Follow along for an enriching discussion with our CEO, Peter Herweck, and industry leaders for a captivating Global Keynote at #InnovationSummit Paris 2024. Watch recording and join the #ImpactMaker movement!️
[Imported] J / K Series Dual Antenna Ports
Remote Operations Forum
Support forum for Schneider Electric SCADA systems, radios and RTUs. From commissioning integration devices and software, to enhancing existing installations or troubleshooting.
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2019-10-2512:05 PM
[Imported] J / K Series Dual Antenna Ports
>>Message imported from previous forum - Category:Trio Data Radios<< User: joelw, originally posted: 2018-10-16 20:29:35 Id:13 This is a re-posting from the obsoleted (October 2018) "Schneider Electric Telemetry & SCADA" forum.
-------------------------------
**_jweder: The J Series and K Series unlicensed radios both have two antenna ports. These can be of great benefit under certain circumstances. The ANT1 port is always used if only one antenna is required, but how and when do you use ANT2?_**
_______________
There are two different ways in which the ANT2 port will come into use:
1) In a radio configured as a Bridge repeater the user may configure the radio as a Dual Antenna Bridge. In this case all communications upstream (towards the Master) will occur on the ANT1 port, and all communications downstream (towards the Remotes) will occur on the ANT2 port. So ensure you connect the antennas appropriately.
It may be desired to have a high gain yagi antenna on ANT1, as the path to the Master is long or obstructed, and more gain is needed. Alternately on ANT2 you may desire to have a low gain omni to communicate with Remotes scattered around the Bridge. Or perhaps a second yagi might be required on ANT2, to communicate with a Remote or Bridge further out.
2) In a radio configured as a Master (Access Point) or Remote the second antenna port may also be enabled. In this case, the radio will always transmit on the ANT1 port, and it will always receive on the ANT2 port. This feature is rarely required, but will be useful in situations where filters or amplifiers are necessary eg in order to overcome losses in cabling and/or filters, or add filters to reduce interference.