Follow along for an enriching discussion with our CEO, Peter Herweck, and industry leaders for a captivating Global Keynote at #InnovationSummit Paris 2024. Watch recording and join the #ImpactMaker movement!️
Adding object to config & facet issues with Room Sensor & Variable Air Volume Data, Flow Data
SpaceLogic for Niagara Forum
This forum is a place for technical users to share information and collaborate on the integration of SpaceLogic BMS controllers into Niagara BMS.
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-02-1611:33 AM
Adding object to config & facet issues with Room Sensor & Variable Air Volume Data, Flow Data
Im running a 4.8 station on my PC, connected to:
I have an MP-V 7A with a RoomSensor Attached (Base=SXWSBTHCXSXX, Cover =SXWSCDPSELXX) – I upgraded the firmware package from 2.0 that was in it to the latest I could find (3.02.02.10022)
- in the attached images im finding conversions of units between the controller and the room sensor with reference to temperature. the thermostat is displaying °F, but the readings in Niagara are showing me °C. The setpoints are not following correctly either- nor is the setpoint control i have allow setpoints on, but when you goto press the setpoint on the thermostat it just shows "Locks".
- Further conversion error with the Flow Data and you can see attached whats in the Commissioning tool and the JACE...
-Was Still experiencing program compiling errors with simply logic was able to use a dual delay and duplicated it, once duplicated, the "duplicate wouldnt allow the program to compile, i removed and replaced, and then another object failed to compile that wasnt affected the first time..
I moved onto an MPC i have wired in my office. was able to configure it, am not able to update firmware on this device currently i dont have an AS here; its running a 1.0firmware. I was able to add IO under config, but once i went to add an Analog Value for a setpoint under config, it failed, would not allow me to bring it in... i tried "repair hosting" no improvement...
I can forward this station fi easier to look at - if it's me or software ATM... I emailed Will Brad and Randy this station last week.