With E-Series Configurator we can select "TCP Service" as a Port Function, which is not available in RemoteConnect.
For example, we have a Trio ER450 radio, its port B is currently conncted to the Port 2 (configured as TCP Service) of a SCADAPack ES for diagnostic purpose. We are upgrading the SCADAPack ES to SCADAPack 575, is there a way to migrate this function to SCADAPack 575?
Thanks.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-01-14 06:51 AM
The TCP service name on the Scadapack E configurator Ports and Modes setting was changed in RemoteConnect and
It is now called Terminal Server.