[Imported] Realflo Flow Extension Units

Highlighted
Sisko

[Imported] Realflo Flow Extension Units

>>Message imported from previous forum - Category:Realflo Electronic Flow Measurement<<
User: mchartrand, originally posted: 2018-10-17 18:44:02 Id:78
This is a re-posting from the obsoleted (October 2018) "Schneider Electric Telemetry & SCADA" forum.

-------------------------------

**_texyank:
What are the engineering units used to calculate the Flow Extension for AGA 3 gas measurement. The meter is set up to use US units of measure, psi, inches of H2O. The flow extension is reported in kg/m3s.
Does the RTU do all calcs using bar and millibar?
Is there a way to have the flow extension reported using the configured units?_**

__________________

PSysak:
Hello,

"What are the engineering units used to calculate the Flow Extension for AGA 3 gas measurement. The meter is set up to use US units of measure, psi, inches of H2O. The flow extension is reported in kg/m3s.
— Yes. It's a fixed unit in the RealFLO current readings view. RealFLO does do some conversion between the contract unit and kg/m3s.

Does the RTU do all calcs using bar and millibar?
— No.

Is there a way to have the flow extension reported using the configured units?
— The current RealFLO version does not support that.