Hi,
We are using a SmartConnector end-point and we call the BearerToken.ObtainToken() API from our code. See the code below.
When we call this API we see an exception in the SmartConnector log file. See below and attached.
public static int ObtainBearerToken ()
{
_bearerToken = null;
try
{
// Obtain Token
Uri uri = new Uri(Settings.m_strURL);
_log.InfoFormat("ObtainBearerToken uri = '{0}', user = '{1}', pass = '{2}'", uri.ToString(), Settings.m_strUser, Settings.m_strPassword);
_bearerToken = BearerToken.ObtainToken(uri, Settings.m_strUser, Settings.m_strPassword, "GetToken");
if (_bearerToken == null)
{
_log.ErrorFormat("ObtainBearerToken fail, token is empty or null");
return -4; // invalid token
}
_log.InfoFormat("ObtainBearerToken pass, token = '{0}'", _bearerToken.ToString());
return 0;
}
catch (Exception ex)
{
_log.ErrorFormat("ObtainBearerToken, Exception, msg = '{0}'", ex.Message);
return -4;
}
}
2022-04-10 13:19:19.9006,Debug,EwsConsume,<no principal>,GetWebServiceInformation,c309cc0a-1c53-4f5f-85a0-5c95ad6d8b4b,CommunicationException Handler,{"ClassName":"System.ServiceModel.EndpointNotFoundException","Message":"There was no endpoint listening at https://10.0.0.19/EcoStruxure/DataExchange that could accept the message. This is often caused by an incorrect address or SOAP action. See InnerException, if present, for more details.","Data":null,"InnerException":{"ClassName":"System.Net.WebException","Message":"Unable to connect to the remote server","Data":null,"InnerException":{"NativeErrorCode":10060,"ClassName":"System.Net.Sockets.SocketException","Message":"A connection attempt failed because the connected party did not properly respond after a period of time, or established connection failed because connected host has failed to respond","Data":null,"InnerException":null,"HelpURL":null,"StackTraceString":" at System.Net.Sockets.Socket.DoConnect(EndPoint endPointSnapshot, SocketAddress socketAddress)\r\n at System.Net.ServicePoint.ConnectSocketInternal(Boolean connectFailure, Socket s4, Socket s6, Socket& socket, IPAddress& address, ConnectSocketState state, IAsyncResult asyncResult, Exception& exception)","RemoteStackTraceString":null,"RemoteStackIndex":0,"ExceptionMethod":"8\nDoConnect\nSystem, Version=4.0.0.0, Culture=neutral, PublicKeyToken=b77a5c561934e089\nSystem.Net.Sockets.Socket\nVoid DoConnect(System.Net.EndPoint, System.Net.SocketAddress)","HResult":-2147467259,"Source":"System","WatsonBuckets":null},"HelpURL":null,"StackTraceString":" at System.Net.HttpWebRequest.GetRequestStream(TransportContext& context)\r\n at System.Net.HttpWebRequest.GetRequestStream()\r\n at System.ServiceModel.Channels.HttpOutput.WebRequestHttpOutput.GetOutputStream()","RemoteStackTraceString":null,"RemoteStackIndex":0,"ExceptionMethod":"8\nGetRequestStream\nSystem, Version=4.0.0.0, Culture=neutral, PublicKeyToken=b77a5c561934e089\nSystem.Net.HttpWebRequest\nSystem.IO.Stream GetRequestStream(System.Net.TransportContext ByRef)","HResult":-2146233079,"Source":"System","WatsonBuckets":null},"HelpURL":null,"StackTraceString":" at System.Runtime.Remoting.Proxies.RealProxy.HandleReturnMessage(IMessage reqMsg, IMessage retMsg)\r\n at System.Runtime.Remoting.Proxies.RealProxy.PrivateInvoke(MessageData& msgData, Int32 type)\r\n at Ews.Client.IDataExchange.GetWebServiceInformation(GetWebServiceInformationRequest1 request)\r\n at Ews.Client.DataExchangeClient.Ews.Client.IDataExchange.GetWebServiceInformation(GetWebServiceInformationRequest1 request)\r\n at Ews.Client.DataExchangeClient.GetWebServiceInformation(GetWebServiceInformationRequest request)\r\n at Ews.Client.EwsClient.ExecuteAndLogCall[TRequest,TResponse](String methodName, TRequest request, Func`2 methodToLog, Boolean includeMetadata)","RemoteStackTraceString":"\r\nServer stack trace: \r\n at System.ServiceModel.Channels.HttpOutput.WebRequestHttpOutput.GetOutputStream()\r\n at System.ServiceModel.Channels.HttpOutput.Send(TimeSpan timeout)\r\n at System.ServiceModel.Channels.HttpChannelFactory`1.HttpRequestChannel.HttpChannelRequest.SendRequest(Message message, TimeSpan timeout)\r\n at System.ServiceModel.Channels.RequestChannel.Request(Message message, TimeSpan timeout)\r\n at System.ServiceModel.Dispatcher.RequestChannelBinder.Request(Message message, TimeSpan timeout)\r\n at System.ServiceModel.Channels.ServiceChannel.Call(String action, Boolean oneway, ProxyOperationRuntime operation, Object[] ins, Object[] outs, TimeSpan timeout)\r\n at System.ServiceModel.Channels.ServiceChannelProxy.InvokeService(IMethodCallMessage methodCall, ProxyOperationRuntime operation)\r\n at System.ServiceModel.Channels.ServiceChannelProxy.Invoke(IMessage message)\r\n\r\nException rethrown at [0]: \r\n","RemoteStackIndex":1,"ExceptionMethod":"8\nHandleReturnMessage\nmscorlib, Version=4.0.0.0, Culture=neutral, PublicKeyToken=b77a5c561934e089\nSystem.Runtime.Remoting.Proxies.RealProxy\nVoid HandleReturnMessage(System.Runtime.Remoting.Messaging.IMessage, System.Runtime.Remoting.Messaging.IMessage)","HResult":-2146233087,"Source":"mscorlib","WatsonBuckets":null},{"ClassName":"System.Net.WebException","Message":"Unable to connect to the remote server","Data":null,"InnerException":{"NativeErrorCode":10060,"ClassName":"System.Net.Sockets.SocketException","Message":"A connection attempt failed because the connected party did not properly respond after a period of time, or established connection failed because connected host has failed to respond","Data":null,"InnerException":null,"HelpURL":null,"StackTraceString":" at System.Net.Sockets.Socket.DoConnect(EndPoint endPointSnapshot, SocketAddress socketAddress)\r\n at System.Net.ServicePoint.ConnectSocketInternal(Boolean connectFailure, Socket s4, Socket s6, Socket& socket, IPAddress& address, ConnectSocketState state, IAsyncResult asyncResult, Exception& exception)","RemoteStackTraceString":null,"RemoteStackIndex":0,"ExceptionMethod":"8\nDoConnect\nSystem, Version=4.0.0.0, Culture=neutral, PublicKeyToken=b77a5c561934e089\nSystem.Net.Sockets.Socket\nVoid DoConnect(System.Net.EndPoint, System.Net.SocketAddress)","HResult":-2147467259,"Source":"System","WatsonBuckets":null},"HelpURL":null,"StackTraceString":" at System.Net.HttpWebRequest.GetRequestStream(TransportContext& context)\r\n at System.Net.HttpWebRequest.GetRequestStream()\r\n at System.ServiceModel.Channels.HttpOutput.WebRequestHttpOutput.GetOutputStream()","RemoteStackTraceString":null,"RemoteStackIndex":0,"ExceptionMethod":"8\nGetRequestStream\nSystem, Version=4.0.0.0, Culture=neutral, PublicKeyToken=b77a5c561934e089\nSystem.Net.HttpWebRequest\nSystem.IO.Stream GetRequestStream(System.Net.TransportContext ByRef)","HResult":-2146233079,"Source":"System","WatsonBuckets":null},,,
2022-04-10 13:19:19.9006,Error,EwsConsume,<no principal>,There was no endpoint listening at https://10.0.0.19/EcoStruxure/DataExchange that could accept the message. This is often caused by an incorrect address or SOAP action. See InnerException, if present, for more details.
Unable to connect to the remote server
A connection attempt failed because the connected party did not properly respond after a period of time, or established connection failed because connected host has failed to respond 10.0.0.19:443
Server stack trace:
at System.ServiceModel.Channels.HttpOutput.WebRequestHttpOutput.GetOutputStream()
at System.ServiceModel.Channels.HttpOutput.Send(TimeSpan timeout)
at System.ServiceModel.Channels.HttpChannelFactory`1.HttpRequestChannel.HttpChannelRequest.SendRequest(Message message, TimeSpan timeout)
at System.ServiceModel.Channels.RequestChannel.Request(Message message, TimeSpan timeout)
at System.ServiceModel.Dispatcher.RequestChannelBinder.Request(Message message, TimeSpan timeout)
at System.ServiceModel.Channels.ServiceChannel.Call(String action, Boolean oneway, ProxyOperationRuntime operation, Object[] ins, Object[] outs, TimeSpan timeout)
at System.ServiceModel.Channels.ServiceChannelProxy.InvokeService(IMethodCallMessage methodCall, ProxyOperationRuntime operation)
at System.ServiceModel.Channels.ServiceChannelProxy.Invoke(IMessage message)
Exception rethrown at [0]:
at System.Runtime.Remoting.Proxies.RealProxy.HandleReturnMessage(IMessage reqMsg, IMessage retMsg)
at System.Runtime.Remoting.Proxies.RealProxy.PrivateInvoke(MessageData& msgData, Int32 type)
at Ews.Client.IDataExchange.GetWebServiceInformation(GetWebServiceInformationRequest1 request)
at Ews.Client.DataExchangeClient.Ews.Client.IDataExchange.GetWebServiceInformation(GetWebServiceInformationRequest1 request)
at Ews.Client.DataExchangeClient.GetWebServiceInformation(GetWebServiceInformationRequest request)
at Ews.Client.EwsClient.ExecuteAndLogCall[TRequest,TResponse](String methodName, TRequest request, Func`2 methodToLog, Boolean includeMetadata)
,["GetWebServiceInformation","c309cc0a-1c53-4f5f-85a0-5c95ad6d8b4b"],
2022-04-10 13:19:19.9006,Debug,Service,<no principal>,ClientPool.CheckOutConnection for http://127.0.0.1:8019/EcoStruxure/DataExchange,
2022-04-10 13:19:19.9006,Error,Processor,<no principal>,There was no endpoint listening at https://10.0.0.19/EcoStruxure/DataExchange that could accept the message. This is often caused by an incorrect address or SOAP action. See InnerException, if present, for more details.
Unable to connect to the remote server
A connection attempt failed because the connected party did not properly respond after a period of time, or established connection failed because connected host has failed to respond 10.0.0.19:443
Server stack trace:
at System.ServiceModel.Channels.HttpOutput.WebRequestHttpOutput.GetOutputStream()
at System.ServiceModel.Channels.HttpOutput.Send(TimeSpan timeout)
at System.ServiceModel.Channels.HttpChannelFactory`1.HttpRequestChannel.HttpChannelRequest.SendRequest(Message message, TimeSpan timeout)
at System.ServiceModel.Channels.RequestChannel.Request(Message message, TimeSpan timeout)
at System.ServiceModel.Dispatcher.RequestChannelBinder.Request(Message message, TimeSpan timeout)
at System.ServiceModel.Channels.ServiceChannel.Call(String action, Boolean oneway, ProxyOperationRuntime operation, Object[] ins, Object[] outs, TimeSpan timeout)
at System.ServiceModel.Channels.ServiceChannelProxy.InvokeService(IMethodCallMessage methodCall, ProxyOperationRuntime operation)
at System.ServiceModel.Channels.ServiceChannelProxy.Invoke(IMessage message)
Exception rethrown at [0]:
at System.Runtime.Remoting.Proxies.RealProxy.HandleReturnMessage(IMessage reqMsg, IMessage retMsg)
at System.Runtime.Remoting.Proxies.RealProxy.PrivateInvoke(MessageData& msgData, Int32 type)
at Ews.Client.IDataExchange.GetWebServiceInformation(GetWebServiceInformationRequest1 request)
at Ews.Client.DataExchangeClient.Ews.Client.IDataExchange.GetWebServiceInformation(GetWebServiceInformationRequest1 request)
at Ews.Client.DataExchangeClient.GetWebServiceInformation(GetWebServiceInformationRequest request)
at Ews.Client.EwsClient.ExecuteAndLogCall[TRequest,TResponse](String methodName, TRequest request, Func`2 methodToLog, Boolean includeMetadata)
at Ews.Client.EwsClient.ExecuteAndLogCall[TRequest,TResponse](String methodName, TRequest request, Func`2 methodToLog)
at Ews.Client.EwsClient.get_EwsVersionImplemented()
at Ews.Client.EwsClient..ctor(EwsSecurity credentials, String address, EwsBindingConfig bindingConfig, Nullable`1 compatibilityVersion)
at Ews.Client.EwsClient..ctor(IEndpoint endpoint, Nullable`1 compatibilityVersion)
at Mongoose.Service.Cache.CachedEwsClient..ctor(String poolKey, IEndpoint endpoint)
at Mongoose.Service.Cache.EwsClientPool.CreateNewInstance(String poolKey, IEndpoint endpoint)
at Mongoose.Service.Cache.ClientPool`3.<>c__DisplayClass5_0.<CheckOutConnection>b__0()
at Mongoose.Service.Cache.ThreadSafeDisposableBase.ThreadSafeCall[T](Func`1 callback)
at Mongoose.Service.Cache.ClientPool`3.CheckOutConnection(TEndpoint endpoint)
at Mongoose.Service.Cache.ManagedEwsClient.ManageCall[T](IEndpoint endpoint, Func`2 method, Nullable`1 callVersion)
at Mongoose.Service.Cache.ManagedEwsClient.GetAlarmEvents(IEndpoint endpoint, Nullable`1 priorityFrom, Nullable`1 priorityTo, String moreDataRef, String[] types, Nullable`1 callVersion)
at Mongoose.Process.Ews.AlarmItemReader.ReadData()
,[],
Any idea what causes the exception?
Thank you.
Mike
Hi,
A connection attempt failed because the connected party did not properly respond after a period of time, or established connection failed because connected host has failed to respond 10.0.0.19:443
Is there a EWS enabled EBO server configured to listen to at http://10.0.0.19:443/EcoStruxure/DataExchange?
Hi,
We use HTTP URL not HTTPS.
Our IP address was changed from 10.0.0.19:8019 to 10.0.0.18:8019. Why does SmartConnector tries to connect to the HTTPS URL instead of HTTP URL?
In any case, SmartConnector should not crash...
Thank you.
Mike
Hello,
Please restart the service and post screenshots of all your REST endpoint configurations.
BR
Armend
Hi Mike,
EBO is configured to redirect all HTTP requests to HTTPS by default. You need to uncheck this in the EBO configuration. You may have done this already but it usually catches people out when creating a HTTP endpoint.
Hi Steve,
Thanks. This property is unchecked in the EBO.
Mike