  • Re: Download all fails after assigning terminal to temperature input
Community Menu
  • Forums
    • By Topic
        • EcoStruxure IT
          • EcoStruxure IT forum
        • Industrial Automation
          • Industry Automation and Control Forum
          • Alliance System Integrators Forum
          • Machine Solutions in the Digital Transformation
          • EcoStruxure Automation Expert / IEC 61499 Forum
          • Industrial Edge Computing Forum
          • Level and Pressure Instrumentation Forum
          • Modicon User Group
          • PLC Club Indonesia
          • SEE Automation Club Forum
          • Fabrika ve Makina Otomasyonu Çözümleri
          • Форум по промышленной автоматизации СНГ
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Forum
          • SCADA and Telemetry Devices Forum
        • Power Distribution IEC
          • Power Distribution and Digital
          • Power Standards & Regulations
          • Paneelbouw & Energie Distributie
        • Power Distribution Softwares
          • EcoStruxure Power Design Forum
          • SEE Electrical Building+ Forum
          • LayoutFAST User Group Forum
        • Solutions for your Business
          • Solutions for Food & Beverage Forum
          • Solutions for Healthcare Forum
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Forum
        • Healthcare
          • Solutions for Healthcare Forum
      • EcoStruxure IT
        • EcoStruxure IT forum
      • Industrial Automation
        • Industry Automation and Control Forum
        • Alliance System Integrators Forum
        • Machine Solutions in the Digital Transformation
        • EcoStruxure Automation Expert / IEC 61499 Forum
        • Industrial Edge Computing Forum
        • Level and Pressure Instrumentation Forum
        • Modicon User Group
        • PLC Club Indonesia
        • SEE Automation Club Forum
        • Fabrika ve Makina Otomasyonu Çözümleri
        • Форум по промышленной автоматизации СНГ
      • SCADA & Telemetry Solutions
        • Geo SCADA Expert Forum
        • SCADA and Telemetry Devices Forum
      • Power Distribution IEC
        • Power Distribution and Digital
        • Power Standards & Regulations
        • Paneelbouw & Energie Distributie
      • Power Distribution Softwares
        • EcoStruxure Power Design Forum
        • SEE Electrical Building+ Forum
        • LayoutFAST User Group Forum
      • Solutions for your Business
        • Solutions for Food & Beverage Forum
        • Solutions for Healthcare Forum
      • Food & Beverage
        • Solutions for Food & Beverage Forum
      • Healthcare
        • Solutions for Healthcare Forum
  • Blogs
    • By Topic
        • Industrial Automation
          • Industrial Edge Computing Blog
          • Industry 4.0 Blog
          • Industrie du Futur France
        • SCADA & Telemetry Solutions
          • SCADA and Telemetry Blog
        • Power Distribution IEC
          • Power Events & Webinars
          • Power Foundations Blog
        • Power Distribution NEMA
          • NEMA Power Foundations Blog
        • Power Distribution Softwares
          • EcoStruxure Power Design Blog
          • SEE Electrical Building+ Blog
        • Solutions for your Business
          • Solutions for Food & Beverage Blog
          • Solutions for Healthcare Blog
          • Solutions for Retail Blog
        • Community experts & publishers
          • Publishers Community
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Blog
        • Healthcare
          • Solutions for Healthcare Blog
        • Retail
          • Solutions for Retail Blog
      • Industrial Automation
        • Industrial Edge Computing Blog
        • Industry 4.0 Blog
        • Industrie du Futur France
      • SCADA & Telemetry Solutions
        • SCADA and Telemetry Blog
      • Power Distribution IEC
        • Power Events & Webinars
        • Power Foundations Blog
      • Power Distribution NEMA
        • NEMA Power Foundations Blog
      • Power Distribution Softwares
        • EcoStruxure Power Design Blog
        • SEE Electrical Building+ Blog
      • Solutions for your Business
        • Solutions for Food & Beverage Blog
        • Solutions for Healthcare Blog
        • Solutions for Retail Blog
      • Community experts & publishers
        • Publishers Community
      • Food & Beverage
        • Solutions for Food & Beverage Blog
      • Healthcare
        • Solutions for Healthcare Blog
      • Retail
        • Solutions for Retail Blog
  • Ideas
        • Industrial Automation
          • Modicon Ideas & new features
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Ideas
          • SCADA and Telemetry Devices Ideas
  • Knowledge Center
    • Building Automation Knowledge Base
    • Industrial Automation How-to videos
    • Ask Exchange
    • Digital E-books
    • Success Stories Corner
    • Power Talks
  • Events & Webinars
  • Support
    • User Guide
    • Leaderboard
    • Releases Notes
How can we help?
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
49405members
Join Now
242700posts
Join Now

Download all fails after assigning terminal to temperature input

Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Solved Go to Solution
Back to SmartX for Niagara
Solved
MatthewBurkhart
Ensign MatthewBurkhart
Ensign
‎2020-09-23 04:44 PM
0 Likes
9
348
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-09-23 04:44 PM

Download all fails after assigning terminal to temperature input

When I create an analog input (Temperature Input) and do a download all, download is successful.

When I configure the engineering units and sensor type and do a download all, download is successful.

When I assign the terminal to UB1 on a MP-C-24A and do a download all, download fails.  

If I take the point out of service and download all, download is successful.

If I place the point back into service and download all, download fails.  

 

The error looks to be write access denied:

 

INFO [19:30:54 23-Sep-20 EDT][schneiderMPX] Download All -- > Started.
INFO [19:30:54 23-Sep-20 EDT][schneiderMPX] Deleting the object(s) from MPX Controller[MP-C-24A].
INFO [19:30:54 23-Sep-20 EDT][schneiderMPX] Creating the object(s) into MPX Controller[MP-C-24A].
INFO [19:30:54 23-Sep-20 EDT][schneiderMPX] Object [Temperature Input] creation status [Already present on controller].
INFO [19:30:54 23-Sep-20 EDT][schneiderMPX] Downloading the object(s) into MPX Controller[MP-C-24A].
SEVERE [19:30:54 23-Sep-20 EDT][schneiderMPX] Error while downloading object[Temperature Input][10-MPX-TemperatureInput].
Cannot write property [presentValue] in [Temperature Input]:
Property:Write Access Denied
at com.tridium.bacnet.stack.transport.BBacnetTransportLayer.sendConfirmedRequest(BBacnetTransportLayer.java:483)
at com.tridium.bacnet.stack.transport.BBacnetTransportLayer.sendConfirmedRequestSimple(BBacnetTransportLayer.java:339)
at com.tridium.bacnet.stack.client.BBacnetClientLayer.writeProperty(BBacnetClientLayer.java:1163)
at javax.baja.bacnet.BBacnetObject.writeProperty(BBacnetObject.java:985)
at com.tridiumx.ps.schneider.config.util.Helper.lambda$downloadObject$2(Helper.java:407)
at java.util.ArrayList$ArrayListSpliterator.forEachRemaining(ArrayList.java:1382)
at java.util.stream.ReferencePipeline$Head.forEachOrdered(ReferencePipeline.java:590)
at com.tridiumx.ps.schneider.config.util.Helper.downloadObject(Helper.java:349)
at com.tridiumx.ps.schneider.device.BDownloadAllObjectsJob.lambda$run$4(BDownloadAllObjectsJob.java:210)
at java.util.stream.ForEachOps$ForEachOp$OfRef.accept(ForEachOps.java:184)
at java.util.stream.SortedOps$SizedRefSortingSink.end(SortedOps.java:352)
at java.util.stream.AbstractPipeline.copyInto(AbstractPipeline.java:482)
at java.util.stream.AbstractPipeline.wrapAndCopyInto(AbstractPipeline.java:471)
at java.util.stream.ForEachOps$ForEachOp.evaluateSequential(ForEachOps.java:151)
at java.util.stream.ForEachOps$ForEachOp$OfRef.evaluateSequential(ForEachOps.java:174)
at java.util.stream.AbstractPipeline.evaluate(AbstractPipeline.java:234)
at java.util.stream.ReferencePipeline.forEachOrdered(ReferencePipeline.java:423)
at com.tridiumx.ps.schneider.device.BDownloadAllObjectsJob.run(BDownloadAllObjectsJob.java:204)
at javax.baja.job.BSimpleJob$JobThread.run(BSimpleJob.java:85)

INFO [19:30:54 23-Sep-20 EDT][schneiderMPX] Downloaded object[Temperature Input] in controller[MP-C-24A].
INFO [19:30:54 23-Sep-20 EDT][schneiderMPX] Downloaded object[deviceObject] in controller[MP-C-24A].
INFO [19:30:54 23-Sep-20 EDT][schneiderMPX] Downloading the object's bindings(s) into MPX Controller[MP-C-24A].
INFO [19:30:54 23-Sep-20 EDT][schneiderMPX] Bindings are downloaded for [Temperature Input] in controller[MP-C-24A].
INFO [19:30:54 23-Sep-20 EDT][schneiderMPX] Download All -> Completed.

Solved! Go to Solution.

Labels
  • Issue
Tags (1)
  • Tags:
  • english
Share
Reply

Accepted Solutions
ChrisHoward
Lieutenant JG ChrisHoward Lieutenant JG
Lieutenant JG
‎2020-09-25 07:01 AM
2 Likes
0
309
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-09-25 07:01 AM

Re: Download all fails after assigning terminal to temperature input

I think we may be able to resolve this issue by asking Tridium to exclude Present_Value for input objects during the download operation.  Understanding 'input' object types are intended to provide values from equipment and are only writable when out-of-service is TRUE, I can't see a use-case that would require the need to write Present_Value for an input object during a download operation.  Of course, the user could still write Present_Value to the controller through the property sheet (assuming out-of-service is TRUE, of course).

See Answer In Context

Tags (1)
  • Tags:
  • english
Share
Reply
  • All forum topics
  • Previous Topic
  • Next Topic
9 Replies 9
Jim_Okapal
Lt. Commander | EcoXpert Master Jim_Okapal Lt. Commander | EcoXpert Master
Lt. Commander | EcoXpert Master
‎2020-09-23 05:50 PM
0 Likes
1
346
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-09-23 05:50 PM

Re: Download all fails after assigning terminal to temperature input

 

Matt,

I tended to get this error on the binary values when i've corrupted the object setup in some way.

What i had to do was go to the Config Folder Manager, discover the point, make sure it's

grayed out at the top display and solid at the bottom display, highlight the bottom object,

delete the point using the button at the bottom of the page. 

 

If the object was not grayed out at the top, then bring it into the bottom half of the section.

Then highlight the new object and delete along with anything else that aren't the standard

objects.

 

Perform a download all for only the basic controller with no new objects to make sure the

application manager is giving you good information. If this still fails, make sure to repair

host by right clicking on the device and choosing it.  Also ping it.  Make sure the properties

page says it's online.  I've even seen it say online and fail, but a ping has tended to get

the ball rolling.  

 

I've noticed that the first object i create in a brand new initialized controller has the hardest

time getting going.  If i repair host and ping, download all and just make sure the core objects

are reading good, then it's been smooth sailing to create your first Input/Output

 

 

Tags (1)
  • Tags:
  • english
Share
Reply
MatthewBurkhart
Ensign MatthewBurkhart
Ensign
‎2020-09-23 07:43 PM
0 Likes
0
337
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-09-23 07:43 PM

Re: Download all fails after assigning terminal to temperature input

Thanks for your input.  I did as you said and deleted the point as described.  I pinged and repaired hosting.  I then tried to repeat the procedure I used before: downloading after each step.  Download All failed when I assigned UI1 to the point.  Once there I cannot download all anymore, even if I delete the termination.  Thanks, Matt

Tags (1)
  • Tags:
  • english
Share
Reply
Jim_Okapal
Lt. Commander | EcoXpert Master Jim_Okapal Lt. Commander | EcoXpert Master
Lt. Commander | EcoXpert Master
‎2020-09-23 07:59 PM
0 Likes
6
335
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-09-23 07:59 PM

Re: Download all fails after assigning terminal to temperature input

As a curiosity, which firmware version is in the MPC-24 at?

As an experiment last week, there was an MPC-24 that l

tried from factory firmware and it was acting pretty badly for

point additions. After that, i upgraded to the 3.2 version of 

firmware and it cleared up.  The bad news is that i had to

get EBO 3.2 all loaded up, and then got the MPC firmware

upgraded by those means.  I was getting access errors as

well from the old firmware.

 

Are you hosting from the N4 Supervisor or the Jace8000?

The Jace8000 definitely won't work at the current time.

Tags (1)
  • Tags:
  • english
Share
Reply
MatthewBurkhart
Ensign MatthewBurkhart
Ensign
‎2020-09-24 05:04 AM
0 Likes
5
330
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-09-24 05:04 AM

Re: Download all fails after assigning terminal to temperature input

The firmware is at 3.2.  I've been factory resetting the MP-C-24A via Ecostruxure to clear out the database.  I am using the Vykon Version of Niagara 4.8 if that makes a difference. 

Tags (1)
  • Tags:
  • english
Share
Reply
Jim_Okapal
Lt. Commander | EcoXpert Master Jim_Okapal Lt. Commander | EcoXpert Master
Lt. Commander | EcoXpert Master
‎2020-09-24 05:14 AM
0 Likes
4
327
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-09-24 05:14 AM

Re: Download all fails after assigning terminal to temperature input

From my understanding, the Vykon is basically the same Jace as

the Schneider version...so that part should be ok.

 

When I did the factory clear, I had hit the reset button for about 25 seconds.

Anything over 20 seconds does the full clear-out.   Does your MPC-24 have

the display on it?   I used it on mine to make sure I was doing a full reset

based on what it was showing me.  

 

Not positive if the EcoStruxure reset vs the Reset button has a difference

or not, but I know this is for sure one difference I can note.

Tags (1)
  • Tags:
  • english
Share
Reply
Jim_Okapal
Lt. Commander | EcoXpert Master Jim_Okapal Lt. Commander | EcoXpert Master
Lt. Commander | EcoXpert Master
‎2020-09-24 05:26 AM
0 Likes
3
325
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-09-24 05:26 AM

Re: Download all fails after assigning terminal to temperature input

Matt, 

I'm typing a 2nd post to the one above in case you saw It before I can edit it.

 

For the Ecostruxure side, do you have it disconnected from the same network

that everything else is on or cleared out the original hosting from that workstation

listing?   I'd be curious that if the ecostruxure side is totally removed from the network,

if it clears up.  Maybe old hosting information in the EBO side station is hanging up 

the Niagara side.

 

If both the Workstation and N4 Supervisor are on the same computer, I had shut down

the EBO station and made sure its service had stopped before enabling the Niagara

service in the Windows control panel.

 

You also mentioned about choosing "UI1" in a later post.   I kind of glossed over that, but

are you sure there still aren't choices for Ub inputs and Uc inputs?   UI1 is more related

to the Vav controller profile.  

Tags (1)
  • Tags:
  • english
Share
Reply
MatthewBurkhart
Ensign MatthewBurkhart
Ensign
‎2020-09-24 04:30 PM
0 Likes
2
313
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-09-24 04:30 PM

Re: Download all fails after assigning terminal to temperature input

I am using an AS-P to reset the MPX.  I have removed it from the network after the reset.  I did mean Ub1 - sorry.  I think the error has something to do with writing the present value.  I get write access denied.  

Tags (1)
  • Tags:
  • english
Share
Reply
RandyDavis
Sisko RandyDavis Sisko
Sisko
‎2020-09-25 05:28 AM
0 Likes
1
311
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-09-25 05:28 AM

Re: Download all fails after assigning terminal to temperature input

When you add the input to the wiresheet it is set out of service.  Selecting a terminal reference and saving will set the Out of Service to false and now you cant write to the object.  If you set the object back Out of Service and do the download all, it will work.


Randy P. Davis

Senior Application Engineer
Global Product Support Services
Digital Buildings LoB
Tags (1)
  • Tags:
  • english
Share
Reply
ChrisHoward
Lieutenant JG ChrisHoward Lieutenant JG
Lieutenant JG
‎2020-09-25 07:01 AM
2 Likes
0
310
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-09-25 07:01 AM

Re: Download all fails after assigning terminal to temperature input

I think we may be able to resolve this issue by asking Tridium to exclude Present_Value for input objects during the download operation.  Understanding 'input' object types are intended to provide values from equipment and are only writable when out-of-service is TRUE, I can't see a use-case that would require the need to write Present_Value for an input object during a download operation.  Of course, the user could still write Present_Value to the controller through the property sheet (assuming out-of-service is TRUE, of course).

See Answer In Context

Tags (1)
  • Tags:
  • english
Share
Reply
Find a Service Provider
Find a certified partner to help you address your integration, installation, maintenance and project needs.
View all Providers
Support

Have a question? Please contact us with details, and we will respond.

Contact Us
FAQ

Look through existing questions to find popular answers.

Learn More
About

Want to know more about Exchange and its possibilities?

Learn More

Full access is just steps away!

Join Exchange for FREE and get unlimited access to our global community of experts.

Connect with Peers & Experts

Discuss challenges in energy and automation with 30,000+ experts and peers.

Get Support in Our Knowledge Base

Find answers in 10,000+ support articles to help solve your product and business challenges.

Ask Questions. Give Solutions

Find peer based solutions to your questions. Provide answers for fellow community members!

Register today for FREE

Register Now

Already have an account?Log in

About Us FAQ Terms & Conditions Privacy Notice Change your cookie settings
©2020, Schneider Electric