I attached the SmartX Room Unit to the MPC with a standard ethernet cable. The Room Unit lights up and responds when I press any of the 3 buttons.
I added a new Room Unit Object, and set its address 4 to match the physical dip switches. The temperature is reading correctly.
Is it a problem that the Status is showing "invalid"? The System Status shows "Operational".
Solved! Go to Solution.
Good to know. Thanks for the explanation.
Only the Temperature and Humidity sensor functionality have been implemented in the current firmware.
Good to know. Thanks for the explanation.