  • Re: how to change MPC-X device id
Community Menu
  • Forums
    • By Topic
        • EcoStruxure IT
          • EcoStruxure IT forum
        • Industrial Automation
          • Industry Automation and Control Forum
          • Alliance System Integrators Forum
          • Machine Solutions in the Digital Transformation
          • EcoStruxure Automation Expert / IEC 61499 Forum
          • Industrial Edge Computing Forum
          • Level and Pressure Instrumentation Forum
          • Modicon User Group
          • PLC Club Indonesia
          • SEE Automation Club Forum
          • Fabrika ve Makina Otomasyonu Çözümleri
          • Форум по промышленной автоматизации СНГ
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Forum
          • SCADA and Telemetry Devices Forum
        • Power Distribution IEC
          • Power Distribution and Digital
          • Power Standards & Regulations
          • Paneelbouw & Energie Distributie
        • Power Distribution Softwares
          • EcoStruxure Power Design Forum
          • SEE Electrical Building+ Forum
          • LayoutFAST User Group Forum
        • Solutions for your Business
          • Solutions for Food & Beverage Forum
          • Solutions for Healthcare Forum
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Forum
        • Healthcare
          • Solutions for Healthcare Forum
      • EcoStruxure IT
        • EcoStruxure IT forum
      • Industrial Automation
        • Industry Automation and Control Forum
        • Alliance System Integrators Forum
        • Machine Solutions in the Digital Transformation
        • EcoStruxure Automation Expert / IEC 61499 Forum
        • Industrial Edge Computing Forum
        • Level and Pressure Instrumentation Forum
        • Modicon User Group
        • PLC Club Indonesia
        • SEE Automation Club Forum
        • Fabrika ve Makina Otomasyonu Çözümleri
        • Форум по промышленной автоматизации СНГ
      • SCADA & Telemetry Solutions
        • Geo SCADA Expert Forum
        • SCADA and Telemetry Devices Forum
      • Power Distribution IEC
        • Power Distribution and Digital
        • Power Standards & Regulations
        • Paneelbouw & Energie Distributie
      • Power Distribution Softwares
        • EcoStruxure Power Design Forum
        • SEE Electrical Building+ Forum
        • LayoutFAST User Group Forum
      • Solutions for your Business
        • Solutions for Food & Beverage Forum
        • Solutions for Healthcare Forum
      • Food & Beverage
        • Solutions for Food & Beverage Forum
      • Healthcare
        • Solutions for Healthcare Forum
  • Blogs
    • By Topic
        • Industrial Automation
          • Industrial Edge Computing Blog
          • Industry 4.0 Blog
          • Industrie du Futur France
        • SCADA & Telemetry Solutions
          • SCADA and Telemetry Blog
        • Power Distribution IEC
          • Power Events & Webinars
          • Power Foundations Blog
        • Power Distribution NEMA
          • NEMA Power Foundations Blog
        • Power Distribution Softwares
          • EcoStruxure Power Design Blog
          • SEE Electrical Building+ Blog
        • Solutions for your Business
          • Solutions for Food & Beverage Blog
          • Solutions for Healthcare Blog
          • Solutions for Retail Blog
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Blog
        • Healthcare
          • Solutions for Healthcare Blog
        • Retail
          • Solutions for Retail Blog
      • Industrial Automation
        • Industrial Edge Computing Blog
        • Industry 4.0 Blog
        • Industrie du Futur France
      • SCADA & Telemetry Solutions
        • SCADA and Telemetry Blog
      • Power Distribution IEC
        • Power Events & Webinars
        • Power Foundations Blog
      • Power Distribution NEMA
        • NEMA Power Foundations Blog
      • Power Distribution Softwares
        • EcoStruxure Power Design Blog
        • SEE Electrical Building+ Blog
      • Solutions for your Business
        • Solutions for Food & Beverage Blog
        • Solutions for Healthcare Blog
        • Solutions for Retail Blog
      • Food & Beverage
        • Solutions for Food & Beverage Blog
      • Healthcare
        • Solutions for Healthcare Blog
      • Retail
        • Solutions for Retail Blog
  • Ideas
        • Industrial Automation
          • Modicon Ideas & new features
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Ideas
          • SCADA and Telemetry Devices Ideas
  • Knowledge Center
    • Building Automation Knowledge Base
    • Industrial Automation How-to videos
    • Ask Exchange
    • Digital E-books
    • Success Stories Corner
    • Power Talks
  • Events & Webinars
  • Support
    • User Guide
    • Leaderboard
    • Releases Notes
How can we help?
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
49243members
Join Now
242457posts
Join Now

how to change MPC-X device id

Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Solved Go to Solution
Back to SmartX Controller Field Trials
Solved
Gary
Lt. Commander Gary Lt. Commander
Lt. Commander
‎2018-01-12 07:00 AM
0 Likes
9
369
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2018-01-12 07:00 AM

how to change MPC-X device id

I have an MPC-18A device ID 200021
I wish to return the device to a default device id.
I have carried out the following.

With network cable to AS-P attached.
Warm start
Cold start
Network reset
Factory defaults
Secure erase

With network cable to AS-P not attached.

Warm start

Cold start

Network reset

Factory defaults

Secure erase

Powered down for 30 minutes

I have loaded a new database in the AS-P
Before re-attaching the MPC-X network to the AS-P I carried out another: -

Warm start

Cold start

Network reset

Factory defaults

Secure erase

Factory reset (for luck)

Powered doqn the MP-C-18A

I attached the MPC to the AS-P network, powered up the MPC.
Created a bacnet interface on the AS-P and checked device descovery only to find the MPC-X there (unhosted) but still with the same device ID.

Does anyone have any other ideas I can try?

Regards
Gary

Solved! Go to Solution.

Share
Reply

Accepted Solutions
sesa182151_brid
Lieutenant sesa182151_brid Lieutenant
Lieutenant
‎2018-01-12 08:34 AM
1 Like
2
277
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2018-01-12 08:34 AM

Re: how to change MPC-X device id

The factory reset should work as long as you are not connected to the hosting server, which will conveniently (not so in this case) auto commission if it recognizes the serial number and thereby restore the ID.

Another post references the reset timings in an MP-X Tech Ref guide but those timings are obsolete. They are now as follows:

0-5s – Warm start

5-10s – cold Start

10-20s – network reset

20-40s – factory reset

See Answer In Context

Attachments
Share
Reply
  • All forum topics
  • Previous Topic
  • Next Topic
9 Replies 9
Mike_Boogemans
Commander | EcoXpert Master Mike_Boogemans Commander | EcoXpert Master
Commander | EcoXpert Master
‎2018-01-12 07:13 AM
0 Likes
0
277
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2018-01-12 07:13 AM

Re: how to change MPC-X device id

You could try using the reset button on the controller to reset to factory condition. The MP-X Tech Ref Guide says you need to press and hold for 40 to 60 seconds to get it to reset to factory conditions. I haven't tried this myself so not 100% sure what will happen.

Mike Boogemans
Alpha Controls & Services
Share
Reply
Jarrod
Sisko | EcoXpert Master Jarrod Sisko | EcoXpert Master
Sisko | EcoXpert Master
‎2018-01-12 07:18 AM
0 Likes
0
277
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2018-01-12 07:18 AM

Re: how to change MPC-X device id

I don't have the software in front of me, but I do remember seeing that there is now the option to change the instance ID of BACnet controllers (thank you R&D).  If I recall, you right click on the device and it is under an advance option under the controller.  I can get a screen capture later if you can't find it.

Share
Reply
Will_Workman
Janeway Will_Workman Janeway
Janeway
‎2018-01-12 08:21 AM
0 Likes
0
277
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2018-01-12 08:21 AM

Re: how to change MPC-X device id

I found out that they can be changed from the Mobile Commissioning Tool.

Share
Reply
BillNeville
Commander BillNeville Commander
Commander
‎2018-01-12 08:27 AM
0 Likes
2
277
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2018-01-12 08:27 AM

Re: how to change MPC-X device id

Jarrod - you are correct.

Right-click on the controller >> Device >> Advanced >> Change device ID.

Share
Reply
sesa182151_brid
Lieutenant sesa182151_brid Lieutenant
Lieutenant
‎2018-01-12 08:34 AM
1 Like
2
278
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2018-01-12 08:34 AM

Re: how to change MPC-X device id

The factory reset should work as long as you are not connected to the hosting server, which will conveniently (not so in this case) auto commission if it recognizes the serial number and thereby restore the ID.

Another post references the reset timings in an MP-X Tech Ref guide but those timings are obsolete. They are now as follows:

0-5s – Warm start

5-10s – cold Start

10-20s – network reset

20-40s – factory reset

See Answer In Context

Attachments
Share
Reply
Gary
Lt. Commander Gary Lt. Commander
Lt. Commander
‎2018-01-19 02:52 AM
0 Likes
1
277
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2018-01-19 02:52 AM

Re: how to change MPC-X device id

Although this doesn't answer my original question, as you would have to know what the default device ID was originally.

(Q: I have an MPC-18A device ID 200021, I wish to return the device to a default device id.)
However your suggestion does allow the device ID to be changed to something different.
I did use this method to change the device ID, but I am left wondering, why a factory reset does not perform this task.
Thank you for your reply, much appriciated.
Gary

Share
Reply
BillNeville
Commander BillNeville Commander
Commander
‎2018-01-19 06:41 AM
0 Likes
0
277
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2018-01-19 06:41 AM

Re: how to change MPC-X device id

The key is disconnecting the connection to your AS before you do the factory reset. Mine reset to 4194303 - which I assume is factory default.

Share
Reply
Will_Workman
Janeway Will_Workman Janeway
Janeway
‎2018-01-19 07:15 AM
0 Likes
1
277
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2018-01-19 07:15 AM

Re: how to change MPC-X device id

I noticed the the reset times on the HOA screen of my MPC did not match the documentation.  Which would explained why the reset was not working on my MPV.  Thanks for the update on the new reset times.

Share
Reply
BillNeville
Commander BillNeville Commander
Commander
‎2018-01-19 11:17 AM
0 Likes
0
277
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2018-01-19 11:17 AM

Re: how to change MPC-X device id

On my MP-C-18A v .90.03777 I'm seeing this:

0-5s – warm start

5-10s – cold Start

10-20s – network reset

20-30s – factory reset

Share
Reply
Find a Service Provider
Find a certified partner to help you address your integration, installation, maintenance and project needs.
View all Providers
Support

Have a question? Please contact us with details, and we will respond.

Contact Us
FAQ

Look through existing questions to find popular answers.

Learn More
About

Want to know more about Exchange and its possibilities?

Learn More

Full access is just steps away!

Join Exchange for FREE and get unlimited access to our global community of experts.

Connect with Peers & Experts

Discuss challenges in energy and automation with 30,000+ experts and peers.

Get Support in Our Knowledge Base

Find answers in 10,000+ support articles to help solve your product and business challenges.

Ask Questions. Give Solutions

Find peer based solutions to your questions. Provide answers for fellow community members!

Register today for FREE

Register Now

Already have an account?Log in

About Us FAQ Terms & Conditions Privacy Notice Change your cookie settings
©2020, Schneider Electric