I have a SmartConnector extension running in 2.5.4 with boolean type History records which appear correct when viewed in the SmartConnector portal, however; they are all reading 0 in EBO 4.0.1.86. See attached screen shot.
Hi Steven,
I've tested this and it looks like there's an issue with boolean serialization. It will be looked at ASAP.
BR
Armend
Just wondering if there is any update on this issue?
Hi Steve,
There's an issue in EBO where EBO's EWS client doesn't understand boolean trends from Smartconnector. I just got word that this will be fixed in 4.0.3.
I'll probably add a "legacy serve" mode to Smartconnector that can be turned on to allow older EBO clients to be used.
BR
Armend
Hi Ardak,
Thanks for the update. If you have a version with this fix, happy to try it out.
Steve