Sign In Help
Schneider Electric
HelpSign In
Schneider Electric Exchange
  • Home
  • Collaborate
  • Develop
  • Shop
Home Collaborate Develop Shop Log in or Register Help

Invite a Co-worker

Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel

Invitation Sent

Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
  • Home
  • Collaborate
  • Exchange Community
  • :
  • SCADA & Telemetry Solutions
  • :
  • SCADA and Telemetry Devices Forum
  • :
  • Re: A TC10 in a rotary Furnace
Community Menu
  • Forums
    • By Topic
        • EcoStruxure IT
          • EcoStruxure IT forum
        • Industrial Automation
          • Industry Automation and Control Forum
          • Alliance System Integrators Forum
          • Machine Solutions in the Digital Transformation
          • EcoStruxure Automation Expert / IEC 61499 Forum
          • Industrial Edge Computing Forum
          • Level and Pressure Instrumentation Forum
          • Modicon User Group
          • PLC Club Indonesia
          • SEE Automation Club Forum
          • Fabrika ve Makina Otomasyonu Çözümleri
          • Форум по промышленной автоматизации СНГ
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Forum
          • SCADA and Telemetry Devices Forum
        • Power Distribution IEC
          • Power Distribution and Digital
          • Power Standards & Regulations
          • Paneelbouw & Energie Distributie
        • Power Distribution Softwares
          • EcoStruxure Power Design Forum
          • SEE Electrical Building+ Forum
          • LayoutFAST User Group Forum
        • Solutions for your Business
          • Solutions for Food & Beverage Forum
          • Solutions for Healthcare Forum
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Forum
        • Healthcare
          • Solutions for Healthcare Forum
      • EcoStruxure IT
        • EcoStruxure IT forum
      • Industrial Automation
        • Industry Automation and Control Forum
        • Alliance System Integrators Forum
        • Machine Solutions in the Digital Transformation
        • EcoStruxure Automation Expert / IEC 61499 Forum
        • Industrial Edge Computing Forum
        • Level and Pressure Instrumentation Forum
        • Modicon User Group
        • PLC Club Indonesia
        • SEE Automation Club Forum
        • Fabrika ve Makina Otomasyonu Çözümleri
        • Форум по промышленной автоматизации СНГ
      • SCADA & Telemetry Solutions
        • Geo SCADA Expert Forum
        • SCADA and Telemetry Devices Forum
      • Power Distribution IEC
        • Power Distribution and Digital
        • Power Standards & Regulations
        • Paneelbouw & Energie Distributie
      • Power Distribution Softwares
        • EcoStruxure Power Design Forum
        • SEE Electrical Building+ Forum
        • LayoutFAST User Group Forum
      • Solutions for your Business
        • Solutions for Food & Beverage Forum
        • Solutions for Healthcare Forum
      • Food & Beverage
        • Solutions for Food & Beverage Forum
      • Healthcare
        • Solutions for Healthcare Forum
  • Blogs
    • By Topic
        • Industrial Automation
          • Industrial Edge Computing Blog
          • Industry 4.0 Blog
          • Industrie du Futur France
        • SCADA & Telemetry Solutions
          • SCADA and Telemetry Blog
        • Power Distribution IEC
          • Power Events & Webinars
          • Power Foundations Blog
        • Power Distribution NEMA
          • NEMA Power Foundations Blog
        • Power Distribution Softwares
          • EcoStruxure Power Design Blog
          • SEE Electrical Building+ Blog
        • Solutions for your Business
          • Solutions for Food & Beverage Blog
          • Solutions for Healthcare Blog
          • Solutions for Retail Blog
        • Community experts & publishers
          • Publishers Community
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Blog
        • Healthcare
          • Solutions for Healthcare Blog
        • Retail
          • Solutions for Retail Blog
      • Industrial Automation
        • Industrial Edge Computing Blog
        • Industry 4.0 Blog
        • Industrie du Futur France
      • SCADA & Telemetry Solutions
        • SCADA and Telemetry Blog
      • Power Distribution IEC
        • Power Events & Webinars
        • Power Foundations Blog
      • Power Distribution NEMA
        • NEMA Power Foundations Blog
      • Power Distribution Softwares
        • EcoStruxure Power Design Blog
        • SEE Electrical Building+ Blog
      • Solutions for your Business
        • Solutions for Food & Beverage Blog
        • Solutions for Healthcare Blog
        • Solutions for Retail Blog
      • Community experts & publishers
        • Publishers Community
      • Food & Beverage
        • Solutions for Food & Beverage Blog
      • Healthcare
        • Solutions for Healthcare Blog
      • Retail
        • Solutions for Retail Blog
  • Ideas
        • Industrial Automation
          • Modicon Ideas & new features
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Ideas
          • SCADA and Telemetry Devices Ideas
  • Knowledge Center
    • Building Automation Knowledge Base
    • Industrial Automation How-to videos
    • Ask Exchange
    • Digital E-books
    • Success Stories Corner
    • Power Talks
  • Events & Webinars
  • Support
    • User Guide
    • Leaderboard
    • Releases Notes
How can we help?
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
49672members
Join Now
243100posts
Join Now

A TC10 in a rotary Furnace

Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Solved Go to Solution
Back to SCADA and Telemetry Devices Forum
Solved
LorenR
Ensign LorenR Ensign
Ensign
‎2020-03-24 07:22 AM
0 Likes
12
4378
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-03-24 07:22 AM

A TC10 in a rotary Furnace

Has anyone of you installed a TC10 in a rotary furnace with ambient temperatures above what our field unit withstands? If you have, how have you done it? What kind of isolation have you used to protect the field unit? Thanks!

Solved! Go to Solution.

Labels
  • Telemetry
Share
Reply

Accepted Solutions
Joel_Weder
Lieutenant Joel_Weder Lieutenant
Lieutenant
‎2020-03-31 10:11 AM
0 Likes
0
3953
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-03-31 10:11 AM

Re: A TC10 in a rotary Furnace

Hello again Loren,

 

OK, so the distance is more reasonable for Accutech. But still the temperature (95 to 120 deg C) is not suitable for Accutech. Unless your SI changes their story, I suggest you move on to consider a different solution.

 

Joel Weder
Telemetry Solutions Specialist
Schneider Electric

See Answer In Context

Share
Reply
  • All forum topics
  • Previous Topic
  • Next Topic
12 Replies 12
MartinChartrand
Lt. Commander MartinChartrand Lt. Commander
Lt. Commander
‎2020-03-24 07:38 AM
0 Likes
11
4376
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-03-24 07:38 AM

Re: A TC10 in a rotary Furnace

Hi LorenR,

I unfortunately don't have any known examples of the field units being used at temperatures above the recommended specification, but suffice it to say that some insulation would be required.

 

To further assist anyone who might want to comment on this, can you please advise:

 

1) What type of field unit housing are you referring to? The old plastic "yellow pyramid hat" type that is no longer available, or the more robust cylindrical metal housing that is available?

 

2) What is the actual ambient air temperature that this field unit needs to work in?

 

3) Does this field unit have an integral antenna or a cable to a remotely located antenna? This would have to be taken into account when designing an insulated enclosure.

 

Let's hope someone has experience in this type of installation.

 

Regards,

Martin Chartrand

SCADA & Telemetry Solution Specialist

Share
Reply
LorenR
Ensign LorenR Ensign
Ensign
‎2020-03-24 08:18 AM
0 Likes
10
4373
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-03-24 08:18 AM

Re: A TC10 in a rotary Furnace

Hi Martin

 

 

1) Field unit with aluminum housing

 

2) 120°C for ambient air temperature, approx. 

 

3) Pending to be determined. They currently have thermocouples with a remote unit for wireless transmission, but they have had too many problems with the cabling (it fails due to the high temps), so they want to try something else. Please check the attached drawing. The first field unit would be installed in MA (highlighted in yellow), and the rest right next to it, in N, P, R... up to WB, being the MA the one withstanding the highest temperature, and the baseradio located in a cabinet at approx. 1.5km away from the MA thermocouple. The cabinet is right below the furnace. 

 

We are considering if possible to make some tests with our demo unit for the communication part, but if requiring a remote antenna, we would also need a cable capable to be in such a high temperature without suffering any damage. 

 

Attachments
Share
Reply
LorenR
Ensign LorenR Ensign
Ensign
‎2020-03-24 08:21 AM
0 Likes
9
4369
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-03-24 08:21 AM

Re: A TC10 in a rotary Furnace

Here's the cabinet's location (left), and the current wireless transmitter (right)

Attachments
Share
Reply
MartinChartrand
Lt. Commander MartinChartrand Lt. Commander
Lt. Commander
‎2020-03-24 09:07 AM
0 Likes
1
4359
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-03-24 09:07 AM

Re: A TC10 in a rotary Furnace

Hi again.

I have one question before commenting further on the operational temperature aspect of this request.

 

Where is this globally located? Location will determine if the radio is to be 900 MHz or 2.4 GHz, which directly affects viable communication distances.

 

From an operational temperature perspective, the field units need to work in temperatures below 80C, so you will need to engineer an isolated box that ensure this maximum temperature is not exceeded. And because the drum is rotating, a unidirectional Yagi antenna likely won't work, this could mean and external remote antenna and cable, in which the cable may need to be insulated too.

 

I have asked a radio expert colleague to comment on what the options could be useful for you here. Please stay tuned.

 

Regards

Martin

 

Share
Reply
LorenR
Ensign LorenR Ensign
Ensign
‎2020-03-24 09:25 AM
0 Likes
0
4354
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-03-24 09:25 AM

Re: A TC10 in a rotary Furnace

Thank you Mark. We will use 900Mhz, customer is a ferronickel producer in Colombia

Share
Reply
Joel_Weder
Lieutenant Joel_Weder Lieutenant
Lieutenant
‎2020-03-24 09:27 AM
0 Likes
6
4352
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-03-24 09:27 AM

Re: A TC10 in a rotary Furnace

Hello Loren,

 

First, I'd like to clarify one item. The Subject line says "TC10 in a rotary Furnace".  From the photos you have attached, it appears the thermocouple only would be in the furnace. The Accutech field unit itself (TC10) would be mounted on the OUTSIDE of the rotating drum. The TC10 housing would likely see a higher than ambient temperature, but 120 degrees??  Or is it 120 degrees INSIDE the rotating drum? 

 

If the temperature outside the drum, where the TC10 would be mounted, is 120 degrees Celsius, then unfortunately Accutech will not be the right solution. If however the 120 degree temperature is only inside the drum, a thermocouple can easily withstand 120 degrees and that will not be a problem.

 

From a wireless perspective, this is a complex environment. The base radio antenna would need to be an omni-directional type (mounted vertically), and installed at a location that can "see" from one end of the rotating drum to the other without obstructions. The TC10 field unit would be equipped with just the standard "internal" antenna, as the distance is short. A yagi (directional) antenna could not be kept pointed at the base radio, so that is not an option.

 

As the drum rotates, the signal level would change significantly due to changing antenna polarization on the TC10. But as the distance appears fairly short (perhaps 100 metres?) the loss caused by this may be acceptable. The primary issue will be the added loss as the barrel rotates the TC10 around to the far side, away from the base radio. If there are some structures above or on the far side of the rotating drum, these may allow reflections of the wireless signal to reach the base radio.

 

If the wireless signal is lost when the drum rotates the TC10 away, this may not in any case be a problem. If the temperature is not changing very rapidly, it may be OK to miss transmissions sometimes. (eg 1/4 of the time) The polling system would need to be designed to accept that only about 3/4 of the messages would be successful.

 

Joel Weder
Telemetry Solutions Specialist
Schneider Electric
Share
Reply
LorenR
Ensign LorenR Ensign
Ensign
‎2020-03-24 09:43 AM
0 Likes
5
4350
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-03-24 09:43 AM

Re: A TC10 in a rotary Furnace

Hi Joel

 

Sorry, I have problems with the use of "in" and "on" :-(. Yes, the thermocouple would be inside, and the TC10 mounted right there on the rotating drum, outside of it. But those 120°C are ambient temperature at MA's location. Please check the attached drawing which explains it better.  The distance from MA (the farthest TE) to the baseradio would be around 1.5Km.

 

An isolation would definitively be required for the TC10's that are closer to the burner on the left, and some considerations as well for the antenna cable if remote omni for the field units are required, but since this would be our first time installing them, we wanted to hear from others who had done it before, and how had they done it 🙂

 

 

Attachments
Share
Reply
Joel_Weder
Lieutenant Joel_Weder Lieutenant
Lieutenant
‎2020-03-24 10:03 AM
0 Likes
4
4345
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-03-24 10:03 AM

Re: A TC10 in a rotary Furnace

Hi again Loren,

 

OK, understood.  The photograph makes it look like the base radio will be very NEAR to the rotating drum, not 1.5 kilometres away!! I think I can actually see a bit of a rotating drum structure in the photo of the base radio enclosure. Or am I confused?  I would strongly suggest that the Accutech base radio be installed near to the rotating drum. You could add a Trio K Series point-to-point radio system to transfer the data over that 1.5 kilometre distance much more successfully. 

 

If the distance from the TC10 field unit to the Accutech base radio is 1.5 kilometres this solution (from a purely wireless perspective) is far more challenging. You could use a high gain yagi (directional) antenna on the base radio, installed above all local obstacles, to partially offset the distance, but the TC10 would still need a no-gain internal antenna. The signal might be sufficient to reach the base radio when the TC10 is at the top or at the bottom of the rotating drum - its omni antenna would then be parallel to the base radio's antenna for best signal transmission. But if any local obstacles (near the rotating drum) maybe only when the TC10 is near the top, above obstacles. You would have to test this in the field.

 

The primary issue remains temperature rating, however. A TC10 field unit has a maximum temperature rating of 85 degrees Celsius. I can't see how you could protect the TC10 for a long time - if the rotating drum and its furnace are running for many hours the temperature inside the protective enclosure will slowly rise towards 120 degrees unless you actively refrigerate the enclosure. If you have some idea about how to do that successfully, great !! But remember that any enclosure around the TC10 will further reduce the wireless signal level, especially if there is a metal layer. 

Joel Weder
Telemetry Solutions Specialist
Schneider Electric
Share
Reply
LorenR
Ensign LorenR Ensign
Ensign
‎2020-03-25 06:55 AM
0 Likes
3
4329
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-03-25 06:55 AM

Re: A TC10 in a rotary Furnace

Hi Joel!

 

No no, I meant 1.5km distance from the MA thermocouple to the baseradio cabinet, not from the baseradio to the rotaring drum. Those two (the BR and the furnace) are indeed very close.  

 

About how to cool it down, no, we have no idea how to do it, which is why we opened this post hoping to find someone who has done it before and could share their experience with us ^_^

 

I hadn't thought about the integral antenna exposed to that temperature until just now, actually.. it would also need to be inside the protective enclosure if it doesn't withstand 120 degrees

Share
Reply
LorenR
Ensign LorenR Ensign
Ensign
‎2020-03-31 07:27 AM
0 Likes
2
3998
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-03-31 07:27 AM

Re: A TC10 in a rotary Furnace

Hi!

No, not just yet. I'm actually waiting for the S.I. to re-confirm some data, since it seems the distances and temperatures he gave me were not correct. I'll update as soon as I hear from him

Share
Reply
LorenR
Ensign LorenR Ensign
Ensign
‎2020-03-31 09:46 AM
0 Likes
1
3958
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-03-31 09:46 AM

Re: A TC10 in a rotary Furnace

Ok, so this is what the S.I. confirmed today:

 

- Distance is meters, with the maximum being 120 to 140 meters from the farthest TT to the radiobase, not 1.5km as he had told us previously.

- Maximum ambient temperature is 95 to 120°C. I don't know, it still sounds like too much. The S.I. is going to reconfirm again.

- TT has to be installed directly on top of the thermocuple, no cable is preferred. 

Share
Reply
Joel_Weder
Lieutenant Joel_Weder Lieutenant
Lieutenant
‎2020-03-31 10:11 AM
0 Likes
0
3954
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-03-31 10:11 AM

Re: A TC10 in a rotary Furnace

Hello again Loren,

 

OK, so the distance is more reasonable for Accutech. But still the temperature (95 to 120 deg C) is not suitable for Accutech. Unless your SI changes their story, I suggest you move on to consider a different solution.

 

Joel Weder
Telemetry Solutions Specialist
Schneider Electric

See Answer In Context

Share
Reply
Find a Service Provider
Find a certified partner to help you address your integration, installation, maintenance and project needs.
View all Providers
Support

Have a question? Please contact us with details, and we will respond.

Contact Us
FAQ

Look through existing questions to find popular answers.

Learn More
About

Want to know more about Exchange and its possibilities?

Learn More

Full access is just steps away!

Join Exchange for FREE and get unlimited access to our global community of experts.

Connect with Peers & Experts

Discuss challenges in energy and automation with 30,000+ experts and peers.

Get Support in Our Knowledge Base

Find answers in 10,000+ support articles to help solve your product and business challenges.

Ask Questions. Give Solutions

Find peer based solutions to your questions. Provide answers for fellow community members!

Register today for FREE

Register Now

Already have an account?Log in

About Us FAQ Terms & Conditions Privacy Notice Change your cookie settings
©2020, Schneider Electric