Hi All,
Currently in the process of integrating a number of EBO sites (5 sites) via the EBO-OPC Server product from ControlSee https://shop.exchange.se.com/en-US/apps/65037/opc-server-for-building-operations/editions into a central monitoring systems (Aveva). If in a years time site no.1 add a new chiller for instance and there are new alarms configured on the EBO headend. Does the ControlSee application automatically pick these points up or do these also need configuring/engineering?
TIA!
Adam
Link copied. Please paste this link to share this article on your social media post.
Hi Adam,
When you add a new alarm in the EBO, there is o need for configuration/engineering. All you need is to add the new alarm in the OPC Client (Aveva in your case). For example, if the alarm id is "/Server 1/Values/Change of State Alarm", you need to add this OPC item in Aveva - "/Server 1/Values/Change of State Alarm.Alarm".
Michael
Link copied. Please paste this link to share this article on your social media post.
Hi Adam,
When you add a new alarm in the EBO, there is o need for configuration/engineering. All you need is to add the new alarm in the OPC Client (Aveva in your case). For example, if the alarm id is "/Server 1/Values/Change of State Alarm", you need to add this OPC item in Aveva - "/Server 1/Values/Change of State Alarm.Alarm".
Michael
Link copied. Please paste this link to share this article on your social media post.
Thank you very much for the confirmation
Link copied. Please paste this link to share this article on your social media post.
Al,
My mistake. You need to do run the Discovery processor in SmartConnector to discover the newly added alarms.
Regards,
Mike
Link copied. Please paste this link to share this article on your social media post.
Right click on the OPC DataHub system-tray icon and choose Properties. In the Properties window, select OPC .