createObjects(Helper.java:192)
at com.tridiumx.ps.schneider.device.BDownloadAllObjectsJob.lambda$run$2(BDownloadAllObjectsJob.java:189)
at java.util.stream.ForEachOps$ForEachOp$OfRef.accept(ForEachOps.java:184)
at java.util.ArrayList.forEach(ArrayList.java:1257)
at java.util.stream.SortedOps$RefSortingSink.end(SortedOps.java:390)
at java.util.stream.Sink$ChainedReference.end(Sink.java:258)
at java.util.stream.AbstractPipeline.copyInto(AbstractPipeline.java:483)
at java.util.stream.AbstractPipeline.wrapAndCopyInto(AbstractPipeline.java:472)
at java.util.stream.ForEachOps$ForEachOp.evaluateSequential(ForEachOps.java:151)
at java.util.stream.ForEachOps$ForEachOp$OfRef.evaluateSequential(ForEachOps.java:174)
at java.util.stream.AbstractPipeline.evaluate(AbstractPipeline.java:234)
at java.util.stream.ReferencePipeline.forEachOrdered(ReferencePipeline.java:423)
at com.tridiumx.ps.schneider.device.BDownloadAllObjectsJob.run(BDownloadAllObjectsJob.java:181)
at javax.baja.job.BSimpleJob$JobThread.run(BSimpleJob.java:85)
INFO [12:00:35 11-Nov-20 EST][schneiderMPX] Downloading the object(s) into MPX Controller[MP_881200].
SEVERE [12:00:35 11-Nov-20 EST][schneiderMPX] Error while downloading object[Space Temp][10-MPX-TemperatureInput].
Cannot write property [objectName] in [Space Temp]:
Object:Unknown Object
at com.tridium.bacnet.stack.transport.BBacnetTransportLayer.sendConfirmedRequest(BBacnetTransportLayer.java:483)
at com.tridium.bacnet.stack.transport.BBacnetTransportLayer.sendConfirmedRequestSimple(BBacnetTransportLayer.java:339)
at com.tridium.bacnet.stack.client.BBacnetClientLayer.writeProperty(BBacnetClientLayer.java:1163)
at javax.baja.bacnet.BBacnetObject.writeProperty(BBacnetObject.java:985)
at com.tridiumx.ps.schneider.config.util.Helper.lambda$downloadObject$2(Helper.java:439)
at java.util.ArrayList$ArrayListSpliterator.forEachRemaining(ArrayList.java:1382)
at java.util.stream.ReferencePipeline$Head.forEachOrdered(ReferencePipeline.java:590)
at com.tridiumx.ps.schneider.config.util.Helper.downloadObject(Helper.java:371)
at com.tridiumx.ps.schneider.device.BDownloadAllObjectsJob.lambda$run$4(BDownloadAllObjectsJob.java:214)
at java.util.stream.ForEachOps$ForEachOp$OfRef.accept(ForEachOps.java:184)
at java.util.stream.SortedOps$SizedRefSortingSink.end(SortedOps.java:352)
at java.util.stream.AbstractPipeline.copyInto(AbstractPipeline.java:483)
at java.util.stream.AbstractPipeline.wrapAndCopyInto(AbstractPipeline.java:472)
at java.util.stream.ForEachOps$ForEachOp.evaluateSequential(ForEachOps.java:151)
at java.util.stream.ForEachOps$ForEachOp$OfRef.evaluateSequential(ForEachOps.java:174)
at java.util.stream.AbstractPipeline.evaluate(AbstractPipeline.java:234)
at java.util.stream.ReferencePipeline.forEachOrdered(ReferencePipeline.java:423)
at com.tridiumx.ps.schneider.device.BDownloadAllObjectsJob.run(BDownloadAllObjectsJob.java:208)
at javax.baja.job.BSimpleJob$JobThread.run(BSimpleJob.java:85)
SEVERE [12:00:35 11-Nov-20 EST][schneiderMPX] Error while downloading object[Space Temp][10-MPX-TemperatureInput].
Cannot write property [outOfService] in [Space Temp]:
Object:Unknown Object
at com.tridium.bacnet.stack.transport.BBacnetTransportLayer.sendConfirmedRequest(BBacnetTransportLayer.java:483)
at com.tridium.bacnet.stack.transport.BBacnetTransportLayer.sendConfirmedRequestSimple(BBacnetTransportLayer.java:339)
at com.tridium.bacnet.stack.client.BBacnetClientLayer.writeProperty(BBacnetClientLayer.java:1163)
at javax.baja.bacnet.BBacnetObject.writeProperty(BBacnetObject.java:985)
at com.tridiumx.ps.schneider.config.util.Helper.lambda$downloadObject$2(Helper.java:439)
at java.util.ArrayList$ArrayListSpliterator.forEachRemaining(ArrayList.java:1382)
at java.util.stream.ReferencePipeline$Head.forEachOrdered(ReferencePipeline.java:590)
at com.tridiumx.ps.schneider.config.util.Helper.downloadObject(Helper.java:371)
at com.tridiumx.ps.schneider.device.BDownloadAllObjectsJob.lambda$run$4(BDownloadAllObjectsJob.java:214)
at java.util.stream.ForEachOps$ForEachOp$OfRef.accept(ForEachOps.java:184)
at java.util.stream.SortedOps$SizedRefSortingSink.end(SortedOps.java:352)
at java.util.stream.AbstractPipeline.copyInto(AbstractPipeline.java:483)
at java.util.stream.AbstractPipeline.wrapAndCopyInto(AbstractPipeline.java:472)
at java.util.stream.ForEachOps$ForEachOp.evaluateSequential(ForEachOps.java:151)
at java.util.stream.ForEachOps$ForEachOp$OfRef.evaluateSequential(ForEachOps.java:174)
at java.util.stream.AbstractPipeline.evaluate(AbstractPipeline.java:234)
at java.util.stream.ReferencePipeline.forEachOrdered(ReferencePipeline.java:423)
at com.tridiumx.ps.schneider.device.BDownloadAllObjectsJob.run(BDownloadAllObjectsJob.java:208)
at javax.baja.job.BSimpleJob$JobThread.run(BSimpleJob.java:85)
SEVERE [12:00:35 11-Nov-20 EST][schneiderMPX] Error while downloading object[Space Temp][10-MPX-TemperatureInput].
Cannot write property [units] in [Space Temp]:
Object:Unknown Object
at com.tridium.bacnet.stack.transport.BBacnetTransportLayer.sendConfirmedRequest(BBacnetTransportLayer.java:483)
at com.tridium.bacnet.stack.transport.BBacnetTransportLayer.sendConfirmedRequestSimple(BBacnetTransportLayer.java:339)
at com.tridium.bacnet.stack.client.BBacnetClientLayer.writeProperty(BBacnetClientLayer.java:1163)
at javax.baja.bacnet.BBacnetObject.writeProperty(BBacnetObject.java:985)
at com.tridiumx.ps.schneider.config.util.Helper.lambda$downloadObject$2(Helper.java:439)
at java.util.ArrayList$ArrayListSpliterator.forEachRemaining(ArrayList.java:1382)
at java.util.stream.ReferencePipeline$Head.forEachOrdered(ReferencePipeline.java:590)
at com.tridiumx.ps.schneider.config.util.Helper.downloadObject(Helper.java:371)
at com.tridiumx.ps.schneider.device.BDownloadAllObjectsJob.lambda$run$4(BDownloadAllObjectsJob.java:214)
at java.util.stream.ForEachOps$ForEachOp$OfRef.accept(ForEachOps.java:184)
at java.util.stream.SortedOps$SizedRefSortingSink.end(SortedOps.java:352)
at java.util.stream.AbstractPipeline.copyInto(AbstractPipeline.java:483)
at java.util.stream.AbstractPipeline.wrapAndCopyInto(AbstractPipeline.java:472)
at java.util.stream.ForEachOps$ForEachOp.evaluateSequential(ForEachOps.java:151)
at java.util.stream.ForEachOps$ForEachOp$OfRef.evaluateSequential(ForEachOps.java:174)
at java.util.stream.AbstractPipeline.evaluate(AbstractPipeline.java:234)
at java.util.stream.ReferencePipeline.forEachOrdered(ReferencePipeline.java:423)
at com.tridiumx.ps.schneider.device.BDownloadAllObjectsJob.run(BDownloadAllObjectsJob.java:208)
at javax.baja.job.BSimpleJob$JobThread.run(BSimpleJob.java:85)
SEVERE [12:00:35 11-Nov-20 EST][schneiderMPX] Error while downloading object[Space Temp][10-MPX-TemperatureInput].
Cannot write property [description] in [Space Temp]:
Object:Unknown Object
at com.tridium.bacnet.stack.transport.BBacnetTransportLayer.sendConfirmedRequest(BBacnetTransportLayer.java:483)
at com.tridium.bacnet.stack.transport.BBacnetTransportLayer.sendConfirmedRequestSimple(BBacnetTransportLayer.java:339)
at com.tridium.bacnet.stack.client.BBacnetClientLayer.writeProperty(BBacnetClientLayer.java:1163)
at javax.baja.bacnet.BBacnetObject.writeProperty(BBacnetObject.java:985)
at com.tridiumx.ps.schneider.config.util.Helper.lambda$downloadObject$2(Helper.java:439)
at java.util.ArrayList$ArrayListSpliterator.forEachRemaining(ArrayList.java:1382)
at java.util.stream.ReferencePipeline$Head.forEachOrdered(ReferencePipeline.java:590)
at com.tridiumx.ps.schneider.config.util.Helper.downloadObject(Helper.java:371)
at com.tridiumx.ps.schneider.device.BDownloadAllObjectsJob.lambda$run$4(BDownloadAllObjectsJob.java:214)
at java.util.stream.ForEachOps$ForEachOp$OfRef.accept(ForEachOps.java:184)
at java.util.stream.SortedOps$SizedRefSortingSink.end(SortedOps.java:352)
at java.util.stream.AbstractPipeline.copyInto(AbstractPipeline.java:483)
at java.util.stream.AbstractPipeline.wrapAndCopyInto(AbstractPipeline.java:472)
at java.util.stream.ForEachOps$ForEachOp.evaluateSequential(ForEachOps.java:151)
at java.util.stream.ForEachOps$ForEachOp$OfRef.evaluateSequential(ForEachOps.java:174)
at java.util.stream.AbstractPipeline.evaluate(AbstractPipeline.java:234)
at java.util.stream.ReferencePipeline.forEachOrdered(ReferencePipeline.java:423)
at com.tridiumx.ps.schneider.device.BDownloadAllObjectsJob.run(BDownloadAllObjectsJob.java:208)
at javax.baja.job.BSimpleJob$JobThread.run(BSimpleJob.java:85)
SEVERE [12:00:35 11-Nov-20 EST][schneiderMPX] Error while downloading object[Space Temp][10-MPX-TemperatureInput].
Cannot write property [minPresValue] in [Space Temp]:
Object:Unknown Object
at com.tridium.bacnet.stack.transport.BBacnetTransportLayer.sendConfirmedRequest(BBacnetTransportLayer.java:483)
at com.tridium.bacnet.stack.transport.BBacnetTransportLayer.sendConfirmedRequestSimple(BBacnetTransportLayer.java:339)
at com.tridium.bacnet.stack.client.BBacnetClientLayer.writeProperty(BBacnetClientLayer.java:1163)
at javax.baja.bacnet.BBacnetObject.writeProperty(BBacnetObject.java:985)
at com.tridiumx.ps.schneider.config.util.Helper.lambda$downloadObject$2(Helper.java:439)
at java.util.ArrayList$ArrayListSpliterator.forEachRemaining(ArrayList.java:1382)
at java.util.stream.ReferencePipeline$Head.forEachOrdered(ReferencePipeline.java:590)
at com.tridiumx.ps.schneider.config.util.Helper.downloadObject(Helper.java:371)
at com.tridiumx.ps.schneider.device.BDownloadAllObjectsJob.lambda$run$4(BDownloadAllObjectsJob.java:214)
at java.util.stream.ForEachOps$ForEachOp$OfRef.accept(ForEachOps.java:184)
at java.util.stream.SortedOps$SizedRefSortingSink.end(SortedOps.java:352)
at java.util.stream.AbstractPipeline.copyInto(AbstractPipeline.java:483)
at java.util.stream.AbstractPipeline.wrapAndCopyInto(AbstractPipeline.java:472)
at java.util.stream.ForEachOps$ForEachOp.evaluateSequential(ForEachOps.java:151)
at java.util.stream.ForEachOps$ForEachOp$OfRef.evaluateSequential(ForEachOps.java:174)
at java.util.stream.AbstractPipeline.evaluate(AbstractPipeline.java:234)
at java.util.stream.ReferencePipeline.forEachOrdered(ReferencePipeline.java:423)
at com.tridiumx.ps.schneider.device.BDownloadAllObjectsJob.run(BDownloadAllObjectsJob.java:208)
at javax.baja.job.BSimpleJob$JobThread.run(BSimpleJob.java:85)
SEVERE [12:00:35 11-Nov-20 EST][schneiderMPX] Error while downloading object[Space Temp][10-MPX-TemperatureInput].
Cannot write property [maxPresValue] in [Space Temp]:
Object:Unknown Object
at com.tridium.bacnet.stack.transport.BBacnetTransportLayer.sendConfirmedRequest(BBacnetTransportLayer.java:483)
at com.tridium.bacnet.stack.transport.BBacnetTransportLayer.sendConfirmedRequestSimple(BBacnetTransportLayer.java:339)
at com.tridium.bacnet.stack.client.BBacnetClientLayer.writeProperty(BBacnetClientLayer.java:1163)
at javax.baja.bacnet.BBacnetObject.writeProperty(BBacnetObject.java:985)
at com.tridiumx.ps.schneider.config.util.Helper.lambda$downloadObject$2(Helper.java:439)
at java.util.ArrayList$ArrayListSpliterator.forEachRemaining(ArrayList.java:1382)
at java.util.stream.ReferencePipeline$Head.forEachOrdered(ReferencePipeline.java:590)
at com.tridiumx.ps.schneider.config.util.Helper.downloadObject(Helper.java:371)
at com.tridiumx.ps.schneider.device.BDownloadAllObjectsJob.lambda$run$4(BDownloadAllObjectsJob.java:214)
at java.util.stream.ForEachOps$ForEachOp$OfRef.accept(ForEachOps.java:184)
at java.util.stream.SortedOps$SizedRefSortingSink.end(SortedOps.java:352)
at java.util.stream.AbstractPipeline.copyInto(AbstractPipeline.java:483)
at java.util.stream.AbstractPipeline.wrapAndCopyInto(AbstractPipeline.java:472)
at java.util.stream.ForEachOps$ForEachOp.evaluateSequential(ForEachOps.java:151)
at java.util.stream.ForEachOps$ForEachOp$OfRef.evaluateSequential(ForEachOps.java:174)
at java.util.stream.AbstractPipeline.evaluate(AbstractPipeline.java:234)
at java.util.stream.ReferencePipeline.forEachOrdered(ReferencePipeline.java:423)
at com.tridiumx.ps.schneider.device.BDownloadAllObjectsJob.run(BDownloadAllObjectsJob.java:208)
at javax.baja.job.BSimpleJob$JobThread.run(BSimpleJob.java:85)
SEVERE [12:00:35 11-Nov-20 EST][schneiderMPX] Error while downloading object[Space Temp][10-MPX-TemperatureInput].
Cannot write property [covIncrement] in [Space Temp]:
Object:Unknown Object
at com.tridium.bacnet.stack.transport.BBacnetTransportLayer.sendConfirmedRequest(BBacnetTransportLayer.java:483)
at com.tridium.bacnet.stack.transport.BBacnetTransportLayer.sendConfirmedRequestSimple(BBacnetTransportLayer.java:339)
at com.tridium.bacnet.stack.client.BBacnetClientLayer.writeProperty(BBacnetClientLayer.java:1163)
at javax.baja.bacnet.BBacnetObject.writeProperty(BBacnetObject.java:985)
at com.tridiumx.ps.schneider.config.util.Helper.lambda$downloadObject$2(Helper.java:439)
at java.util.ArrayList$ArrayListSpliterator.forEachRemaining(ArrayList.java:1382)
at java.util.stream.ReferencePipeline$Head.forEachOrdered(ReferencePipeline.java:590)
at com.tridiumx.ps.schneider.config.util.Helper.downloadObject(Helper.java:371)
at com.tridiumx.ps.schneider.device.BDownloadAllObjectsJob.lambda$run$4(BDownloadAllObjectsJob.java:214)
at java.util.stream.ForEachOps$ForEachOp$OfRef.accept(ForEachOps.java:184)
at java.util.stream.SortedOps$SizedRefSortingSink.end(SortedOps.java:352)
at java.util.stream.AbstractPipeline.copyInto(AbstractPipeline.java:483)
at java.util.stream.AbstractPipeline.wrapAndCopyInto(AbstractPipeline.java:472)
at java.util.stream.ForEachOps$ForEachOp.evaluateSequential(ForEachOps.java:151)
at java.util.stream.ForEachOps$ForEachOp$OfRef.evaluateSequential(ForEachOps.java:174)
at java.util.stream.AbstractPipeline.evaluate(AbstractPipeline.java:234)
at java.util.stream.ReferencePipeline.forEachOrdered(ReferencePipeline.java:423)
at com.tridiumx.ps.schneider.device.BDownloadAllObjectsJob.run(BDownloadAllObjectsJob.java:208)
at javax.baja.job.BSimpleJob$JobThread.run(BSimpleJob.java:85)
SEVERE [12:00:35 11-Nov-20 EST][schneiderMPX] Error while downloading object[Space Temp][10-MPX-TemperatureInput].
Cannot write property [terminalReference] in [Space Temp]:
Object:Unknown Object
at com.tridium.bacnet.stack.transport.BBacnetTransportLayer.sendConfirmedRequest(BBacnetTransportLayer.java:483)
at com.tridium.bacnet.stack.transport.BBacnetTransportLayer.sendConfirmedRequestSimple(BBacnetTransportLayer.java:339)
at com.tridium.bacnet.stack.client.BBacnetClientLayer.writeProperty(BBacnetClientLayer.java:1163)
at javax.baja.bacnet.BBacnetObject.writeProperty(BBacnetObject.java:985)
at com.tridiumx.ps.schneider.config.util.Helper.lambda$downloadObject$2(Helper.java:439)
at java.util.ArrayList$ArrayListSpliterator.forEachRemaining(ArrayList.java:1382)
at java.util.stream.ReferencePipeline$Head.forEachOrdered(ReferencePipeline.java:590)
at com.tridiumx.ps.schneider.config.util.Helper.downloadObject(Helper.java:371)
at com.tridiumx.ps.schneider.device.BDownloadAllObjectsJob.lambda$run$4(BDownloadAllObjectsJob.java:214)
at java.util.stream.ForEachOps$ForEachOp$OfRef.accept(ForEachOps.java:184)
at java.util.stream.SortedOps$SizedRefSortingSink.end(SortedOps.java:352)
at java.util.stream.AbstractPipeline.copyInto(AbstractPipeline.java:483)
at java.util.stream.AbstractPipeline.wrapAndCopyInto(AbstractPipeline.java:472)
at java.util.stream.ForEachOps$ForEachOp.evaluateSequential(ForEachOps.java:151)
at java.util.stream.ForEachOps$ForEachOp$OfRef.evaluateSequential(ForEachOps.java:174)
at java.util.stream.AbstractPipeline.evaluate(AbstractPipeline.java:234)
at java.util.stream.ReferencePipeline.forEachOrdered(ReferencePipeline.java:423)
at com.tridiumx.ps.schneider.device.BDownloadAllObjectsJob.run(BDownloadAllObjectsJob.java:208)
at javax.baja.job.BSimpleJob$JobThread.run(BSimpleJob.java:85)
SEVERE [12:00:35 11-Nov-20 EST][schneiderMPX] Error while downloading object[Space Temp][10-MPX-TemperatureInput].
Cannot write property [digitalFilter] in [Space Temp]:
Object:Unknown Object
at com.tridium.bacnet.stack.transport.BBacnetTransportLayer.sendConfirmedRequest(BBacnetTransportLayer.java:483)
at com.tridium.bacnet.stack.transport.BBacnetTransportLayer.sendConfirmedRequestSimple(BBacnetTransportLayer.java:339)
at com.tridium.bacnet.stack.client.BBacnetClientLayer.writeProperty(BBacnetClientLayer.java:1163)
at javax.baja.bacnet.BBacnetObject.writeProperty(BBacnetObject.java:985)
at com.tridiumx.ps.schneider.config.util.Helper.lambda$downloadObject$2(Helper.java:439)
at java.util.ArrayList$ArrayListSpliterator.forEachRemaining(ArrayList.java:1382)
at java.util.stream.ReferencePipeline$Head.forEachOrdered(ReferencePipeline.java:590)
at com.tridiumx.ps.schneider.config.util.Helper.downloadObject(Helper.java:371)
at com.tridiumx.ps.schneider.device.BDownloadAllObjectsJob.lambda$run$4(BDownloadAllObjectsJob.java:214)
at java.util.stream.ForEachOps$ForEachOp$OfRef.accept(ForEachOps.java:184)
at java.util.stream.SortedOps$SizedRefSortingSink.end(SortedOps.java:352)
at java.util.stream.AbstractPipeline.copyInto(AbstractPipeline.java:483)
at java.util.stream.AbstractPipeline.wrapAndCopyInto(AbstractPipeline.java:472)
at java.util.stream.ForEachOps$ForEachOp.evaluateSequential(ForEachOps.java:151)
at java.util.stream.ForEachOps$ForEachOp$OfRef.evaluateSequential(ForEachOps.java:174)
at java.util.stream.AbstractPipeline.evaluate(AbstractPipeline.java:234)
at java.util.stream.ReferencePipeline.forEachOrdered(ReferencePipeline.java:423)
at com.tridiumx.ps.schneider.device.BDownloadAllObjectsJob.run(BDownloadAllObjectsJob.java:208)
at javax.baja.job.BSimpleJob$JobThread.run(BSimpleJob.java:85)
SEVERE [12:00:35 11-Nov-20 EST][schneiderMPX] Error while downloading object[Space Temp][10-MPX-TemperatureInput].
Cannot write property [valueOffset] in [Space Temp]:
Object:Unknown Object
at com.tridium.bacnet.stack.transport.BBacnetTransportLayer.sendConfirmedRequest(BBacnetTransportLayer.java:483)
at com.tridium.bacnet.stack.transport.BBacnetTransportLayer.sendConfirmedRequestSimple(BBacnetTransportLayer.java:339)
at com.tridium.bacnet.stack.client.BBacnetClientLayer.writeProperty(BBacnetClientLayer.java:1163)
at javax.baja.bacnet.BBacnetObject.writeProperty(BBacnetObject.java:985)
at com.tridiumx.ps.schneider.config.util.Helper.lambda$downloadObject$2(Helper.java:439)
at java.util.ArrayList$ArrayListSpliterator.forEachRemaining(ArrayList.java:1382)
at java.util.stream.ReferencePipeline$Head.forEachOrdered(ReferencePipeline.java:590)
at com.tridiumx.ps.schneider.config.util.Helper.downloadObject(Helper.java:371)
at com.tridiumx.ps.schneider.device.BDownloadAllObjectsJob.lambda$run$4(BDownloadAllObjectsJob.java:214)
at java.util.stream.ForEachOps$ForEachOp$OfRef.accept(ForEachOps.java:184)
at java.util.stream.SortedOps$SizedRefSortingSink.end(SortedOps.java:352)
at java.util.stream.AbstractPipeline.copyInto(AbstractPipeline.java:483)
at java.util.stream.AbstractPipeline.wrapAndCopyInto(AbstractPipeline.java:472)
at java.util.stream.ForEachOps$ForEachOp.evaluateSequential(ForEachOps.java:151)
at java.util.stream.ForEachOps$ForEachOp$OfRef.evaluateSequential(ForEachOps.java:174)
at java.util.stream.AbstractPipeline.evaluate(AbstractPipeline.java:234)
at java.util.stream.ReferencePipeline.forEachOrdered(ReferencePipeline.java:423)
at com.tridiumx.ps.schneider.device.BDownloadAllObjectsJob.run(BDownloadAllObjectsJob.java:208)
at javax.baja.job.BSimpleJob$JobThread.run(BSimpleJob.java:85)
SEVERE [12:00:35 11-Nov-20 EST][schneiderMPX] Error while downloading object[Space Temp][10-MPX-TemperatureInput].
Cannot write property [thermisterType] in [Space Temp]:
Object:Unknown Object
at com.tridium.bacnet.stack.transport.BBacnetTransportLayer.sendConfirmedRequest(BBacnetTransportLayer.java:483)
at com.tridium.bacnet.stack.transport.BBacnetTransportLayer.sendConfirmedRequestSimple(BBacnetTransportLayer.java:339)
at com.tridium.bacnet.stack.client.BBacnetClientLayer.writeProperty(BBacnetClientLayer.java:1163)
at javax.baja.bacnet.BBacnetObject.writeProperty(BBacnetObject.java:985)
at com.tridiumx.ps.schneider.config.util.Helper.lambda$downloadObject$2(Helper.java:439)
at java.util.ArrayList$ArrayListSpliterator.forEachRemaining(ArrayList.java:1382)
at java.util.stream.ReferencePipeline$Head.forEachOrdered(ReferencePipeline.java:590)
at com.tridiumx.ps.schneider.config.util.Helper.downloadObject(Helper.java:371)
at com.tridiumx.ps.schneider.device.BDownloadAllObjectsJob.lambda$run$4(BDownloadAllObjectsJob.java:214)
at java.util.stream.ForEachOps$ForEachOp$OfRef.accept(ForEachOps.java:184)
at java.util.stream.SortedOps$SizedRefSortingSink.end(SortedOps.java:352)
at java.util.stream.AbstractPipeline.copyInto(AbstractPipeline.java:483)
at java.util.stream.AbstractPipeline.wrapAndCopyInto(AbstractPipeline.java:472)
at java.util.stream.ForEachOps$ForEachOp.evaluateSequential(ForEachOps.java:151)
at java.util.stream.ForEachOps$ForEachOp$OfRef.evaluateSequential(ForEachOps.java:174)
at java.util.stream.AbstractPipeline.evaluate(AbstractPipeline.java:234)
at java.util.stream.ReferencePipeline.forEachOrdered(ReferencePipeline.java:423)
at com.tridiumx.ps.schneider.device.BDownloadAllObjectsJob.run(BDownloadAllObjectsJob.java:208)
at javax.baja.job.BSimpleJob$JobThread.run(BSimpleJob.java:85)
INFO [12:00:35 11-Nov-20 EST][schneiderMPX] Downloaded object[Space Temp] in controller[MP_881200].
INFO [12:00:35 11-Nov-20 EST][schneiderMPX] Downloaded object[deviceObject] in controller[MP_881200].
INFO [12:00:35 11-Nov-20 EST][schneiderMPX] Downloading the object's bindings(s) into MPX Controller[MP_881200].
INFO [12:00:35 11-Nov-20 EST][schneiderMPX] Bindings are downloaded for [Space Temp] in controller[MP_881200].
INFO [12:00:35 11-Nov-20 EST][schneiderMPX] Download All -> Completed.
At the very top of the error log you posted, the JACE was unable to create the object in the MPX. The rest of the errors are due to the object not existing.
Can you take a Wireshark capture between the JACE and the MPX while performing a download all with the JACE running build 23?
Thanks.
Will,
I'm attaching the wireshark capture. The test went as follows
for a blank wiresheet other than the "Device Object" already there.
10.111.222.1 = Jace
10.111.222.3 = Vav Box
10.111.222.6 = Laptop Workstation
1) Performed a Discover in the Config Manager
2) Discover is successful
3) Performed a Download All Objects
4) Download All Objects is successful
5) Performed an Upload All Objects
6) Upload All Objects is successful.
7) Dragged a Temperature Input onto the wiresheet
😎 Block creation is successful and has a valid ID.
9) Performed a Download All Objects
10) Download fails
As a side note, I performed a different test where i placed a few objects into
the VAV box using the N4 Supervisor, deleted the controller, brought it into
the Jace, repaired hosting, performed a discover, saw the previous objects,
performed an Upload All...and the blocks successfully came into the Jace
hosted controller. If i then did a Download All, it was successful as well with
the existing added objects. But...if i bring in a fresh new object, it fails just
like before for a Download All
This should almost go without saying, but below is a screencap of the Jace
Software Manager.
The packet capture you posted does not include any traffic to the MP-V controller. It appears to only include FOXS traffic between the JACE and your WB laptop. This usually happens when you run Wireshark directly on a laptop. You will need to use something to capture the traffic between the JACE and the MPX device. This will require a PC with more than 1 network adapter or more than 1 PC.
Here are a few diagrams of how you can capture this data:
Sorry for the multiple posts. For some reason the pictures did not get saved unless I put them in a separate post.
You can also put the shark tap between the JACE and the switch.
Another question: Which version of firmware is in your MP device?
We have done some internal testing and have been unable to reproduce what you are experiencing. For our tests we have been running MP Firmware 3.01.02 and 3.02.01.
Will,
It's firmware 3.02.01. Wanted to get the Build 28 a whirl before heading back to this one.