Can you please report if you are having issues finding un-initialized controllers? I am writing this to see if you experience having to check Global? to find uninitialized controllers.
I just started a new station with Iteration 41 and added BACnet network #1 to Primary IP. I was looking for un-initialized controllers because I had factory reset them, and selected Device Discovery for network 1 (Global? was unchecked). I switched to Unitialized Device View and no devices. Went back to discovery and saw all my other networks, but this time checked Global? and my devices showed up in the Un-initialized view.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-03-26 07:53 AM
All,
Discovering uninitialized devices is not a function of device discovery. Every uninitialized SmartX IP device broadcasts it serial number every 60 seconds. If you having trouble seeing devices just wait a few minutes and they should show up in the uninitialized device view.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-03-25 09:55 PM
David,
I haven't had to click on global, but when in the UnInitialized Device View" i have to let
it sit there for a minute or two while it waits for the uninitialized devices to ping once
every 60 seconds. If i catch the screen at the wrong time, i'll be waiting for nearly
2 minutes...but eventually all devices shows up.
If this isn't the exact situation you're describing, then i haven't had to click global, but i
see the above situation play out nearly every time. From what i understand, the 60
second ping time is normal for the MPX
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-03-26 07:53 AM
All,
Discovering uninitialized devices is not a function of device discovery. Every uninitialized SmartX IP device broadcasts it serial number every 60 seconds. If you having trouble seeing devices just wait a few minutes and they should show up in the uninitialized device view.