Sign In Help
Schneider Electric
HelpSign In
Schneider Electric Exchange
  • Home
  • Collaborate
  • Develop
  • Shop
Home Collaborate Develop Shop Log in or Register Help

Invite a Co-worker

Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel

Invitation Sent

Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
  • Home
  • Collaborate
  • Exchange Community
  • :
  • Private Communities
  • :
  • SmartX for Niagara
  • :
  • Block examples (attachment) for WPTech/FB people
Community Menu
  • Forums
    • By Topic
        • EcoStruxure IT
          • EcoStruxure IT forum
        • Industrial Automation
          • Industry Automation and Control Forum
          • Alliance System Integrators Forum
          • Machine Solutions in the Digital Transformation
          • EcoStruxure Automation Expert / IEC 61499 Forum
          • Industrial Edge Computing Forum
          • Level and Pressure Instrumentation Forum
          • Modicon User Group
          • PLC Club Indonesia
          • SEE Automation Club Forum
          • Fabrika ve Makina Otomasyonu Çözümleri
          • Форум по промышленной автоматизации СНГ
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Forum
          • SCADA and Telemetry Devices Forum
        • Power Distribution IEC
          • Power Distribution and Digital
          • Power Standards & Regulations
          • Paneelbouw & Energie Distributie
          • Eldistribution & Fastighetsautomation
        • Power Distribution Softwares
          • EcoStruxure Power Design Forum
          • SEE Electrical Building+ Forum
          • LayoutFAST User Group Forum
        • Wireless Information Network Solutions
          • Instrument Area Network
          • Remote Monitoring
          • Tank Level Monitoring
          • Remote Data Collection
        • Solutions for your Business
          • Solutions for Food & Beverage Forum
          • Solutions for Healthcare Forum
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Forum
        • Healthcare
          • Solutions for Healthcare Forum
      • EcoStruxure IT
        • EcoStruxure IT forum
      • Industrial Automation
        • Industry Automation and Control Forum
        • Alliance System Integrators Forum
        • Machine Solutions in the Digital Transformation
        • EcoStruxure Automation Expert / IEC 61499 Forum
        • Industrial Edge Computing Forum
        • Level and Pressure Instrumentation Forum
        • Modicon User Group
        • PLC Club Indonesia
        • SEE Automation Club Forum
        • Fabrika ve Makina Otomasyonu Çözümleri
        • Форум по промышленной автоматизации СНГ
      • SCADA & Telemetry Solutions
        • Geo SCADA Expert Forum
        • SCADA and Telemetry Devices Forum
      • Power Distribution IEC
        • Power Distribution and Digital
        • Power Standards & Regulations
        • Paneelbouw & Energie Distributie
        • Eldistribution & Fastighetsautomation
      • Power Distribution Softwares
        • EcoStruxure Power Design Forum
        • SEE Electrical Building+ Forum
        • LayoutFAST User Group Forum
      • Wireless Information Network Solutions
        • Instrument Area Network
        • Remote Monitoring
        • Tank Level Monitoring
        • Remote Data Collection
      • Solutions for your Business
        • Solutions for Food & Beverage Forum
        • Solutions for Healthcare Forum
      • Food & Beverage
        • Solutions for Food & Beverage Forum
      • Healthcare
        • Solutions for Healthcare Forum
  • Blogs
    • By Topic
        • Industrial Automation
          • Industrial Edge Computing Blog
          • Industry 4.0 Blog
          • Industrie du Futur France
        • SCADA & Telemetry Solutions
          • SCADA and Telemetry Blog
        • Power Distribution IEC
          • Power Events & Webinars
          • Power Foundations Blog
        • Power Distribution NEMA
          • NEMA Power Foundations Blog
        • Power Distribution Softwares
          • EcoStruxure Power Design Blog
          • SEE Electrical Building+ Blog
        • Solutions for your Business
          • Solutions for Food & Beverage Blog
          • Solutions for Healthcare Blog
          • Solutions for Retail Blog
        • Community experts & publishers
          • Publishers Community
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Blog
        • Healthcare
          • Solutions for Healthcare Blog
        • Retail
          • Solutions for Retail Blog
      • Industrial Automation
        • Industrial Edge Computing Blog
        • Industry 4.0 Blog
        • Industrie du Futur France
      • SCADA & Telemetry Solutions
        • SCADA and Telemetry Blog
      • Power Distribution IEC
        • Power Events & Webinars
        • Power Foundations Blog
      • Power Distribution NEMA
        • NEMA Power Foundations Blog
      • Power Distribution Softwares
        • EcoStruxure Power Design Blog
        • SEE Electrical Building+ Blog
      • Solutions for your Business
        • Solutions for Food & Beverage Blog
        • Solutions for Healthcare Blog
        • Solutions for Retail Blog
      • Community experts & publishers
        • Publishers Community
      • Food & Beverage
        • Solutions for Food & Beverage Blog
      • Healthcare
        • Solutions for Healthcare Blog
      • Retail
        • Solutions for Retail Blog
  • Ideas
        • Industrial Automation
          • Modicon Ideas & new features
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Ideas
          • SCADA and Telemetry Devices Ideas
  • Knowledge Center
    • Building Automation Knowledge Base
    • Industrial Automation Knowledge Base
    • Industrial Automation How-to videos
    • SCADA & Telemetry Solutions Knowledge Base
    • Digital E-books
    • Success Stories Corner
    • Power Talks
  • Events & Webinars
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Technology Partners
  • Support
    • Ask Exchange
    • Leaderboard
    • Our Community Guidelines
    • Community User Guide
    • How-To & Best Practices
    • More
Join Now
How can we help?
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
51289members
Join Now
245505posts
Join Now

Block examples (attachment) for WPTech/FB people

Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Back to SmartX for Niagara
Jim_Okapal
Lt. Commander | EcoXpert Master Jim_Okapal Lt. Commander | EcoXpert Master
Lt. Commander | EcoXpert Master
‎2020-09-19 10:57 AM
2 Likes
6
401
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-09-19 10:57 AM

Block examples (attachment) for WPTech/FB people

 

Script Blocks.jpg

 

I'm going to share with the Tridium/MPX community the script blocks that I'm 

in the process of testing, using the scripts i was tinkering with back in 2015.

These are not Schneider Electric sanctioned blocks.   They were 100% functional

in EBO back in 2015 and I'll be seeing how the Tridium/MPX process handles them.

I'm providing these as a way for those people not comfortable in general with script

programming to have as much block usage as possible ahead of time before

the new SE wiresheet blocks are available to us.  In the end, it looks like the Schneider

Wiresheet creates a large "mega-script" encompassing all of their blocks from the

wiresheet to keep the amount of script program objects being loaded into the MPX

to a minimum.  Being that the blocks i'm showing you are individual scripts...if you

brought in 100 objects, then you'd have 100 scripts being downloaded.   Schneider

is going to have a palette of their own script blocks that "code together" in a particular

way so they flow on one script.  The blocks i'm showing you won't be involved with

that process. They'd remain as separate entities.  

 

History:

Back in 2015, it was becoming apparent that WPTech wasn't going to always

be applicable for programming jobs if an AS-P had modules  or if there weren't

any MNB controllers on the job either.  I had two options due to nobody else being

scripters or anybody feeling comfortable even attempting it. Choice1 was to get

the AS-P function (xenta) blocks into a format that looked like WPTech blocks

by using HFBs, or Choice2 was to create script blocks that you combine

together.   For our techs, choice1 was going to be the clear winner.  While

creating the WPTech function blocks,  I also dabbled in the scripting choice

as a side project because you just never know when it would come in handy.   

 

Currently in the wiresheet:

Most blocks will be inherent what the intent is, but some are made different for a 

reason.  The LOGIC and MATH blocks are all encompassing, kind of similar to

NW8000.  The LoopLarge block was a PID created for full educational use.  It has

the normal PI you'd expect plus derivative, error checking for settings, a ramp

function, feedback in the case of overrides, enable/disable, block update times,

diagnostics of key variables, and maximum documentation.  The LoopMedium was

a loop created for normal "PI" usage with a ramp function, feedback, enable/disable,

block update times, along with basic documentation. The LoopSmall was the smallest

possible "PI" loop of our format that could function and had no added features. The

StringExperiment block was to demonstrate working with strings and various syntaxes.

It was also used to parse words in a sentence or a sequence of numbers. When it

comes across a "space" it breaks that section off and indexes it.

 

I've brought in the scripts shown in the picture and they all compile.  After a

"download all" each one but 2 show they're humming along.  The 2 will show an

E right off the bat because the MATH block is expecting a public numeric value

for the number of inputs the block will use and instead shows a "null".   Once the

public numeric is manually given a value, then the E line will clear out within 30

secs.  In EBO, a public numerics value would have been saved along with the

EBO export.  Bringing it in fresh like this from a notepad document, it would be

null.  I should have had a line to account for this back in 2015, but back then i

wasn't planning for a Tridium MPX need for them in 2020.  The StringExperiment 

block is the other one but don't worry about that one for the time being.  

 

How to experiment with them:

After you've pasted the one you're interested in, into the script editor, and have

compiled to make sure it works, be sure to set the initial data types for each of

the inputs and outputs to the relevant types you need such as boolean or integer

or keep it as float.  It appears that the integer setting isn't working in the script

editor at the moment, but that's what you'd normally do.  After you've compiled,

sent to station, sent to controller, performed a download all....the blocks should

be usable.   I know several of the blocks need a public numeric set after the

block is first created, similar to a configuration setting or setpt. If something

doesn't work (such as what i'm seeing with digital values not being seen in

scripts in one of the posts i made....and also publlic numerics not holding

their values in another post), don't be too concerned at the moment.

I'll be going through the blocks in the coming days and reporting what i see

happening. These are mainly to help the people with Block Programming 

experience have block choices in advance to connect Inputs/Outputs, test

logic, and get comfortable with the wiresheet and config folder setup 

before the Schneider Blocks come out.

 

Thanks

 

Additional post for "Function Script" Blocks

"Function" Script Block examples (attachment) for WPTech/FB people. 

Attachments
Script Blocks.zip
Tags (1)
  • Tags:
  • english
Share
Reply
  • All forum topics
  • Previous Topic
  • Next Topic
6 Replies 6
RandyDavis
Sisko RandyDavis Sisko
Sisko
‎2020-09-21 05:54 AM
2 Likes
2
356
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-09-21 05:54 AM

Re: Block examples (attachment) for WPTech/FB people

Jim,  Thanks for the contribution of all this work.  I will do some testing with these today

 

Just to let you and all Beta participants know, the Phase II wire sheet programming palette of objects, very similar to what you have done, is moving forward nicely


Randy P. Davis

Senior Application Engineer
Global Product Support Services
Digital Buildings LoB
Tags (1)
  • Tags:
  • english
Share
Reply
Jim_Okapal
Lt. Commander | EcoXpert Master Jim_Okapal Lt. Commander | EcoXpert Master
Lt. Commander | EcoXpert Master
‎2020-09-21 01:41 PM
0 Likes
1
347
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-09-21 01:41 PM

Re: Block examples (attachment) for WPTech/FB people

Update for the Tridium-MPX community:

After performing some testing with various blocks today, there's a few other

posts I've made regarding issues i'm seeing with binary values and public

numerics, along with demonstrating the issue with a picture of the wiresheet

for some of the block connections.  

 

So far, some items to watch out for are:

1) Incoming binary points to the script block will freeze up the block

display, but the script inside (actually inside the MPX) will still work.

2) To un-freeze the block, attach an analog value to the location that

had the binary value attached.  

3) To use a digital input that the script is intending to have... link an analog

value to it and use 0 for OFF and any number greater than 0 for ON.  

4) Public numerics don't seem to be holding their values... so to get around

that, the next best choice is to link an external analog value to the spot where

the public numeric is located on the block.

5)  LonLinks may randomly appear as you add and delete blocks from your

wiresheet. "n:dataLink"

 

In the next few pictures , I'll be showing some examples of what the previous

issues from above entail, while also showing the LOGIC and MATH block since

it was a combo block more similar to NW8000.   Some other new posts concerning

issues are uitilizing the TSTAT, SELECT, and DualDelay to demonstrate the examples,

but i'll paste them here as well.

 

 

Demonstrating a workaround in needing an external object to set the Public Numeric:

Public Numeric Wiresheet.jpg

 

Demonstating that a Binary Value is being seen as Null at the script block

Binary Problem.jpg

 

Demonstrating how the binary value is freezing up the script object.  If using an

Analog value in the place of a Binary value, it works fine.  

DualOnOffDelay AI-BI.jpg

 

LOGIC and MATH blocks connected up, but keeping in mind the problem items from above

and using Analogs where needed in the place of digitals and public numerics.

Logic Math.jpg

Tags (1)
  • Tags:
  • english
Share
Reply
Jim_Okapal
Lt. Commander | EcoXpert Master Jim_Okapal Lt. Commander | EcoXpert Master
Lt. Commander | EcoXpert Master
‎2020-09-21 02:47 PM
0 Likes
0
342
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-09-21 02:47 PM

Re: Block examples (attachment) for WPTech/FB people

 

Here's a couple more uses:

 

CountUp, CountDown:

In case if anyone was wondering why i also had a PulseGenerator in the blocks, it was 

to test the CountUp and CountDown in a more automatic way.

CountUp CountDown.jpg

 

Reset Block:

The nice thing about public numerics would be that the "reset" items could actually be changed

from inside of the block to save wiresheet real estate by using less blocks if it ends up being a

usable feature.   It could just be the block by itself connected to the block before it and after it.

 

Reset.jpg

Tags (1)
  • Tags:
  • english
Share
Reply
Jim_Okapal
Lt. Commander | EcoXpert Master Jim_Okapal Lt. Commander | EcoXpert Master
Lt. Commander | EcoXpert Master
‎2020-09-21 03:33 PM
0 Likes
0
336
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-09-21 03:33 PM

Re: Block examples (attachment) for WPTech/FB people

The large loop block (Codename: Goliath) in action:

 

Updating every 5 seconds

Direct Acting

SpaceTemp = 75 deg

SpaceSetpt = 70 deg

Error = 5 deg

Kp (Gain) = 5

Ki = .1

 

What we see from script block with Tridium polling time delay

Proportion Total = (SignalPropWithK) = 25%

Integration Total = (SignalIntegWithK) = 8.96% and rising

Derivative Total = (SignalDerivWithK) = 0

LoopOutput = 33.96%

 

What we see from LoopOutput Analog Value with Tridium polling time delay

Analog Value Polled output = 34.17%

 

LargeLoop.jpg

Tags (1)
  • Tags:
  • english
Share
Reply
Will_Workman
Janeway Will_Workman Janeway
Janeway
‎2020-09-23 06:12 AM
0 Likes
0
316
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-09-23 06:12 AM

Re: Block examples (attachment) for WPTech/FB people

Jim,

 

Thank you for sharing your Script version of WPT blocks.  I plan on doing some testing with them as well.

Tags (1)
  • Tags:
  • english
Share
Reply
Julio_Cortes
Commander Julio_Cortes Commander
Commander
‎2020-09-23 07:00 AM
1 Like
0
312
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-09-23 07:00 AM

Re: Block examples (attachment) for WPTech/FB people

@Jim_Okapal  I think your work and history portion is proof that we have provided the right feedback to product management for quite sometime.  Thank you for sharing your library of objects it looks like this is a great start. Once again thank you for all your feedback.

Tags (1)
  • Tags:
  • english
Share
Reply
Top Experts
User Count
Will_Workman
Janeway Will_Workman Janeway
13
ChrisHoward
Lieutenant JG ChrisHoward Lieutenant JG
7
RandyDavis
Sisko RandyDavis Sisko
2
David_Purser
Sisko David_Purser Sisko
1
barry_sweet_abs
Lieutenant JG barry_sweet_abs
1
See More Top Experts
Find a Service Provider
Find a certified partner to help you address your integration, installation, maintenance and project needs.
View all Providers
Support

Have a question? Please contact us with details, and we will respond.

Contact Us
FAQ

Look through existing questions to find popular answers.

Learn More
About

Want to know more about Exchange and its possibilities?

Learn More

Full access is just steps away!

Join Exchange for FREE and get unlimited access to our global community of experts.

Connect with Peers & Experts

Discuss challenges in energy and automation with 30,000+ experts and peers.

Get Support in Our Knowledge Base

Find answers in 10,000+ support articles to help solve your product and business challenges.

Ask Questions. Give Solutions

Find peer based solutions to your questions. Provide answers for fellow community members!

Register today for FREE

Register Now

Already have an account?Log in

About Us FAQ Terms & Conditions Privacy Notice Change your cookie settings
©2020, Schneider Electric