Sign In Help
Schneider Electric
HelpLogin / Register

Invite a Co-worker

Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel

Invitation Sent

Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
  • Home
  • Communities
  • :
  • SCADA & Telemetry Solutions
  • :
  • SCADA and Telemetry Devices Forum
  • :
  • T_SPx70 Data Types
Community Menu
  • Forums
    • By Topic
        • EcoStruxure Building
          • Field Devices Forum
        • EcoStruxure Power & Grid
          • Metering & Power Quality
        • EcoStruxure IT
          • EcoStruxure IT forum
        • Industrial Automation
          • Industry Automation and Control Forum
          • Alliance System Integrators Forum
          • Machine Automation Forum
          • EcoStruxure Automation Expert / IEC 61499 Forum
          • Industrial Edge Computing Forum
          • Level and Pressure Instrumentation Forum
          • Modicon User Group
          • PLC Club Indonesia
          • SEE Automation Club Forum
          • Fabrika ve Makina Otomasyonu Çözümleri
          • Форум по промышленной автоматизации СНГ
          • Motorabgangstechnik & Antriebstechnik Forum
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Forum
          • SCADA and Telemetry Devices Forum
        • Power Distribution IEC
          • Power Distribution and Digital
          • Power Standards & Regulations
          • Solutions for Motor Management
          • Paneelbouw & Energie Distributie
          • Eldistribution & Fastighetsautomation
          • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
        • Power Distribution NEMA
          • US Utility Forum
        • Power Distribution Softwares
          • EcoStruxure Power Design Forum
          • LayoutFAST User Group Forum
        • Wireless Information Network Solutions
          • Instrument Area Network
          • Remote Monitoring
          • Tank Level Monitoring
          • Remote Data Collection
        • Solutions for your Business
          • Solutions for Food & Beverage Forum
          • Solutions for Healthcare Forum
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Forum
        • Healthcare
          • Solutions for Healthcare Forum
      • EcoStruxure Building
        • Field Devices Forum
      • EcoStruxure Power & Grid
        • Metering & Power Quality
      • EcoStruxure IT
        • EcoStruxure IT forum
      • Industrial Automation
        • Industry Automation and Control Forum
        • Alliance System Integrators Forum
        • Machine Automation Forum
        • EcoStruxure Automation Expert / IEC 61499 Forum
        • Industrial Edge Computing Forum
        • Level and Pressure Instrumentation Forum
        • Modicon User Group
        • PLC Club Indonesia
        • SEE Automation Club Forum
        • Fabrika ve Makina Otomasyonu Çözümleri
        • Форум по промышленной автоматизации СНГ
        • Motorabgangstechnik & Antriebstechnik Forum
      • SCADA & Telemetry Solutions
        • Geo SCADA Expert Forum
        • SCADA and Telemetry Devices Forum
      • Power Distribution IEC
        • Power Distribution and Digital
        • Power Standards & Regulations
        • Solutions for Motor Management
        • Paneelbouw & Energie Distributie
        • Eldistribution & Fastighetsautomation
        • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
      • Power Distribution NEMA
        • US Utility Forum
      • Power Distribution Softwares
        • EcoStruxure Power Design Forum
        • LayoutFAST User Group Forum
      • Wireless Information Network Solutions
        • Instrument Area Network
        • Remote Monitoring
        • Tank Level Monitoring
        • Remote Data Collection
      • Solutions for your Business
        • Solutions for Food & Beverage Forum
        • Solutions for Healthcare Forum
      • Food & Beverage
        • Solutions for Food & Beverage Forum
      • Healthcare
        • Solutions for Healthcare Forum
  • Blogs
    • By Topic
        • EcoStruxure Power & Grid
          • Backstage Access Resources
        • Industrial Automation
          • Industry 4.0 Blog
          • Industrie du Futur France
        • SCADA & Telemetry Solutions
          • SCADA and Telemetry Blog
        • Power Distribution IEC
          • Power Events & Webinars
          • Power Foundations Blog
          • UK&I Residential and Commercial Electrical Distribution
        • Power Distribution NEMA
          • NEMA Power Foundations Blog
        • Power Distribution Softwares
          • EcoStruxure Power Design Blog
        • Solutions for your Business
          • Solutions for Food & Beverage Blog
          • Solutions for Healthcare Blog
          • Solutions for Retail Blog
          • Solutions for eMobility
          • Digital Hospital Solutions – UK&I
        • Knowledge Center
          • Industrial Automation How-to videos
          • Digital E-books
          • Success Stories Corner
        • Community experts & publishers
          • Publishers Community
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Blog
        • Healthcare
          • Solutions for Healthcare Blog
        • Retail
          • Solutions for Retail Blog
        • Retail
          • Solutions for eMobility
        • Retail
          • Digital Hospital Solutions – UK&I
      • EcoStruxure Power & Grid
        • Backstage Access Resources
      • Industrial Automation
        • Industry 4.0 Blog
        • Industrie du Futur France
      • SCADA & Telemetry Solutions
        • SCADA and Telemetry Blog
      • Power Distribution IEC
        • Power Events & Webinars
        • Power Foundations Blog
        • UK&I Residential and Commercial Electrical Distribution
      • Power Distribution NEMA
        • NEMA Power Foundations Blog
      • Power Distribution Softwares
        • EcoStruxure Power Design Blog
      • Solutions for your Business
        • Solutions for Food & Beverage Blog
        • Solutions for Healthcare Blog
        • Solutions for Retail Blog
        • Solutions for eMobility
        • Digital Hospital Solutions – UK&I
      • Knowledge Center
        • Industrial Automation How-to videos
        • Digital E-books
        • Success Stories Corner
      • Community experts & publishers
        • Publishers Community
      • Food & Beverage
        • Solutions for Food & Beverage Blog
      • Healthcare
        • Solutions for Healthcare Blog
      • Retail
        • Solutions for Retail Blog
      • Retail
        • Solutions for eMobility
      • Retail
        • Digital Hospital Solutions – UK&I
  • Ideas
        • Industrial Automation
          • Modicon Ideas & new features
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Ideas
          • SCADA and Telemetry Devices Ideas
  • Knowledge Center
    • Building Automation Knowledge Base
    • Industrial Automation Knowledge Base
    • Industrial Automation How-to videos
    • SCADA & Telemetry Solutions Knowledge Base
    • Digital E-books
    • Success Stories Corner
    • Power Talks
  • Events & Webinars
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Technology Partners
  • Support
    • Ask Exchange
    • Leaderboard
    • Our Community Guidelines
    • Community User Guide
    • How-To & Best Practices
    • More
Join Now
How can we help?
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
52874members
Join Now
248224posts
Join Now

T_SPx70 Data Types

Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Solved Go to Solution
Back to SCADA and Telemetry Devices Forum
Solved
SCADAPro52
Ensign SCADAPro52
Ensign
‎2020-12-02 11:53 AM
0 Likes
5
694
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-12-02 11:53 AM

T_SPx70 Data Types

Can the alarm setpoints on a T_SPx70_Analog point be changed programmatically i.e. via logic? Unable to find an answer in the documentation.

45+ years in SCADA & ICS and still learning every day!
Labels
  • Logic
  • RTU
  • SCADA
Tags (7)
  • Tags:
  • english
  • RenoteConnect
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Share
Reply

Accepted Solutions
Joel_Weder
Lieutenant Joel_Weder Lieutenant
Lieutenant
‎2020-12-03 07:46 AM
0 Likes
1
659
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-12-03 07:46 AM

Re: T_SPx70 Data Types

Hi SCADAPro52,

 

As pointed out by Alastair after my first post, I was incorrect in saying that a Modbus or DNP3 address could be assigned to an attribute of an object directly. It can be done via other means, which I'll mention in a moment. But in fact what you can do is assign a DNP3 or Modbus address to the object as a whole.

 

After creating a new Project in RemoteConnect with the appropriate options, you go to the Objects tab and then Object Configuration. Scroll down to the analog object in question and double-click on it. Set the object to be a T_SPx70_ADV_ANALOG type, then a bit further down in the same window click on the DNP3 (or Modbus) tab for that object. After assigning a point number, you can configure the DNP3 Group & Variation, and a data class.

 

I missed one item regarding how to write to an attribute remotely. What I'd do is create a new object with a DNP3 point #, just for external communication, that can be written to by a DNP3 SCADA host or HMI. Then add a bit of logic to copy that value to the level attribute.  It would be accessed as (for example) PIO_SP575_AI1.L1_LIMIT

 

Joel Weder
Telemetry Solutions Specialist
Schneider Electric

See Answer In Context

Tags (6)
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Share
Reply
  • All forum topics
  • Previous Topic
  • Next Topic
5 Replies 5
Joel_Weder
Lieutenant Joel_Weder Lieutenant
Lieutenant
‎2020-12-02 03:03 PM
0 Likes
3
688
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-12-02 03:03 PM

Re: T_SPx70 Data Types

Hello SCADAPro52,

 

Yes, it certainly is possible to write to the configurable limits which are attributes of the  T_SPx70_Adv_Analog objects. These can be set initially on the Alert Notifications tab for an advanced analog object, but those initial values often need to change. You can also assign a Modbus or DNP3 register to these attributes, so you can write to them remotely.

 

Joel Weder
Telemetry Solutions Specialist
Schneider Electric
Tags (6)
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Share
Reply
AlastairF
Lieutenant JG AlastairF Lieutenant JG
Lieutenant JG
‎2020-12-02 05:49 PM
0 Likes
0
684
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-12-02 05:49 PM

Re: T_SPx70 Data Types

The Object DNP3 or ModBus address exists for the Object value. In the case of ModBus there is no address that can be assigned to say Limit 3H.

When you use the T_SPx70_ADV_ANALOG Logic variable type, the parameters (in most cases) may be written to by logic.  this starts to get messy as you have to create a second object with logic variable and assign that a ModBus address and map across to the original parameter. Typically you need to do this when there is a local HMI as a user interface. Ideally you should make these changes on the original object via GEO SCADA as one point of truth.

 

Another option in Logic is to use the OBJ_WriteField function block. This can also be used in conjunction with OBJ_DNP3PointToID command if the object doesn't have a Logic variable type associated with it.

This is a very powerful and flexible command. I have used it to assign a fixed timestamp to an object before creating an event.

 
Tags (6)
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Share
Reply
SCADAPro52
Ensign SCADAPro52
Ensign
‎2020-12-03 05:57 AM
0 Likes
2
670
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-12-03 05:57 AM

Re: T_SPx70 Data Types

Thanks for the reply Joel.  That is what I thought.

However, I'm not clear on how to assign a DNP3 variable to the attribute.  

Where can I find assistance on this?

 

Appreciate the assist on this!

45+ years in SCADA & ICS and still learning every day!
Tags (6)
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Share
Reply
Joel_Weder
Lieutenant Joel_Weder Lieutenant
Lieutenant
‎2020-12-03 07:46 AM
0 Likes
1
660
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-12-03 07:46 AM

Re: T_SPx70 Data Types

Hi SCADAPro52,

 

As pointed out by Alastair after my first post, I was incorrect in saying that a Modbus or DNP3 address could be assigned to an attribute of an object directly. It can be done via other means, which I'll mention in a moment. But in fact what you can do is assign a DNP3 or Modbus address to the object as a whole.

 

After creating a new Project in RemoteConnect with the appropriate options, you go to the Objects tab and then Object Configuration. Scroll down to the analog object in question and double-click on it. Set the object to be a T_SPx70_ADV_ANALOG type, then a bit further down in the same window click on the DNP3 (or Modbus) tab for that object. After assigning a point number, you can configure the DNP3 Group & Variation, and a data class.

 

I missed one item regarding how to write to an attribute remotely. What I'd do is create a new object with a DNP3 point #, just for external communication, that can be written to by a DNP3 SCADA host or HMI. Then add a bit of logic to copy that value to the level attribute.  It would be accessed as (for example) PIO_SP575_AI1.L1_LIMIT

 

Joel Weder
Telemetry Solutions Specialist
Schneider Electric

See Answer In Context

Tags (6)
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Share
Reply
SCADAPro52
Ensign SCADAPro52
Ensign
‎2020-12-15 08:35 AM
0 Likes
0
554
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-12-15 08:35 AM

Re: T_SPx70 Data Types

Thanks for the guidance with this topic.

 

I was able to figure out how to access the object parameters and configure the logic necessary to set the alarm values for two different points at the same time.  Also, will be configuring system to only allow remote (SCADA) changes to setpoints and not local changes to comply with CRM regulations.

 

Appreciate the assist Gentlemen!

45+ years in SCADA & ICS and still learning every day!
Tags (6)
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Share
Reply
Top Experts
User Count
sbeadle
Sisko sbeadle Sisko
15
Joel_Weder
Lieutenant Joel_Weder Lieutenant
11
MartinChartrand
Commander MartinChartrand Commander
7
Jimi
Lt. Commander Jimi Lt. Commander
3
BevanWeiss
Sisko BevanWeiss
3
Hardin4019
Lieutenant Hardin4019
1
See More Top Experts
Find a Service Provider
Find a certified partner to help you address your integration, installation, maintenance and project needs.
View all Providers
Support

Have a question? Please contact us with details, and we will respond.

Contact Us
FAQ

Look through existing questions to find popular answers.

Learn More
About

Want to know more about Exchange and its possibilities?

Learn More

Full access is just steps away!

Join Exchange for FREE and get unlimited access to our global community of experts.

Connect with Peers & Experts

Discuss challenges in energy and automation with 30,000+ experts and peers.

Get Support in Our Knowledge Base

Find answers in 10,000+ support articles to help solve your product and business challenges.

Ask Questions. Give Solutions

Find peer based solutions to your questions. Provide answers for fellow community members!

Register today for FREE

Register Now

Already have an account?Log in

About Us FAQ Terms & Conditions Privacy Notice Change your cookie settings
©2021, Schneider Electric