A support forum for AVEVA Plant SCADA (formerly Citect SCADA). Share new and exciting product information, connect, learn, and collaborate with the ecosystem of Plant SCADA Users. AVEVA Plant SCADA a reliable, flexible and high-performance Supervisory Control and Data Acquisition software solution for industrial process customers. This forum is to connect, share, learn and collaborate new and exciting product information. Feel free to join and share to your Ecosystem of Plant SCADA Users.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-12-01 03:44 PM
Estimados colegas, saludos cordiales.
Tengo problemas con la importacion de archivos PNG, necesito importar archivos sin fondo o crear simbolos con archivos PNG. no me permite importarlos y si los importa, eston estan en blanco y negro o simplemente no se ve nada.
Alguien tuvo el mimso inconveniente? espero su ayuda por favor!
Gracias.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-12-02 06:37 AM
The easiest way to do this is to import a normal png with a plain white (or single colour) background, then use Swap Colors from the Tools menu to change the background to transparent (the selection with an x through it).
I find this is often easier than using a dedicated graphics package to set a transparent background.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-12-02 06:23 AM
Hello @sesa222731 , Do you know who can support on this?
Regards,
R.-
Rodrigo G.
Industrial Automation Community manager
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-12-02 06:37 AM
The easiest way to do this is to import a normal png with a plain white (or single colour) background, then use Swap Colors from the Tools menu to change the background to transparent (the selection with an x through it).
I find this is often easier than using a dedicated graphics package to set a transparent background.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-12-02 11:18 AM
@Xavhiii You're likely to hit a wider target audience if you were to write in English (or at least use Google Translate to include an 'English' version).
In regards to wanting to have transparent (alpha channel) PNG files, this is not supported under Citect, as per:
https://www.se.com/au/en/faqs/FA27/
So you will typically have to do this in other ways.
You could probably try to get your PNG image into the Citect Graphic Builder and modify it from there to add/remove pixels as necessary.
If the background is always a consistent colour, then you could just replace your transparent sections with this colour to emulate transparency. More difficult if the content behind is dynamic.