We have a critical and large project with single EC; multiple ES and several SmartX controllers (AS-Ps).
Question:
If we deploy SoapEwsRestProvider@ EC; would that be able to expose all the objects under ES and ASPs?
Supplementary Question:
Assuming we can deploy multiple smart connectors and target different objects or servers to improve the performance of the SC; given that all the children objects are visible under EC?
Link copied. Please paste this link to share this article on your social media post.
Question:
If we deploy SoapEwsRestProvider@ EC; would that be able to expose all the objects under ES and ASPs?
Confirmed that the answer is True. EC will expose objects from children.
Link copied. Please paste this link to share this article on your social media post.
Question:
If we deploy SoapEwsRestProvider@ EC; would that be able to expose all the objects under ES and ASPs?
Confirmed that the answer is True. EC will expose objects from children.
Link copied. Please paste this link to share this article on your social media post.
Looks like you ran some tests on your own :). You are correct!
Best Regards,
-Jeff
Link copied. Please paste this link to share this article on your social media post.
Evren,
Sorry to wake an old thread -
What path did you use to expose those objects? I see not definitions for this in existing documentation and cannot get the smart connector to function through an EC to an ES (whereas the connection direct to the ES before worked fine)
Thanks!