Hello,
I was using a SmartConnector extension without any issue for several months.
Yesterday it suddenly stopped.
I have the following error message in the ProgramData/SmartConnector/2019-04-10.log file :
2019-04-10 12:51:21.6263,Error,Service,<no principal>,Error while building type Mongoose.Service.LoggerFilterProvider. See the inner exception for details
1.) new LoggerFilterProvider()
2.) Mongoose.Service.LoggerFilterProvider
3.) Instance of SxL.Common.ILoggerFilterProvider (Mongoose.Service.LoggerFilterProvider)
4.) Container.GetInstance(SxL.Common.ILoggerFilterProvider)
Échec de la connexion pour l'utilisateur 'SmartConnector'. Raison : le mot de passe associé à ce compte a expiré.
à lambda_method(Closure , IBuildSession , IContext )
à StructureMap.Building.BuildPlan.Build(IBuildSession session, IContext context)
à StructureMap.BuildSession.BuildNewInSession(Type pluginType, Instance instance)
à StructureMap.Pipeline.NulloTransientCache.Get(Type pluginType, Instance instance, IBuildSession session)
à StructureMap.BuildSession.ResolveFromLifecycle(Type pluginType, Instance instance)
à StructureMap.SessionCache.GetObject(Type pluginType, Instance instance, ILifecycle lifecycle)
à StructureMap.SessionCache.GetDefault(Type pluginType, IPipelineGraph pipelineGraph)
à StructureMap.Container.GetInstance(Type pluginType)
à StructureMap.Container.GetInstance[T]()
à Mongoose.Service.Mongoose.OnStart(String[] args)
,[],
And I'm not able anymore to connect to smartconnectorserver.com with my credential to check the licences...
Any idea or similar issue already faced ?
Thanks.
Dimitri
Link copied. Please paste this link to share this article on your social media post.
I finnaly figuredout that this error was due to a configuration on my SQL Server side.
Indeed, the "Enforce pasword expiration" box was checked for the user (here named SmartConnector) accessing the DB
Link copied. Please paste this link to share this article on your social media post.