I’m using SmartConnector to control SBO. I followed the manual and I’m able to get/put values if they are "Analog/Digital Value". But when I try to do the same with "Digital Output", GET works but PUT fails.
How do you update "Requested Value" of "Digital Output"? Or simply update "Digital Output"?
I use /Values/{id}/Value and GET works but PUT doesn't. It says READ_ONLY.
Link copied. Please paste this link to share this article on your social media post.
Hi Mayumi,
I was a little bit off. What you want to do is:
PUT http://(URL)/Values/(path)/Value
Where path is a encoded version of:
11/Quraz/Servers/Demo shop/IO Bus/2F-07 DO-FC-8/HV_FS_01_01_01/RequestedValue (notice how the /RequestedValue is part of the path)
Therefore the whole request would be:
PUT: http://(URL)/Values/11%252FQuraz%252FServers%252FDemo%2520shop%252FIO%2520Bus%252F2F-07%2520DO-FC-8%252FHV_FS_01...
Let me know if that helps!
Regards,
-Jeff
Link copied. Please paste this link to share this article on your social media post.
Hi Mayumi,
The path ({id}) for the RequestedValue of an IO output should look something like:
11/Server 1/Servers/InnovationAS/IO Bus/UI-8.DO-FC-4/Cooling/RequestedValue
Please note the use of '11' instead of the typical '01'. This is because the RequestedValue is a property of an object, but not the object itself.
Regards,
-Jeff
Link copied. Please paste this link to share this article on your social media post.
HI Jeffrey,
Thanks for your reply.
But it doesn't seem to work.
I tried...
GET http://(URL)/Values/01/(path)/Value - This works
PUT http://(URL)/Values/11/(path)/RequestedValue - "Not Found"
Mayumi
Link copied. Please paste this link to share this article on your social media post.
This is the test result...
PUT: http://(URL)/Values/01%252FQuraz%252FServers%252FDemo%2520shop%252FIO%2520Bus%252F2F-07%2520DO-FC-8%... - 404, Not Found/No message
PUT: http://(URL)/Values/11%252FQuraz%252FServers%252FDemo%2520shop%252FIO%2520Bus%252F2F-07%2520DO-FC-8%... - 404, Not Found/No message
PUT: http://(URL)/Values/01%252FQuraz%252FServers%252FDemo%2520shop%252FIO%2520Bus%252F2F-07%2520DO-FC-8%252FHV_FS_01... - 500, Internal Server Error/NOT_FORCEABLE
PUT: http://(URL)/Values/11%252FQuraz%252FServers%252FDemo%2520shop%252FIO%2520Bus%252F2F-07%2520DO-FC-8%252FHV_FS_01... - 500, Internal Server Error/INVALID_ID
PUT: http://(URL)/Values/01%252FQuraz%252FServers%252FDemo%2520shop%252FIO%2520Bus%252F2F-07%2520DO-FC-8%252FHV_FS_01... - 500, Internal Server Error/READ_ONLY
PUT: http://(URL)/Values/11%252FQuraz%252FServers%252FDemo%2520shop%252FIO%2520Bus%252F2F-07%2520DO-FC-8%252FHV_FS_01... - 500, Internal Server Error/INVALID_ID
Link copied. Please paste this link to share this article on your social media post.
Hi Mayumi,
I was a little bit off. What you want to do is:
PUT http://(URL)/Values/(path)/Value
Where path is a encoded version of:
11/Quraz/Servers/Demo shop/IO Bus/2F-07 DO-FC-8/HV_FS_01_01_01/RequestedValue (notice how the /RequestedValue is part of the path)
Therefore the whole request would be:
PUT: http://(URL)/Values/11%252FQuraz%252FServers%252FDemo%2520shop%252FIO%2520Bus%252F2F-07%2520DO-FC-8%252FHV_FS_01...
Let me know if that helps!
Regards,
-Jeff
Link copied. Please paste this link to share this article on your social media post.
Worked!!
Thank you so much!!!!