Follow along for an enriching discussion with our CEO, Peter Herweck, and industry leaders for a captivating Global Keynote at #InnovationSummit Paris 2024. Watch recording and join the #ImpactMaker movement!️
[Imported] Siemens S7-1200 polling Accutech base radio
Remote Operations Forum
Support forum for Schneider Electric SCADA systems, radios and RTUs. From commissioning integration devices and software, to enhancing existing installations or troubleshooting.
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2019-10-2502:47 PM
[Imported] Siemens S7-1200 polling Accutech base radio
>>Message imported from previous forum - Category:Accutech<< User: mchartrand, originally posted: 2018-10-17 19:11:57 Id:91 This is a re-posting from the obsoleted (October 2018) "Schneider Electric Telemetry & SCADA" forum.
-------------------------------
**_AA: I understand it is not really modicon modbus but can be beaten to work. Does anyone have any tips?_**
______________________________
mchartrand: The Siemens S7-1200 would need to talk Modbus RTU via an RS-485 connection in order to poll data from the base radio.
__________________
**_AA: Right. I am hoping someone can advise of bit and word order as well as any offset used and if they use the 4 in 40k registers or not._**
___________________________
mchartrand: There are two possible addressing modes. You need to refer to the user manual for the correct Modbus register addresses for whichever mode you select. You will need to download and install Accutech Manager (free of charge) in order to get to the .chm user manual.
__________________________
**_AA: I hear that base radio firmware 1.86 will have word order selections supporting 1234, 3412, 2143 and 4321 which will make most these type integration issues go away. 4321 is used by Thermo AutoPilot legacy versions where comm parameters are not selectable. These selections are made from the pushbuttons on the base radio._**
________________________
mchartrand: I've been advised by our Software engineers that this is correct.