Sign In Help
Schneider Electric
HelpSign In
Schneider Electric Exchange
  • Home
  • Collaborate
  • Develop
  • Shop
Home Collaborate Develop Shop Log in or Register Help

Invite a Co-worker

Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel

Invitation Sent

Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
  • Home
  • Collaborate
  • Exchange Community
  • :
  • SCADA & Telemetry Solutions
  • :
  • SCADA and Telemetry Devices Ideas
  • :
  • SCADAPack 575 Partial Downloads for Slow Radio Networks
Community Menu
  • Forums
    • By Topic
        • EcoStruxure IT
          • EcoStruxure IT forum
        • Industrial Automation
          • Industry Automation and Control Forum
          • Alliance System Integrators Forum
          • Machine Solutions in the Digital Transformation
          • EcoStruxure Automation Expert / IEC 61499 Forum
          • Industrial Edge Computing Forum
          • Level and Pressure Instrumentation Forum
          • Modicon User Group
          • PLC Club Indonesia
          • SEE Automation Club Forum
          • Fabrika ve Makina Otomasyonu Çözümleri
          • Форум по промышленной автоматизации СНГ
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Forum
          • SCADA and Telemetry Devices Forum
        • Power Distribution IEC
          • Power Distribution and Digital
          • Power Standards & Regulations
          • Paneelbouw & Energie Distributie
        • Power Distribution Softwares
          • EcoStruxure Power Design Forum
          • SEE Electrical Building+ Forum
          • LayoutFAST User Group Forum
        • Solutions for your Business
          • Solutions for Food & Beverage Forum
          • Solutions for Healthcare Forum
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Forum
        • Healthcare
          • Solutions for Healthcare Forum
      • EcoStruxure IT
        • EcoStruxure IT forum
      • Industrial Automation
        • Industry Automation and Control Forum
        • Alliance System Integrators Forum
        • Machine Solutions in the Digital Transformation
        • EcoStruxure Automation Expert / IEC 61499 Forum
        • Industrial Edge Computing Forum
        • Level and Pressure Instrumentation Forum
        • Modicon User Group
        • PLC Club Indonesia
        • SEE Automation Club Forum
        • Fabrika ve Makina Otomasyonu Çözümleri
        • Форум по промышленной автоматизации СНГ
      • SCADA & Telemetry Solutions
        • Geo SCADA Expert Forum
        • SCADA and Telemetry Devices Forum
      • Power Distribution IEC
        • Power Distribution and Digital
        • Power Standards & Regulations
        • Paneelbouw & Energie Distributie
      • Power Distribution Softwares
        • EcoStruxure Power Design Forum
        • SEE Electrical Building+ Forum
        • LayoutFAST User Group Forum
      • Solutions for your Business
        • Solutions for Food & Beverage Forum
        • Solutions for Healthcare Forum
      • Food & Beverage
        • Solutions for Food & Beverage Forum
      • Healthcare
        • Solutions for Healthcare Forum
  • Blogs
    • By Topic
        • Industrial Automation
          • Industrial Edge Computing Blog
          • Industry 4.0 Blog
          • Industrie du Futur France
        • SCADA & Telemetry Solutions
          • SCADA and Telemetry Blog
        • Power Distribution IEC
          • Power Events & Webinars
          • Power Foundations Blog
        • Power Distribution NEMA
          • NEMA Power Foundations Blog
        • Power Distribution Softwares
          • EcoStruxure Power Design Blog
          • SEE Electrical Building+ Blog
        • Solutions for your Business
          • Solutions for Food & Beverage Blog
          • Solutions for Healthcare Blog
          • Solutions for Retail Blog
        • Community experts & publishers
          • Publishers Community
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Blog
        • Healthcare
          • Solutions for Healthcare Blog
        • Retail
          • Solutions for Retail Blog
      • Industrial Automation
        • Industrial Edge Computing Blog
        • Industry 4.0 Blog
        • Industrie du Futur France
      • SCADA & Telemetry Solutions
        • SCADA and Telemetry Blog
      • Power Distribution IEC
        • Power Events & Webinars
        • Power Foundations Blog
      • Power Distribution NEMA
        • NEMA Power Foundations Blog
      • Power Distribution Softwares
        • EcoStruxure Power Design Blog
        • SEE Electrical Building+ Blog
      • Solutions for your Business
        • Solutions for Food & Beverage Blog
        • Solutions for Healthcare Blog
        • Solutions for Retail Blog
      • Community experts & publishers
        • Publishers Community
      • Food & Beverage
        • Solutions for Food & Beverage Blog
      • Healthcare
        • Solutions for Healthcare Blog
      • Retail
        • Solutions for Retail Blog
  • Ideas
        • Industrial Automation
          • Modicon Ideas & new features
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Ideas
          • SCADA and Telemetry Devices Ideas
  • Knowledge Center
    • Building Automation Knowledge Base
    • Industrial Automation How-to videos
    • Ask Exchange
    • Digital E-books
    • Success Stories Corner
    • Power Talks
  • Events & Webinars
  • Support
    • User Guide
    • Leaderboard
    • Releases Notes
How can we help?
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
49672members
Join Now
243100posts
Join Now

SCADAPack 575 Partial Downloads for Slow Radio Networks

Options
  • Subscribe to RSS Feed
  • Mark as New
  • Mark as Read
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
2 Likes

SCADAPack 575 Partial Downloads for Slow Radio Networks

Status: Under consideration Submitted by Lieutenant JG Teaan on ‎2020-11-05 07:01 PM
7 Comments (7 New)

Hi,

 

When creating large configuration for the SCADAPack 5X and probably the SCADAPack 4X it is near impossible to download the configuration over a slow communication link such as a radio network consisting of Trio M450 or similar radios. This situation is worsened if the radio network has a high utilization. Currently if a sizeable configuration with logic needs to be downloaded over a serial connection of 9600bps it take upward of 25 minutes to download with a direct serial cable link and therefore the probability of failure over a radio network with 4800bps bandwidth is extremely high

 

A suggestion would be to allow for partial downloads to the SCADAPack. This would be suggested from Geo SCADA Expert as well as from Remote Connect. 

 

A staged download might be suggested where changes on different parts of the configuration can be indicated and only those changes downloaded to the RTU. As an example if an analog tag is added or changed then only the addition of the tag is added or if the logic is changed then only the logic is transferred. 

 

The same process can be followed with an upload which sufferers from the same problems as download. In this instance an upload can again be divided into different sections. Each section is downloaded and verified. Therefore if an upload should fail and sections have already been uploaded and completed. These are flagged as completed successfully and won't be uploaded again except if explicitly requested by the user.

 

Regards

Teaan

Tags (7)
  • Find more ideas tagged with:
  • english
  • Partial Download
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Labels (2)
See more ideas labeled with:
  • Geo SCADA Expert
  • SCADAPack
Comment
Share
  • Back to Idea Exchange
  • Previous
  • Next
7 Comments
MartinChartrand
Lt. Commander MartinChartrand Lt. Commander
Lt. Commander
‎2020-11-06 04:53 AM
  • Mark as Read
  • Mark as New
  • Bookmark
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-11-06 04:53 AM
Status changed to: Under consideration

@Teaan Thank you for your clear description of your challenge as well taking the time to come up with a solution.

I will bring this up at the next product team meeting and let the community know what our thoughts are on your idea.

Regards,

Martin

Teaan
Lieutenant JG Teaan
Lieutenant JG
‎2020-11-09 04:58 AM
  • Mark as Read
  • Mark as New
  • Bookmark
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-11-09 04:58 AM

@MartinChartrand thank you very much I appreciate it.

 

Regards

Teaan van Staden

MartinChartrand
Lt. Commander MartinChartrand Lt. Commander
Lt. Commander
‎2020-11-12 11:49 AM
  • Mark as Read
  • Mark as New
  • Bookmark
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-11-12 11:49 AM

Hello again,

We're investigating further and will keep the community apprised of any news as it becomes available. Again, thanks for your comments.

Martin

Teaan
Lieutenant JG Teaan
Lieutenant JG
‎2020-12-16 11:02 PM
  • Mark as Read
  • Mark as New
  • Bookmark
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-12-16 11:02 PM

Hi Martin,

 

Just following up and if there might be any feedback regarding the partial downloads yet?

 

Regards

Teaan

MartinChartrand
Lt. Commander MartinChartrand Lt. Commander
Lt. Commander
‎2020-12-17 04:22 AM
  • Mark as Read
  • Mark as New
  • Bookmark
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-12-17 04:22 AM

Hi Teaan,

Thank you for following up. Your idea was discussed at the last SCADAPack product meeting and is still being considered. I will be reviewing it again with the team at the next meeting in January and will hopefully have a more concrete answer for you then.

Have a safe and happy New Year.

Regards,

Martin

Teaan
Lieutenant JG Teaan
Lieutenant JG
‎2020-12-17 06:55 AM
  • Mark as Read
  • Mark as New
  • Bookmark
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-12-17 06:55 AM

Hi Martin,

 

Thank you so much for the feedback. I will follow up again end of January.

 

Regards

Teaan

BevanWeiss
Admiral BevanWeiss
Admiral
‎2020-12-17 02:32 PM
  • Mark as Read
  • Mark as New
  • Bookmark
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-12-17 02:32 PM

I really like the idea of being able to make 'live' changes to the configuration.

 

For example, when tuning DNP3 event deadbands etc, it would be incredibly useful if when connected ONLINE, making a change and applying it here was the same as in the Logic Editor.. and it was sent as a change to the RTU itself, so that the new setting would take effect immediately (without having to do a full 'Write to Device' with the logic restarting etc).

Comment
Preview Exit Preview

never-displayed

Hint:
@ links to members, content
 
  • Back to Idea Exchange
  • Previous
  • Next
Labels
  • Geo SCADA Expert 1
  • SCADAPack 2
Idea Statuses
  • Submitted 0
  • Under consideration 4
  • Accepted 0
  • Declined 0
  • Partially delivered 0
  • Fully delivered 0
  • Abandoned 0
Top Liked Authors
User Likes Count
BevanWeiss
Admiral BevanWeiss
1
View All
Support

Have a question? Please contact us with details, and we will respond.

Contact Us
FAQ

Look through existing questions to find popular answers.

Learn More
About

Want to know more about Exchange and its possibilities?

Learn More

Full access is just steps away!

Join Exchange for FREE and get unlimited access to our global community of experts.

Connect with Peers & Experts

Discuss challenges in energy and automation with 30,000+ experts and peers.

Get Support in Our Knowledge Base

Find answers in 10,000+ support articles to help solve your product and business challenges.

Ask Questions. Give Solutions

Find peer based solutions to your questions. Provide answers for fellow community members!

Register today for FREE

Register Now

Already have an account?Log in

About Us FAQ Terms & Conditions Privacy Notice Change your cookie settings
©2020, Schneider Electric