If you have N4 Supervisor and EBO Enterprise server on the same
computer, make sure to go to software administrator in EBO and
stop your station. I usually load all 4 of the main EBO programs
by default when i'm upgrading to a new version. I forgot that i wanted
to post this a few days ago when investigating alot of Application Director
conflicts relating to port 443 in the N4 Supervisor.
@Jim_Okapal the same thing happens if you are running more than 1 version of EBO.
For Niagara stations running on my laptop, I uncheck the box for "Auto-Start".
For EBO Enterprise Server and Enterprise Central I go into the windows services and change them to start manually.
This way I never have anything running on boot up and I can manually start which ever piece of software I need to use.
The same thing happens with port 47808 for BACnet. You cannot run WPT Commissioning Tool or download to a MNB from WPT if you have an Niagara station with a BACnet network or an ES with a BACnet Interface running.