Hello
I noticed that if Smart Connector user tries to get data from COV trend log which has no new data for couple of months then response will be empty. If user will use sampleOnOrAfter parameter with value "2021-12-01" then response will show COV trend.
What is oldest date which Get TrendSamples will return when using only trendid parameter?
We had some boolean values which have not changes very often, but customer would like get that data even it has not been changed for couple of months.
--
Esa
Link copied. Please paste this link to share this article on your social media post.
Hi Esa,
The default value for sampleOnOrAfter is 30 days.
I will make sure it's added to the docs for the next version.
BR
Armend
Link copied. Please paste this link to share this article on your social media post.
Hi Esa,
The default value for sampleOnOrAfter is 30 days.
I will make sure it's added to the docs for the next version.
BR
Armend