Sign In Help
Schneider Electric
HelpSign In
Schneider Electric Exchange
  • Home
  • Collaborate
  • Develop
  • Shop
Home Collaborate Develop Shop Log in or Register Help

Invite a Co-worker

Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel

Invitation Sent

Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
  • Home
  • Collaborate
  • Exchange Community
  • :
  • SCADA & Telemetry Solutions
  • :
  • SCADA and Telemetry Devices Forum
  • :
  • Trio eDiags implemented quite differently between J-series and Q-series radios
Community Menu
  • Forums
    • By Topic
        • EcoStruxure IT
          • EcoStruxure IT forum
        • Industrial Automation
          • Industry Automation and Control Forum
          • Alliance System Integrators Forum
          • Machine Solutions in the Digital Transformation
          • EcoStruxure Automation Expert / IEC 61499 Forum
          • Industrial Edge Computing Forum
          • Level and Pressure Instrumentation Forum
          • Modicon User Group
          • PLC Club Indonesia
          • SEE Automation Club Forum
          • Fabrika ve Makina Otomasyonu Çözümleri
          • Форум по промышленной автоматизации СНГ
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Forum
          • SCADA and Telemetry Devices Forum
        • Power Distribution IEC
          • Power Distribution and Digital
          • Power Standards & Regulations
          • Paneelbouw & Energie Distributie
        • Power Distribution Softwares
          • EcoStruxure Power Design Forum
          • SEE Electrical Building+ Forum
          • LayoutFAST User Group Forum
        • Wireless Information Network Solutions
          • Instrument Area Network
          • Remote Monitoring
          • Tank Level Monitoring
          • Remote Data Collection
        • Solutions for your Business
          • Solutions for Food & Beverage Forum
          • Solutions for Healthcare Forum
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Forum
        • Healthcare
          • Solutions for Healthcare Forum
      • EcoStruxure IT
        • EcoStruxure IT forum
      • Industrial Automation
        • Industry Automation and Control Forum
        • Alliance System Integrators Forum
        • Machine Solutions in the Digital Transformation
        • EcoStruxure Automation Expert / IEC 61499 Forum
        • Industrial Edge Computing Forum
        • Level and Pressure Instrumentation Forum
        • Modicon User Group
        • PLC Club Indonesia
        • SEE Automation Club Forum
        • Fabrika ve Makina Otomasyonu Çözümleri
        • Форум по промышленной автоматизации СНГ
      • SCADA & Telemetry Solutions
        • Geo SCADA Expert Forum
        • SCADA and Telemetry Devices Forum
      • Power Distribution IEC
        • Power Distribution and Digital
        • Power Standards & Regulations
        • Paneelbouw & Energie Distributie
      • Power Distribution Softwares
        • EcoStruxure Power Design Forum
        • SEE Electrical Building+ Forum
        • LayoutFAST User Group Forum
      • Wireless Information Network Solutions
        • Instrument Area Network
        • Remote Monitoring
        • Tank Level Monitoring
        • Remote Data Collection
      • Solutions for your Business
        • Solutions for Food & Beverage Forum
        • Solutions for Healthcare Forum
      • Food & Beverage
        • Solutions for Food & Beverage Forum
      • Healthcare
        • Solutions for Healthcare Forum
  • Blogs
    • By Topic
        • Industrial Automation
          • Industrial Edge Computing Blog
          • Industry 4.0 Blog
          • Industrie du Futur France
        • SCADA & Telemetry Solutions
          • SCADA and Telemetry Blog
        • Power Distribution IEC
          • Power Events & Webinars
          • Power Foundations Blog
        • Power Distribution NEMA
          • NEMA Power Foundations Blog
        • Power Distribution Softwares
          • EcoStruxure Power Design Blog
          • SEE Electrical Building+ Blog
        • Solutions for your Business
          • Solutions for Food & Beverage Blog
          • Solutions for Healthcare Blog
          • Solutions for Retail Blog
        • Community experts & publishers
          • Publishers Community
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Blog
        • Healthcare
          • Solutions for Healthcare Blog
        • Retail
          • Solutions for Retail Blog
      • Industrial Automation
        • Industrial Edge Computing Blog
        • Industry 4.0 Blog
        • Industrie du Futur France
      • SCADA & Telemetry Solutions
        • SCADA and Telemetry Blog
      • Power Distribution IEC
        • Power Events & Webinars
        • Power Foundations Blog
      • Power Distribution NEMA
        • NEMA Power Foundations Blog
      • Power Distribution Softwares
        • EcoStruxure Power Design Blog
        • SEE Electrical Building+ Blog
      • Solutions for your Business
        • Solutions for Food & Beverage Blog
        • Solutions for Healthcare Blog
        • Solutions for Retail Blog
      • Community experts & publishers
        • Publishers Community
      • Food & Beverage
        • Solutions for Food & Beverage Blog
      • Healthcare
        • Solutions for Healthcare Blog
      • Retail
        • Solutions for Retail Blog
  • Ideas
        • Industrial Automation
          • Modicon Ideas & new features
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Ideas
          • SCADA and Telemetry Devices Ideas
  • Knowledge Center
    • Building Automation Knowledge Base
    • Industrial Automation Knowledge Base
    • Industrial Automation How-to videos
    • SCADA & Telemetry Solutions Knowledge Base
    • Digital E-books
    • Success Stories Corner
    • Power Talks
  • Events & Webinars
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Technology Partners
  • Support
    • Ask Exchange
    • Leaderboard
    • Our Community Guidelines
    • Community User Guide
    • How-To & Best Practices
    • More
Join Now
How can we help?
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
51021members
Join Now
245069posts
Join Now

Trio eDiags implemented quite differently between J-series and Q-series radios

Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Solved Go to Solution
Back to SCADA and Telemetry Devices Forum
Solved
BevanWeiss
Admiral BevanWeiss
Admiral
‎2020-07-07 07:10 PM
0 Likes
5
1390
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-07 07:10 PM

Trio eDiags implemented quite differently between J-series and Q-series radios

Hi,

I've recently been configuring some Q-series radios for Trio eDiags to GeoSCADA Expert.

 

Is there an explanation for why the Trio J-series radios allow for retrieval of the eDiags from the Diagnostic Entry Point radio, but for Q-series radios each radio needs to be polled individually for the eDiags?  It feels like polling each radio individually will take up more network traffic than if just an entry point radio can retain these records and be polled for this without additional network traffic.

 

I assume it likely has to do with the target network sizes, where a J-series network is anticipated to be 'smaller' (less nodes) than a Q-series network.  Or perhaps related to the overall bandwidth being less on the Q-series, and hence more fine grained control over the network traffic related to diagnostics being desirable.  But it would be nice to know in any case.

 


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..

Solved! Go to Solution.

Labels
  • Radio
Tags (1)
  • Tags:
  • english
Share
Reply

Accepted Solutions
Joel_Weder
Lieutenant Joel_Weder Lieutenant
Lieutenant
‎2020-07-08 11:36 AM
0 Likes
4
1379
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-08 11:36 AM

Re: Trio eDiags implemented quite differently between J-series and Q-series radios

Hello @BevanWeiss 

 

Trio did indeed modify the eDiagnostics protocol when creating the newer Q Series. With J Series, if a technician wishes to perform diagnostic polling of the network from a radio other than the current eDiags Gateway radio, they must disable that gateway first and then enable the gateway feature in the radio they are connected to. This can be logistically challenging and time-consuming. Instead, with Q Series the maintenance staff can connect to any radio in the system and initiate system-wide polling without any re-configuration required.


Also, with the newer eDiags implementation, the building of a configuration in Geo SCADA to monitor Trio Q radios is accomplished very much as is done when adding a SCADAPack RTU or other device. One UDP channel per radio network, one Set, radios as outstations each with own IP and serial number, then whatever points you wish to monitor.


Note that a J Series radio configured as the eDiags Gateway does not store diagnostic data from other radios. It simply converts the Ethernet eDiags polls to the appropriate over-the-air protocol and sends them out. Each radio being polled will respond only to diagnostic messages sent over-the-air to its serial number. The Gateway radio then converts these messages back to the LAN eDiags protocol and sends them to TView+ Diagnostics or Geo SCADA, without storing them other than momentarily in its Rx buffer. The radio system must transport a diagnostic poll and response for each JR radio, just as it does for each Q radio.

 

I have attached three simple documents summarizing how to set up eDiags for both J Series and Q Series radios, both with TView+ Diagnostics and with Geo SCADA, for anyone who may wish to do this. Also attached is a Geo SCADA database which can be used as the starting point for a Trio monitoring system.

 

Joel Weder
Telemetry Solutions Specialist
Schneider Electric

See Answer In Context

Attachments
Trio Diagnostics Documents.zip
Tags (1)
  • Tags:
  • english
Share
Reply
Joel_Weder
Lieutenant Joel_Weder Lieutenant
Lieutenant
‎2020-07-14 12:43 PM
0 Likes
0
1321
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-14 12:43 PM

Re: Trio eDiags implemented quite differently between J-series and Q-series radios

@BevanWeiss  We have investigated this issue and you're correct that PIC 190 has for some reason been removed from the list of available diagnostic parameters in Geo SCADA. We feel this may be an error and Trio product management team will pursue it.

 

As a related matter, I've received approval to post PIC lists for the newer Q Series radios as well as the older E Series. These lists are attached. Please note however that these lists are static documents, while the Trio offer does change over time. 

 

Joel Weder
Telemetry Solutions Specialist
Schneider Electric

See Answer In Context

Attachments
Tags (1)
  • Tags:
  • english
Share
Reply
  • All forum topics
  • Previous Topic
  • Next Topic
5 Replies 5
Joel_Weder
Lieutenant Joel_Weder Lieutenant
Lieutenant
‎2020-07-08 11:36 AM
0 Likes
4
1380
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-08 11:36 AM

Re: Trio eDiags implemented quite differently between J-series and Q-series radios

Hello @BevanWeiss 

 

Trio did indeed modify the eDiagnostics protocol when creating the newer Q Series. With J Series, if a technician wishes to perform diagnostic polling of the network from a radio other than the current eDiags Gateway radio, they must disable that gateway first and then enable the gateway feature in the radio they are connected to. This can be logistically challenging and time-consuming. Instead, with Q Series the maintenance staff can connect to any radio in the system and initiate system-wide polling without any re-configuration required.


Also, with the newer eDiags implementation, the building of a configuration in Geo SCADA to monitor Trio Q radios is accomplished very much as is done when adding a SCADAPack RTU or other device. One UDP channel per radio network, one Set, radios as outstations each with own IP and serial number, then whatever points you wish to monitor.


Note that a J Series radio configured as the eDiags Gateway does not store diagnostic data from other radios. It simply converts the Ethernet eDiags polls to the appropriate over-the-air protocol and sends them out. Each radio being polled will respond only to diagnostic messages sent over-the-air to its serial number. The Gateway radio then converts these messages back to the LAN eDiags protocol and sends them to TView+ Diagnostics or Geo SCADA, without storing them other than momentarily in its Rx buffer. The radio system must transport a diagnostic poll and response for each JR radio, just as it does for each Q radio.

 

I have attached three simple documents summarizing how to set up eDiags for both J Series and Q Series radios, both with TView+ Diagnostics and with Geo SCADA, for anyone who may wish to do this. Also attached is a Geo SCADA database which can be used as the starting point for a Trio monitoring system.

 

Joel Weder
Telemetry Solutions Specialist
Schneider Electric

See Answer In Context

Attachments
Trio Diagnostics Documents.zip
Tags (1)
  • Tags:
  • english
Share
Reply
BevanWeiss
Admiral BevanWeiss
Admiral
‎2020-07-08 10:13 PM
0 Likes
3
1363
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-08 10:13 PM

Re: Trio eDiags implemented quite differently between J-series and Q-series radios

Thanks Joel,

 

I assume that the over-the-air datasize of a Trio native Diagnostic Frame (like would be sent from the Diagnostic Entry Point JR radio) and a UDP wrapped eDiag frame (like would traverse for the Qx radio configuration) are not grossly dissimilar?

 

Are you also the person in the know in regards to PICs?

It's been a real struggle to find a definitive list of what PICs are available across different radio models, and different radio firmwares.

 

One simple example that has come up recently is in regards to the string PIC 190, which used to be the Firmware version.

I've been advised that this particular PIC has been deprecated, but there doesn't appear to be an equivalent replacement for it that is nice and human (operator) readable.


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..
Tags (1)
  • Tags:
  • english
Share
Reply
Joel_Weder
Lieutenant Joel_Weder Lieutenant
Lieutenant
‎2020-07-10 07:51 AM
0 Likes
2
1340
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-10 07:51 AM

Re: Trio eDiags implemented quite differently between J-series and Q-series radios

@BevanWeiss   I did a bit of testing yesterday with Geo SCADA 2019. PIC 190 is still available in that version, and worked well to poll the firmware version from a QR150 running beta firmware 2.4.0. 

 

On a related note, I've sent an email to Luke Enriquez and John Snopek to see if we can release a complete PIC list, and will share it if so.

 

Joel Weder
Telemetry Solutions Specialist
Schneider Electric
Tags (1)
  • Tags:
  • english
Share
Reply
BevanWeiss
Admiral BevanWeiss
Admiral
‎2020-07-10 08:47 PM
0 Likes
1
1333
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-10 08:47 PM

Re: Trio eDiags implemented quite differently between J-series and Q-series radios

@Joel_Weder What version of GeoSCADA 2019? 😉

I believe this is a very recent change (as of May 2020 Update) to remove PIC 190 from the String point list

 

Whilst I do have it working under GeoSCADA 2019 May 2020 very well... I've had to manually type in the PIC 190 rather than selecting it from the drop down, and have been advised by GeoSCADA Tech Support that this is due to the Trio team advising this PIC was deprecated, and should not be utilised moving forward.

 

You can see below that it's not in the auto-pick drop down... I've had to manually define it.

2020-07-11 13_45_48-ViewX.png


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..
Tags (1)
  • Tags:
  • english
Share
Reply
Joel_Weder
Lieutenant Joel_Weder Lieutenant
Lieutenant
‎2020-07-14 12:43 PM
0 Likes
0
1322
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-14 12:43 PM

Re: Trio eDiags implemented quite differently between J-series and Q-series radios

@BevanWeiss  We have investigated this issue and you're correct that PIC 190 has for some reason been removed from the list of available diagnostic parameters in Geo SCADA. We feel this may be an error and Trio product management team will pursue it.

 

As a related matter, I've received approval to post PIC lists for the newer Q Series radios as well as the older E Series. These lists are attached. Please note however that these lists are static documents, while the Trio offer does change over time. 

 

Joel Weder
Telemetry Solutions Specialist
Schneider Electric

See Answer In Context

Attachments
Tags (1)
  • Tags:
  • english
Share
Reply
Related Products
Schneider Electric
Trio Licensed Radios
Top Experts
User Count
sbeadle
Sisko sbeadle Sisko
15
Joel_Weder
Lieutenant Joel_Weder Lieutenant
11
MartinChartrand
Lt. Commander MartinChartrand Lt. Commander
7
Jimi
Lt. Commander Jimi Lt. Commander
3
BevanWeiss
Admiral BevanWeiss
3
See More Top Experts
Find a Service Provider
Find a certified partner to help you address your integration, installation, maintenance and project needs.
View all Providers
Support

Have a question? Please contact us with details, and we will respond.

Contact Us
FAQ

Look through existing questions to find popular answers.

Learn More
About

Want to know more about Exchange and its possibilities?

Learn More

Full access is just steps away!

Join Exchange for FREE and get unlimited access to our global community of experts.

Connect with Peers & Experts

Discuss challenges in energy and automation with 30,000+ experts and peers.

Get Support in Our Knowledge Base

Find answers in 10,000+ support articles to help solve your product and business challenges.

Ask Questions. Give Solutions

Find peer based solutions to your questions. Provide answers for fellow community members!

Register today for FREE

Register Now

Already have an account?Log in

About Us FAQ Terms & Conditions Privacy Notice Change your cookie settings
©2020, Schneider Electric