[Imported] RealFLO.tfc File

Highlighted
Sisko

[Imported] RealFLO.tfc File

>>Message imported from previous forum - Category:Realflo Electronic Flow Measurement<<
User: mchartrand, originally posted: 2018-10-17 18:49:13 Id:82
This is a re-posting from the obsoleted (October 2018) "Schneider Electric Telemetry & SCADA" forum. The original posters' identities have not been included. Schneider Electric is not responsible for the content of these posts.

-------------------------------

**_loriet:
I have noticed that the *.tfc does not hold the complete meter configuration. For example, I transferred just the *.tfc to another computer to print the configuration, when I opened the file it wasn't complete. The sensor configuration was incorrect. When I transferred all files, *.tf* files and then opened the *.tfc the configuration was correct.
Exactly what files constitute the configuration? It used to be just the *.tfc file._**

______________________

swesley:
Hi Lorie,
You also need the TFS file. The TFS file has the non flow computer settings.
You can also create a template file, but in short you need all the files created for that one.