Follow along for an enriching discussion with our CEO, Peter Herweck, and industry leaders for a captivating Global Keynote at #InnovationSummit Paris 2024. Watch recording and join the #ImpactMaker movement!️
[Imported] Maximum distance specifications
Remote Operations Forum
Support forum for Schneider Electric SCADA systems, radios and RTUs. From commissioning integration devices and software, to enhancing existing installations or troubleshooting.
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2019-10-2512:45 PM
[Imported] Maximum distance specifications
>>Message imported from previous forum - Category:Trio Data Radios<< User: joelw, originally posted: 2018-10-17 17:53:07 Id:57 This is a re-posting from the obsoleted (October 2018) "Schneider Electric Telemetry & SCADA" forum.
----------------------
**_jweder: The question often arises "how far can your radios reach?" This is not as easy to answer as it sounds._**
______________
Yes there is an ideal maximum range, presuming very tall towers (can you afford 300 foot towers, or maybe you have mountains available?) and nothing in the way. For our 900 MHz spread spectrum radios this maximum is about 70 km. (or 43 miles) For the 450 MHz licensed radios this ideal distance is somewhat greater, but the tower heights must increase to go much farther. (otherwise one or both sites must be on large hills or mountains)
In reality however, the terrain and obstacles such as trees and buildings will have great effect on the actual distance. Real world tower heights are constrained by budgets and municipal regulations. It's a rare system that can afford 200-400 foot towers, so often hills or mountains are used to gain height.
If you want to have a fairly reliable indicator of maximum range, the only good way to to this is to do a path analysis. This can be done with software such as Path Loss or Radio Mobile. Schneider Electric will do a path study for you if requested. Fill out the attached spreadsheet (using the pdf document also included as guidance) then send it to TRSSpathstudy[at]schneider-electric.com
Attached file: (editor/8e/f4wxawq28boq.xls), Schneider Electric TRSS Radio Path Study Request Form ver 011.xls File size: 78848
Attached file: (editor/rt/p23lang5cxh9.pdf), SE Radio Path Analysis Procedure (R1.3).pdf File size: 1254340